Originally Posted by Wayne 440 View Post
IIRC, the overspeed switch is in the generator end bell and provides a ground to the control board on overspeed. The switch could be stuck or dirty, wire broken, etc.
Ok, I found it. I will check it out tomorrow. 150-0717
How does the engine control shut down the generator? what does it send (ground-power) and where does it send it-does it tell the transfer switch to shut it down?
Old 03-13-2017, 09:36:51 PM
Billy J Shafer's Avatar
Depending on the system. It will ground or open the system. At the main control board. The transfer switch shuts down after it has gone through the timers. If normal power is off when genset shuts down. It will get dark.
Old 03-13-2017, 09:41:24 PM
I understand the timers. but looking at the schematic, I don't see what shuts it down. If I can see how it shuts down then i can start looking. Not knowing what it suppose to do, i don't know where to even start looking
The Following User Says Thank You to gjinc For This Post:
Old 03-13-2017, 10:47:35 PM
EricWood's Avatar
EricWood EricWood is offline
gjinc,
If I understand this thread correctly, you're being told of where to look for the overspeed protection on the generator, which is a magnetically restrained centrifugal switch, that is located on the tail end of the generator shaft at the rear of the set, behind the cover. It is for shutting the generator down in the event of uncontrolled high speed engine operation, and has nothing to do with the transfer switch.
The transfer switch, which would have to have the overvoltage feature enabled/set correctly, would only disconnect from the errant source, if the other power source was available and accepted by the controls. There is no "load shed" feature to overvoltage protection. Overvoltage protection only worked on these switches to switch from the out of spec power source, to a good source, if available.
If you wanted an OTPC switch to disconnect upon overvoltage, you would have to have the "Load Shed" module kit installed, and add an independent overvoltage sensor (such as made by TimeMark), and wire its normally open contact to operate a DC-powered latching relay, that would require you to go push a normally closed, spring-loaded momentary button to unlatch it and restore generator power once it was acceptable again. (double-pole DC relay; one set of contacts latches in the relay, the other set of contacts latches in the load shed signal)
Last edited by EricWood; 03-13-2017 at 10:49:54 PM. Reason: removed comments about incorrect transfer switch
The Following 4 Users Say Thank You to EricWood For This Post:
Old 03-13-2017, 11:08:46 PM
Thanks Eric, that's what I wanted to know about the transfer switch.
I found the switch on the tail end.
Now the only thing I need to figure out is how the engine control shuts down
the generator when a fault occurs. The switch or sensor trips a fault, light comes on,
then how does it shut the unit dow?
Old 03-13-2017, 11:23:02 PM
Motorhead's Avatar
The way I would see that the centrifugal switch shuts the engine and generator down would be that the engine ignition system runs through a normally closed relay. When the centrifugal switch trips, it then grounds the normally closed relay electromagnetic coil which opens and disconnects the power supplied to the engines ignition system. If your engine has a standard points ignition system then when the centrifugal switch tripped and grounded, it would ground out the POINTS side of the ignition coil.
The Control panel
and gauges of my
7.5JB
Old 03-13-2017, 11:34:10 PM
Thanks, that makes sense. i am trying to read the schematic as to what relay, what terminals the signal travel through to find what is not working. I don't know if a wire, relay, or if engine control board is bad
Old 03-13-2017, 11:59:19 PM
EricWood's Avatar
Reference the attached diagram. Your 5-light control board opens the circuit to your K12's B-side of the coil for all alarms, to shut down switched B+, which powers your fuel solenoid and ignition. (K12 is the relay on the upper right side interior of your control box, closest to the door.
Are you saying that you can trip overspeed and the unit doesn't shut down? A couple things about those overspeed switches. They are seldom activated. That being said, rust can sieze them up, or make the pivoting movement more difficult to move, that the actual trip point is inconsistent, or much higher than necessary. Add some lube to the pivot points, and move it by hand several times, until you can flick it, and it returns back to the magnet by itself. Also, the button bolt it makes contact with--long ago they were alloy coated, but, they will corrode over time, and/or get coated with grime and dirt, to where the pivot arm isn't getting the grounding signal through it all. Rip off a small piece of scotchbrite pad and shine that screw up if needed.
Not sure if that's the answer you were looking for. If not, could you restate your exact question, as to what you believe is not working, and what led you to that conclusion.
Name:	5-Light Diagram.png
The Following 2 Users Say Thank You to EricWood For This Post:
Old 03-14-2017, 12:18:24 AM
Thank You. That will help me out greatly! I could not follow it on the schematic.
I do not know if the light was on or not, I shut it down as soon as I saw the rpms.
I remember sometime in the past that I had a light on and it was still running. When I got around to checking it out, I never got any lights again while testing.
I'll check this out tomorrow.
Have a nice evening
Old 03-14-2017, 03:33:09 PM
Ok, I cleaned the over speed switch and the contacts. It works pretty good now.
It will trip the light on the engine control but does not shut down the generator