Onan Enclosure Thoughts - 6.5NH


this thread has 27 replies and has been viewed 1052 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-12-2017, 12:20:38 AM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 114
Thanks: 11
Thanked 23 Times in 12 Posts
Default Onan Enclosure Thoughts - 6.5NH

So I'm very nearly finishing the rebuild of my new 6.5NH. Muffler should be fabbed up and installed this week and then I'm going to go about getting it mounted and connected.

I'm starting to think about an enclosure. For cost (copper is expensive) the unit will probably be within 10 feet of the home. Exhaust will be exiting right next to Vacu-flow exit and pointing AWAY from the house so I'm thinking that we should be safe from any CO poisoning via the eaves. (it is a very tall 2 story house so even 10 feet might be overkill).

I'm looking at budget friendly options. I likely will be putting something on a wood-framed gravel pad to start (might do a concrete slab in the future). I'm considering building something out of plywood and painting with a fire-proofing agent just to be safe. I'm not sure how exhaust can be safely routed through a wood enclosure though? Maybe a large chicken-wire opening for the vacuflow and muffler to exit within a few inches of it? Trying to avoid trapping too much exhaust heat in the enclosure.

Is wood just stupid? Are there better options? I've seen those suncast/rubbermaid solutions but I don't know how well those work out for anyone. I realize obviously I'm going to be putting intake vents as well (probably a full side of intake vents at the generator end to assist in fresh intake to the vacuflow).

Would love some thoughts/pictures that you all have - I searched a bit but didn't find anything quite specific on this topic.
Reply With Quote
Sponsored Links
  #2  
Old 03-12-2017, 01:49:57 AM
Ray Lynch Ray Lynch is offline
Subscriber
 
Join Date: Aug 2014
Location: New Windsor, New York, USA
Posts: 495
Thanks: 333
Thanked 325 Times in 206 Posts
Default Re: Enclosure Thoughts - 6.5NH

See posts #24, 25 and 26 in attached link for what I did for my JB.

Ray

https://www.smokstak.com/forum/showt...=140244&page=2
Reply With Quote
The Following 4 Users Say Thank You to Ray Lynch For This Post:
  #3  
Old 03-12-2017, 10:04:05 AM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 114
Thanks: 11
Thanked 23 Times in 12 Posts
Default Re: Enclosure Thoughts - 6.5NH

Thanks Ray - your first run enclosure looks along the lines of what I wanted to build as a quick start - we are fast approaching what I think will be a very stormy spring here in TN and I'd like to get this set up in the next weekend or two.

Couple questions - what did you use for the sides and where did you source it? Is it plywood with cutouts for the vents or are they fully vented panels? How was the noise management with this enclosure?
Reply With Quote
  #4  
Old 03-12-2017, 11:11:42 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,918
Thanks: 8,734
Thanked 14,280 Times in 6,737 Posts
Default Re: Enclosure Thoughts - 6.5NH

With an NH the noise shouldn't be a problem to keep down. For the exhaust going through wood. You can get thimbles for stove pipe thru wood. The main thing is to give it plenty of cooling air and make it easy to service. Ray has a very good install. You should be ok with the house and exhaust. I believe the required space is eight feet.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following User Says Thank You to Billy J Shafer For This Post:
  #5  
Old 03-12-2017, 11:28:13 AM
Kevin K Kevin K is online now
Registered-III
 
Join Date: Jan 2005
Location: upstate New York USA
Posts: 3,775
Thanks: 3,461
Thanked 3,882 Times in 2,067 Posts
Default Re: Enclosure Thoughts - 6.5NH

While the "Gold Standard" generator housing is a 10x10 or 12x12 wooden shed like Leon has for his JB, a doghouse style enclosure can also be used. A wooden shed has the advantage of keeping the generator temperature above the surrounding air temperature at night, and prevents condensation and rust from forming on the generator. On the other hand, there is the problem of safely routing the exhaust through the flammable wooden wall , which can be accomplished by using a small thimble made for a wood stove flue pipe.

I would consider raising the enclosure two feet above ground level, with stacked cement blocks, legs, or a stand of stacked 6x6 pressure treated timber filled with crushed stone. Here in the Northeast, it is not uncommon to have a two foot deep coating of snow on the ground, and you don't want to dig the generator out before you use it. A raised generator shed also keeps it out of the splash zone during a rain storm, and above ground level in case of a flood. Your back will thank you because you don't need to bend over or lie on the ground to service it. Raising it may also help with rodent incursion issues.

If you have an inherently regulated generator like the NH, the output voltage is a function of engine speed. Because of governor droop, the speed will typically range from 62Hz no load to 58 or 59 Hz full load, and consequently the voltage under full load is typically on the order of 110VAC. This doesn't leave much room for voltage drop in the wiring to the house, so you may want to use a bit heavier wire to minimize voltage loss.
Reply With Quote
  #6  
Old 03-12-2017, 11:45:54 AM
Ray Lynch Ray Lynch is offline
Subscriber
 
Join Date: Aug 2014
Location: New Windsor, New York, USA
Posts: 495
Thanks: 333
Thanked 325 Times in 206 Posts
Default Re: Enclosure Thoughts - 6.5NH

Quote:
Originally Posted by AppleTech View Post
Thanks Ray - your first run enclosure looks along the lines of what I wanted to build as a quick start - we are fast approaching what I think will be a very stormy spring here in TN and I'd like to get this set up in the next weekend or two.

Couple questions - what did you use for the sides and where did you source it? Is it plywood with cutouts for the vents or are they fully vented panels? How was the noise management with this enclosure?
Three of the sides are 1/2" pt plywood that I cut for the vents. The vents are from Lowes. The 4th side where the muffler exits is made from 2 metal closet doors that I got from CL and cut down. This 4th metal side is shown in the pics for the 2nd enclosure.
The roof is metal. The roof frame is metal studs.
The noise level is similar to my 12.5 HP ride on mower.
I know wiring and trenching are $ and work but get it as far from your house as practical.
Exhaust fumes have a way of finding the inside of your house under the right conditions.
Good luck.
Ray
Reply With Quote
The Following 2 Users Say Thank You to Ray Lynch For This Post:
  #7  
Old 03-12-2017, 02:20:48 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,905
Thanks: 427
Thanked 5,758 Times in 4,184 Posts
Default Re: Enclosure Thoughts - 6.5NH

Looking at mud splashed up on stuff looks splash zone from rain extends 2 - 2.5 ft up from ground. So I'ld consider vent louvers inside the enclosure also, aimed so as up going splash comes thru outer louver it hits backside of internal louver instead of gen. Saw a GE gen at home Depot recently, it's air intake vents are at top, on under side of overhanging cover. About 2.5 ft up.

Good to have space between enclosure and gen so if snow makes it thru enclosure vents then it has someplace to go before it clogs the gen cooling intakes. This is another good reason to raise the gen

If you use wood or plastic for enclosure walls there are fire code rules for min distance to combustibles.
Gut feeling is plastic will warp up from heat.

Gens on ground without a slab , I'ld put some type of moisture barrier under gen to prevent moisture from coming up from the ground and making high humidity in the gen enclosure. Humidity leads to condensation on the gen.

I like the gravel under the gen , they say mice don't like walking on it. But I suspect won't make much difference for such a short walk. Plus can lose carb parts in it. Maybe place gravel around the enclosure, if tree leaves won't cover it over in a few years.

I would say if house is taller ( 2 story vs 1) then gen should be further away from house, (possibility of CO making it to 2nd floor). Not sure, here I think code says 10 ft from gen to building. Rules about distances from exhaust to windows too.

I do like Leon's shed, makes for a warm place out of wind to work on gen if it won't start during outage. Plus should get no condensation if you close off vents when not in use.

Last edited by len k; 03-12-2017 at 03:16:17 PM.
Reply With Quote
  #8  
Old 03-12-2017, 09:02:30 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 114
Thanks: 11
Thanked 23 Times in 12 Posts
Default Re: Enclosure Thoughts - 6.5NH

I ran across this on Craigslist. All-aluminum enclosure for $200. Surely more expensive than building one from plywood although it would save me lots of time. Looks to be already insulated, although I'm guessing not fire rated.

https://nashville.craigslist.org/mat/6026744552.html
Reply With Quote
  #9  
Old 03-12-2017, 10:48:33 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 114
Thanks: 11
Thanked 23 Times in 12 Posts
Default Re: Enclosure Thoughts - 6.5NH

Quote:
Originally Posted by AppleTech View Post
I ran across this on Craigslist. All-aluminum enclosure for $200. Surely more expensive than building one from plywood although it would save me lots of time. Looks to be already insulated, although I'm guessing not fire rated.

https://nashville.craigslist.org/mat/6026744552.html
Their full site is here gcenclosures.com. Having issues with emails going through but I'm going to call them tomorrow and see if they offer any units sans insulation so I could install my own of the proper spec.
Reply With Quote
  #10  
Old 03-12-2017, 11:24:03 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 4,027
Thanks: 5,155
Thanked 1,717 Times in 1,152 Posts
Default Re: Enclosure Thoughts - 6.5NH

Wow, that's looks like a NICE enclosure!!
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 6.5 nh in its new portable enclosure yellowlister Onan Generators 16 02-09-2015 03:12:43 AM
Onan 5.0 CCK 3CR/8457R Enclosure; Dale Russell Onan Generators 3 09-23-2014 08:02:00 PM
Onan MAJB enclosure Jeff Klein Onan Generators 0 06-06-2013 02:03:29 AM
Onan Weatherproof Enclosure country bumpkin Onan Generators 10 09-22-2010 10:30:37 PM
Onan 12.0 DJC Enclosure (Noisy!) Steve Dawkins Onan Generators 37 03-17-2005 05:56:07 AM