Default Onan 12.5JC-3CR, Questions, Just purchased

I purchased this to use as back up power at home. I'm going to set up a breaker panel interlock with a 50A power inlet and SO cord to feed it. No fancy automatic transfer switch at this time. The unit runs and makes power. I just installed the PerTronics ignition - still could use new wires, cap, rotor and plugs. Runs good now. but has a little miss now and then. The control box doesn't have any visible mouse damage inside and all the wiring looks to be original. I did have to clear an old nest out from between the cylinders. It has the air shutters which open as it warms up. The unit has an all weather housing, which is nice, but hard to get at the spark plugs.

Model: 12.5JC-3CR/11417U
Serial: 0873683987


I believe this was manufactured in August of 1973??? Does this JC have the YD generator? I'd like to add the low oil pressure and high temperature shut downs if possible. I'm not super comfortable leaving a engine run for several hours without being able to watch for trouble. I know low oil pressure or overheating is VERY unlikely on a well maintained engine, but I'm a little crazy. Is there a set of pre-made spark plug wires that will fit, or do I have to get the universal ones?

I'm brand new to these Onans. Seems like an extremely well built unit, however - like an old tractor.

Click image for larger version

Name:	0317171705.jpg
Views:	134
Size:	84.5 KB
ID:	277817

Click image for larger version

Name:	0317171706.jpg
Views:	108
Size:	66.3 KB
ID:	277818

Click image for larger version

Name:	0317171707.jpg
Views:	99
Size:	71.5 KB
ID:	277819

Click image for larger version

Name:	0317171707b.jpg
Views:	119
Size:	118.0 KB
ID:	277820
Reply With Quote
Sponsored Links
  #2  
Old 03-18-2017, 04:13:11 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,717
Thanks: 4,951
Thanked 5,252 Times in 2,873 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

I guess I will retype this entire book since the first draft seems to have been swallowed up by my computer.

Welcome to The Stak, home of all things Onan and many Green Diseases infected folks.

Yes. Your set was built in 8/1973 to spec. U. It is a magneciter gen-end not a YD. Service manual 967-0500 and parts manual 967-0220 can be downloaded from this link for free, thanks to Doug & Mikes hard work. http://www.twinslan.net/~n0nas/manuals/onan/
The occasional miss may be cured by gapping the plugs to .035 if you have not already done this. Tune up parts listed below should be available from the local auto parts store.

Plugs; Champion H8
Points; Carquest 50-3507
Points; Napa CS709
Condenser; Carquest 50-1517
Condenser; Napa AL38
Coil; Carquest 52-2016
Distributor cap; Carquest 51-1509
Distributor cap; Napa AL91
Rotor; Napa AL32
Oil filter; Wix 51452
Oil filter; Napa 1084

I use the generic cut to fit spark plug wires. You can probably buy OEM wires if you want to mortgage your home to get them from Onan.

I think you will find a wiring diagram in the back of the service manual for a set with low oil pressure and high air temp. switches.

This is not the entire first draft, but. I will look after awhile for the build sheet & wiring diagram.

I found the build sheet and what I "think" is the correct diagram.
Attached Files
File Type: pdf 12.5 JC 3-18-17.pdf (25.1 KB, 34 views)
File Type: pdf 12.5 JC diagram 612-2658.pdf (121.2 KB, 35 views)

Last edited by Max Thompson; 03-18-2017 at 04:37:48 PM. Reason: Added build sheet & diagram
Reply With Quote
The Following 6 Users Say Thank You to Max Thompson For This Post:
  #3  
Old 03-18-2017, 04:33:02 PM
BigBlockChev's Avatar
BigBlockChev BigBlockChev is offline
Subscriber
 
Join Date: Jan 2007
Location: Coquitlam, BC, Canada
Posts: 1,803
Thanks: 311
Thanked 1,327 Times in 778 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

It is a little hard to see but it appears that the top of the control box is flat which means it is a magneciter. If the generator end has 6 bolt bosses only 4 of which are used then it is a magneciter, if it has 4 bolt bosses then it is a YD gen end, the battery case obscures that detail in the first pic. The stock oil pressure switch would be located near the oil filter and have a single terminal, it opens on pressure build. It would be easier to add a two terminal, pressure to close oil pressure switch in series with the wires going to the centrifugal switch beside the oil filter, or in series with the power wire going to the coil in the same location. The stock high temp cutout switch is mounted in the discharge air stream at the rear of the machine below the exhaust manifold on the sheetmetal. You could wire a Klixon type switch in the same location in series with the coil to achieve the same effect.https://www.digikey.com/products/en/...=0&pageSize=25, sorry I cant give you a temp value for the air cooled machines , I mainly deal with the marine water cooled gensets , which use about a 250deg sensor. Since it appears that you don't have the factory options it would be more difficult to add the stock switches since the wiring etc is not there now. Cheers Dan
__________________
It's always something simple.
One test is worth a thousand guesses.
If some is good and more is better then too much is just enough
Reply With Quote
  #4  
Old 03-18-2017, 05:53:31 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,423
Thanks: 634
Thanked 1,959 Times in 1,174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Oops! The stock Onan High Temperature Cutoff Switch mounts on the exhaust manifold stud. The switch is connected in series with the control circuits and the ignition coil. It operates at 375 degrees plus or minus 10. It is designed for all the J line air cooled plants.

The switch part number is 309 K 211. THe J-line air cooled plants are designed to have a discharged air temperature 140 degrees above ambient. If you can find a new HAT switch, I have the original Onan installation and performance data should you want a copy.
Reply With Quote
The Following 2 Users Say Thank You to Leon N. For This Post:
  #5  
Old 03-18-2017, 06:00:53 PM
TLB01 TLB01 is offline
Subscriber
 
Join Date: Feb 2017
Location: Seabeck, Washington
Posts: 268
Thanks: 32
Thanked 131 Times in 78 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Those "Hat" snap switches are a common part on pellet stoves and HVAC blowers. Cheap and plentiful.
Reply With Quote
  #6  
Old 03-18-2017, 07:43:34 PM
Mike57 Mike57 is offline
Subscriber
 
Join Date: Sep 2013
Location: Sunnyvale, Texas, USA
Posts: 159
Thanks: 104
Thanked 87 Times in 57 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Leon, I'm curious about the 140 degree number. Were they saying a JB/JC were supposed to run exhaust air temps of ambient plus 140? I've run my JC loaded at mid 80's ambient and not had exhaust air go over 180 degrees (CHT was in the low 300's). I'm pretty sure if exhaust air ever hit 375, a JC motor would be toast by that time. I replaced my HAT with one that kicks at 250.
Reply With Quote
  #7  
Old 03-18-2017, 08:24:13 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,423
Thanks: 634
Thanked 1,959 Times in 1,174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Mike, the Onan tech told me the " maximum" rate of rise of the air temperature passing through the unit is 140 degrees above the ambient temperature. When you stop to think about it, that applies whether your machine is located in let's say, Texas or Alaska. Obviously this 140 degree figure will be affected by how the unit is installed. That is, the duct work, air flow restrictions etc. In my opinion and experience, the J line cooling systems were purposely over designed to account for such installation variables and swings in ambient temperatures.

In my installation, my JB ambient ranges from below zero to just over 100 degrees.

Be advised, the exhaust air never reaches 375 degrees. The figure of 375 applies to the Onan sensor which monitors the temperature of the exhaust manifold which is obviously much much hotter that the air flowing over it. I am sure Onan did not want false shut downs due to a hot day in Texas, for example. Also note, the Onan temperature controlled shutters restirct the exhaust cooling air and NOT the intake cooling air.
Reply With Quote
The Following User Says Thank You to Leon N. For This Post:
  #8  
Old 03-18-2017, 09:40:06 PM
oakyone oakyone is offline
Registered
 
Join Date: Mar 2017
Location: Sheridan, Oregon
Posts: 22
Thanks: 14
Thanked 0 Times in 0 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Wow. Thanks everyone for responding so soon. I've already read a lot about these old Onans here and it's VERY helpful. I love old machines - new stuff usually isn't built to as high a standard.

375F seems reasonable (for overheat sensor) if it's mounted right to the exhaust manifold. I'm in western Oregon, so it rarely gets to 100F here and very rarely down to 0F or below.

Sounds like a two wire oil pressure switch should be pretty simple to install along with the overheat switch in the same circuit.

The unit has a solenoid valve between the two propane regulators. (Not sure why it has two, but it runs well.) The right hand switch on the control panel energizes this valve, but the set runs and starts fine weather it's on or off. Curious.

When I get a chance to work on it more, I'll update my progress. Any additional feedback on the exhaust manifold temp would be appreciated. Of course, 375F is WAY to hot for the air leaving the shutters.

Click image for larger version

Name:	0317171708.jpg
Views:	79
Size:	71.3 KB
ID:	277879

Click image for larger version

Name:	0317171708a.jpg
Views:	68
Size:	98.5 KB
ID:	277880

Click image for larger version

Name:	0317171709.jpg
Views:	94
Size:	96.8 KB
ID:	277881

Click image for larger version

Name:	0317171710.jpg
Views:	71
Size:	85.1 KB
ID:	277882
Reply With Quote
  #9  
Old 03-18-2017, 09:46:50 PM
oakyone oakyone is offline
Registered
 
Join Date: Mar 2017
Location: Sheridan, Oregon
Posts: 22
Thanks: 14
Thanked 0 Times in 0 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

One thing I forgot. It's my understanding the generator has built in protection in the control box. I want to protect the wire feeding out of the gen set, but do I have to worry about overload to the generator? I know a standard circuit breaker is very unlikely to trip, because the set can't hit the high inrush like main power.
Reply With Quote
  #10  
Old 03-18-2017, 09:56:19 PM
KPack KPack is offline
Subscriber
 
Join Date: Feb 2016
Location: Bryan, Texas
Posts: 413
Thanks: 1,260
Thanked 356 Times in 174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Make sure you have the right coil resister or non resister read the wiring schematic to see if yours has the resister or not made my Jc run better when I got the right one.
Reply With Quote
  #11  
Old 03-18-2017, 10:01:57 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,423
Thanks: 634
Thanked 1,959 Times in 1,174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

No that is not correct. There is no generator overload protection built into the control box. The control box only controls the JC engine side of the machine. You must provide your own generator over load protection external to the machine. Need the services of an electrician for this.

BTW! Looks like some one re labeled the remote vs hand crank ( local start) switch as an on/off switch. It must never be left on when the generator is stopped.

And Yes, the hot air discharge will never reach 375 degrees.
Reply With Quote
  #12  
Old 03-18-2017, 10:14:31 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,717
Thanks: 4,951
Thanked 5,252 Times in 2,873 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Quote:
Originally Posted by oakyone View Post
Sounds like a two wire oil pressure switch should be pretty simple to install along with the overheat switch in the same circuit.

The unit has a solenoid valve between the two propane regulators. (Not sure why it has two, but it runs well.) The right hand switch on the control panel energizes this valve, but the set runs and starts fine weather it's on or off. Curious.
The first regulator is a pressure regulator. The second is the "demand regulator" which is not a "pressure regulator", but a flow regulator. The demand regulator opens with vacuum from the intake manifold through the carb. (I caused a stir awhile back by saying "vacuum from the carb.).

Onan used a one wire N/O pressure switch (close at 15 psi).
Reply With Quote
  #13  
Old 03-18-2017, 10:38:53 PM
oakyone oakyone is offline
Registered
 
Join Date: Mar 2017
Location: Sheridan, Oregon
Posts: 22
Thanks: 14
Thanked 0 Times in 0 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Leon N.

Why is the remote vs hand crank switch making the solenoid between the regulators click? Is the start stop switch located under the little door in the top end of the housing (not the one on the control panel) a remote start stop? Both of these start and stop the engine whether that right hand toggle is off or on. I'm confused.
Reply With Quote
  #14  
Old 03-18-2017, 11:18:56 PM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,138
Thanks: 4,688
Thanked 959 Times in 644 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

I believe when in the hand crank position, it powers everything to make the generator run so that means, you are putting 12 volts to the gas shut off valve as well as voltage to the coil and points all the time it is in the hand crank position wheter the engine is running or not, therefor if left in hand crank and the engine is not running, you will burn up the points and maybe the coil and you will drain the battery.
When you toggle the start/stop toggle switch to start the generator, it activates everything I mentioned above however when you let off the switch it returns to center, the run relay inside the control box is activated which then keeps the generator running

I do not know anything about the start/stop under the little door, others will chime in on that.

Last edited by nothingbutdarts; 03-18-2017 at 11:29:07 PM. Reason: added info
Reply With Quote
  #15  
Old 03-19-2017, 12:54:34 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,423
Thanks: 634
Thanked 1,959 Times in 1,174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Post 13. That switch on the right should be labeled "electric start" in the upper position and "hand crank" in the lower position. No matter what position that switch is in, you must activate the left side switch to start the JC or even stop the JC. Refer to the owners manual and 967-500. Not sure what you mean by the little door in the top end of the housing? Please show us a picture. sounds like there is a third switch which may be an extension of the start/stop switch you showed in post 8.

Geeze can't sleep. One more thing. That picture you show in post 8 of the output wiring from the generator. make sure the generator power lead T2 is Grounded to the chassis before you apply 12 VDC to crank the JC or you may damage the Magneciter back end. I suspect behind that lower plate I am referring to probably hides the generator power output 4 wires. Good night.

Last edited by Leon N.; 03-19-2017 at 01:15:59 AM. Reason: More info
Reply With Quote
  #16  
Old 03-19-2017, 01:12:23 AM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,138
Thanks: 4,688
Thanked 959 Times in 644 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Leon, I believe he is asking about the switch under the little door on the rear of his machine, it's the switch shown in the 3rd picture down in his post #8
Reply With Quote
  #17  
Old 03-19-2017, 03:17:18 AM
JohnnyC JohnnyC is online now
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 3,850
Thanks: 1,088
Thanked 1,751 Times in 1,037 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Quote:
Originally Posted by Leon N. View Post
Geeze can't sleep.
--- snip ---
Good night.
Same here, can't sleep either. It is 3:13 am. Last pot of coffee was at 10:15 pm and I knew that was too late. No I am paying for it......

Quote:
Originally Posted by nothingbutdarts View Post
Leon, I believe he is asking about the switch under the little door on the rear of his machine, it's the switch shown in the 3rd picture down in his post #8
That is another switch for starting. It is practical especially when the enclosure is shut closed.

JohnnyC
New Jersey
Reply With Quote
  #18  
Old 03-19-2017, 07:25:03 PM
oakyone oakyone is offline
Registered
 
Join Date: Mar 2017
Location: Sheridan, Oregon
Posts: 22
Thanks: 14
Thanked 0 Times in 0 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Okay, I'll post just the pic with the extra start/stop switch here.

https://www.smokstak.com/forum/attac...1&d=1489887367

It's under the little door at the top.

If that solenoid is supposed to shut off the propane, it's not working. The unit runs well whether it's energized or not. I'll also trace the wires from the switch in question tomorrow.

I'll re-read the manual and try to find out more about the electric start/hand crank. I didn't think the JC had any provision for hand cranking.

---------- Post added at 04:12:47 PM ---------- Previous post was at 04:09:02 PM ----------

That is another switch for starting. It is practical especially when the enclosure is shut closed.

JohnnyC
New Jersey[/QUOTE]

Yes. Is it the same as a remote start switch? Is a remote start switch just wired to the same terminals as the main one on the control panel?

Thanks everyone for the help!

---------- Post added at 04:25:03 PM ---------- Previous post was at 04:12:47 PM ----------

Geeze can't sleep. One more thing. That picture you show in post 8 of the output wiring from the generator. make sure the generator power lead T2 is Grounded to the chassis before you apply 12 VDC to crank the JC or you may damage the Magneciter back end. I suspect behind that lower plate I am referring to probably hides the generator power output 4 wires. Good night.[/QUOTE]

Yes, the main leads are in the box just below the control panel. T1 and T4 each go to one of the fuses in the old school disconnect box. (Above and to the left of the magnaciter.) T2 and T3 are grounded to the chassis in the same disconnect box. I checked that it was wired to match the diagram from the Onan manual and on the lid of the junction box, but I didn't know about the 12 volt damage possibility. Thanks for the tip.
Reply With Quote
  #19  
Old 03-19-2017, 07:28:12 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,423
Thanks: 634
Thanked 1,959 Times in 1,174 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Wrong! The JC did have provisions for a hand crank starting method. Take a look, for example, at the wiring diagrams on pages 86 & 87 in 967-500.
Reply With Quote
  #20  
Old 03-19-2017, 07:40:51 PM
oakyone oakyone is offline
Registered
 
Join Date: Mar 2017
Location: Sheridan, Oregon
Posts: 22
Thanks: 14
Thanked 0 Times in 0 Posts
Default Re: Onan 12.5JC-3CR, Questions, Just purchased

Okay, the lid of the junction box says "CAUTION T2 MUST BE GROUNDED"
Now I get it!

---------- Post added at 04:40:51 PM ---------- Previous post was at 04:29:17 PM ----------

Okay, now I see there is provision for hand cranking. I suppose that could come in handy if you didn't have a way to jump it, or the starter went gunny-bag when you needed emergency power. Now I'll have to shop for a J series hand crank!

I'm going to have to try and get to the bottom of this propane solenoid. It's not shutting the fuel off, if that was it's purpose.
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 12.0 DJC Parts purchased question Tony Clever Onan Generators 9 06-16-2016 09:04:40 PM
Onan 5.0 CCK 3CR recently purchased, have a couple questions Lurch Onan Generators 23 11-25-2015 12:09:26 AM
Onan 4.0 CCK purchased on CL taylorlift Onan Generators 23 12-26-2014 05:37:00 PM
Onan DJB Genset - Just Purchased keeper Onan Generators 22 12-02-2014 02:07:39 AM
Second PE-197 purchased macjeeper Military MEP and Aircraft Gen-Sets 4 01-23-2012 02:47:26 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 10:34:39 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277