Wiring up 6.5NH (Backfeed Discussion)


this thread has 17 replies and has been viewed 451 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-20-2017, 03:47:36 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Wiring up 6.5NH (Backfeed Discussion)

OK - so I spoke with a local electrician and he mentioned that the most economical way for me to hook into my setup based on how my boxes are set up (primary mains box and a sub panel in the garage) would be to add a breaker to the main box and backfeed into that rather than going with an external transfer switch. Per code here it is OK as long as precautions are taken to prevent both power sources from being live at the same time. This kit seems to resolve that (http://www.geninterlock.com/product/...ansfer-switch/).

So I wanted to run my plans by everyone here based on my discussion with him as I also value everyone's input here. I have a 6.5NH that will be pushing 4-wire 120v out:

- Add a breaker to the main panel (dual 30-amp, one for each leg) for the generator to hook into
- Add the above linked generator interlock physical lock-out
- 30-40 foot run of #8 4-wire out to the generator pad (he recommended buried conduit as well as #8 in case I ever wanted to upgrade the generator to a higher-KW unit.
- In the same conduit, I would have a #14 3-wire hooked into the same panel (but obviously a different breaker) to feed a battery minder when on utility power.

And apparently reading up online I can probably do the work in the main box myself. I was a bit sheepish at first but it looks like all the connections are on the lower side (since it is an outdoor box) so I won't be getting my hands up near the mains... am I crazy?
Reply With Quote
Sponsored Links
  #2  
Old 03-20-2017, 03:59:43 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 15,365
Thanks: 7,782
Thanked 12,530 Times in 5,913 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

In one word YES. You never want to work on a live system. One slip and you will find out why. I have never worked on a live system. Unless it was a system that could not be shut down. Hospital,nursing home,military base and so on. Then I had my hot gloves,rubber mats,hot blankets and a rope around me. So my helper could pull me off

You do not want to do this yourself. Because if something goes wrong and insurance company finds out you did the work. Insurance will be canceled leaving you to pay for ALL damage. Hire a qualified person,have an inspector sign off on it.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 2 Users Say Thank You to Billy J Shafer For This Post:
  #3  
Old 03-20-2017, 04:13:52 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by Billy J Shafer View Post
You do not want to do this yourself. Because if something goes wrong and insurance company finds out you did the work. Insurance will be canceled leaving you to pay for ALL damage. Hire a qualified person,have an inspector sign off on it.
Good enough reason. I can definitely bring them out to do the box install. Do the other portions sound reasonable?
Reply With Quote
  #4  
Old 03-20-2017, 05:12:28 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 15,365
Thanks: 7,782
Thanked 12,530 Times in 5,913 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Sounds fine to me. But it will need to comply with the local codes.

I was involved in a case down here. Man backfeed through the dryer plug. Then left to go to town. Fire got started. By the time it was all over. His bill was over 1.4 million. He had to pay. He lost everything just to pay the bill.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 3 Users Say Thank You to Billy J Shafer For This Post:
  #5  
Old 03-20-2017, 05:27:17 PM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 4,033
Thanks: 849
Thanked 3,731 Times in 1,577 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

This probably will work for you.
http://www.interlockkit.com/
Reply With Quote
  #6  
Old 03-20-2017, 05:32:28 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by I like oldstuff View Post
This probably will work for you.
http://www.interlockkit.com/
I saw that one first and that got me searching. The one I linked to is actually very similar but less expensive! Much cheaper than a transfer switch.
Reply With Quote
  #7  
Old 03-20-2017, 05:50:30 PM
LRomero LRomero is offline
Subscriber
 
Join Date: Jun 2016
Location: New Iberia, Louisiana
Posts: 251
Thanks: 27
Thanked 68 Times in 40 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Have you guys seen the electric meter interlock version? Don't know the pricing, just came across this last week when I was looking at ATS'.

http://www.generlink.com/about_generlink.cfm
Reply With Quote
  #8  
Old 03-20-2017, 06:15:46 PM
RETCPO RETCPO is offline
Registered-II
 
Join Date: Sep 2010
Location: Hampton, VA USA
Posts: 481
Thanks: 172
Thanked 273 Times in 187 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

GenerLink will only be marketed to electric utilities to resell to their residential customers.

http://www.generlink.com/about_pepcotech.cfm
Reply With Quote
  #9  
Old 03-20-2017, 08:43:47 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,414
Thanks: 67
Thanked 1,174 Times in 963 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Upgrade the 14-3 to 12 gauge. Cost a few $ more but has a lot more capacity.

If you have a main breaker, I see little danger to you working in the box below it when it is shut off.
Reply With Quote
The Following User Says Thank You to Jim Rankin For This Post:
  #10  
Old 03-20-2017, 08:57:30 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by Jim Rankin View Post
Upgrade the 14-3 to 12 gauge. Cost a few $ more but has a lot more capacity.

If you have a main breaker, I see little danger to you working in the box below it when it is shut off.
Thanks for the tip. That was my thought re: the box. The only live item would be above the main breakers, and I would not be going up there. I'm pretty meticulous and don't mess around. I also plan to never run my unit when I'm not home.

I can appreciate both sides of the fence!
Reply With Quote
  #11  
Old 03-20-2017, 09:02:39 PM
Jim McIntyre's Avatar
Jim McIntyre Jim McIntyre is offline
Subscriber
 
Join Date: Nov 2004
Location: Mooresville, Indiana, USA
Posts: 3,621
Thanks: 571
Thanked 1,838 Times in 1,098 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by AppleTech View Post
...

So I wanted to run my plans by everyone here based on my discussion with him as I also value everyone's input here. I have a 6.5NH that will be pushing 4-wire 120v out:

- Add a breaker to the main panel (dual 30-amp, one for each leg) for the generator to hook into
- Add the above linked generator interlock physical lock-out
- 30-40 foot run of #8 4-wire out to the generator pad (he recommended buried conduit as well as #8 in case I ever wanted to upgrade the generator to a higher-KW unit.
- In the same conduit, I would have a #14 3-wire hooked into the same panel (but obviously a different breaker) to feed a battery minder when on utility power....
"4-wire 120v"? What's that?

IF you mean 3-wire 120/240 (Two hot lines plus one neutral) then OK.

Keep in mind the neutral does not connect to the chassis of the genset at the genset. The neutral wire from your genset connects only to your neutral bus bar in the main box. The chassis of the genset gets 'grounded' to the main panel through the bare (or green) #8 ground wire.
Reply With Quote
  #12  
Old 03-20-2017, 09:08:02 PM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 15,365
Thanks: 7,782
Thanked 12,530 Times in 5,913 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

The reason I say to kill all power. It's not easy to go into a power panel. Where someone has lost an arm and your job is to clean out the mess.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
  #13  
Old 03-20-2017, 10:38:43 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by Jim McIntyre View Post
"4-wire 120v"? What's that?

IF you mean 3-wire 120/240 (Two hot lines plus one neutral) then OK.
Yes sorry I meant 4 wire including the ground but you're right 3 wire is what I meant!
Reply With Quote
  #14  
Old 03-21-2017, 12:02:40 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 2,477
Thanks: 2,876
Thanked 973 Times in 684 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

120 volts won't make a mess or make you lose any limbs. It'll just stop your heart.

So be careful not to touch anything that's energized.

Last edited by Vanman; 03-21-2017 at 01:31:28 AM.
Reply With Quote
  #15  
Old 03-21-2017, 07:41:59 AM
I like oldstuff I like oldstuff is offline
Subscriber
 
Join Date: Jan 2012
Location: Milwaukee, Wisconsin, USA
Posts: 4,033
Thanks: 849
Thanked 3,731 Times in 1,577 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

The Generlink is a neat device. They won't allow them here so I called the utility and asked why. They don't want the extra length hanging on the meter socket which could cause damage if you push down on it. ..Lame...
Reply With Quote
  #16  
Old 03-21-2017, 02:10:47 PM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 57
Thanks: 1
Thanked 12 Times in 5 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

OK I called my local Building/Codes folks. They said the only thing I will need a permit for is generator connection if I don't bury any lines - If I run them along the exterior of the house to the generator I won't need permits/inspection for that portion.

I spoke with the state inspector and he was intrigued by the generator interlock device and said it sounded like it met the requirements of preventing backfeed and thought it sounded like a really neat solution.
Reply With Quote
The Following User Says Thank You to AppleTech For This Post:
  #17  
Old 03-22-2017, 03:44:45 AM
lokay5's Avatar
lokay5 lokay5 is offline
Subscriber
 
Join Date: May 2007
Location: Merlin, Oregon
Posts: 1,247
Thanks: 3,215
Thanked 723 Times in 456 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Keep in mind -

The GenerLink site says -

Quote - GenerLink™ is installed by your local electric utility in less than 30 minutes. Unquote

Quote:
Originally Posted by I like oldstuff View Post
The Generlink is a neat device. They won't allow them here so I called the utility and asked why. They don't want the extra length hanging on the meter socket which could cause damage if you push down on it. ..Lame...
Considering the average consumer, it makes perfect sense to me.
Reply With Quote
  #18  
Old 03-22-2017, 10:03:57 AM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 1,140
Thanks: 343
Thanked 291 Times in 214 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

And it's only good for 30 amps (per their spec sheet).

Quote:
Originally Posted by RETCPO View Post
GenerLink will only be marketed to electric utilities to resell to their residential customers.

http://www.generlink.com/about_pepcotech.cfm
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Vintage ad of the day discussion? 73eldo Antique Gas Engine Discussion 3 01-02-2013 11:50:14 PM
With all the discussion about painting engines... David Steam Stationary Engines, Traction Engines, Steam Boats 2 05-06-2010 08:26:09 PM
Backfeed Disaster Almost 2cubs2cases Onan Generators 13 08-06-2009 09:05:27 PM
Reverse Discussion Ray Wangler Steam Stationary Engines, Traction Engines, Steam Boats 41 08-22-2006 09:53:56 PM
What would you do? (eBay Discussion) Smoke eBayŠ Auction Discussion 16 11-15-2004 09:54:11 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:56:08 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277