Go Back   SmokStak > SmokStak® Vintage Electrical Equipment > Generators & Electric Motors General Discussion > Generac Generators (SEARS, etc.)
Generac Generators (SEARS, etc.) Restoring, maintaining and operating Generac generators.
Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts
this thread has 1 replies and has been viewed 96 times
Old 06-12-2019, 11:17:07 AM
James A. B. James A. B. is offline
Angry Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts
Generac Guardian Standby Generator
(model)item#:0041094, s/n:35254444,volts:120/240, amps:66.6/33.3, watts:8000
My Generac generator (when rocker switch is set to manual) starts, runs for maybe 10 seconds then shuts down, restarts (on it's own) and shuts down again in lesser time. These are the same symptoms as if the High Temperature Sensor would be faulty. History- I have had trouble with the Low Oil Pressure Sensor, the High Temperature Sensor and the main Regulator from the propane tank.
These problems occurred in a short period of time, couple months each and after each issue the generator worked fine after faulty part replacement. My current problem has the same symptoms as if the High Temperature Sensor is bad but there are there aren't any Fault LED's lit. When the ambient temperature would get hot enough the generator would stay running as if there isn't any problems. I have connected a Water Column Gauge to the demand regulator (internal regulator thats connects to the carburetor) and the Gauge reads 11.5" to 12" Water Column which is the proper pressure. For fuel I use a 7 gallon propane tank and have been using that size tank for 8 years without any problems. I have researched this problem through the internet and have not found any answers or anybody else having this problem. It definitley has me baffled and I would truly appreciate anybodys input. Thanks
Old 06-12-2019, 12:04:44 PM
Email NOT Working
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts
Is it putting out voltage during the short time it runs? Some of these will shut down if they don't see voltage output and restart in hopes of exciting the field again.
Generac 0047000: Shuts Down After AC Runs for a Few Minutes Danceswithbeercans Generac Generators (SEARS, etc.) 11 07-24-2018 02:52:19 AM
17kw generac starts and shuts down after 2 sec wstang254 Generac Generators (SEARS, etc.) 11 11-21-2012 11:50:30 AM
Generac 17kw starts n shuts down wstang254 Generac Generators (SEARS, etc.) 13 11-17-2012 04:00:59 AM
Onan 6.5MCCK-3CR/1H Starts runs for 45 seconds and shuts off truk911 Onan Generators 4 10-16-2011 03:47:58 PM
Onan 4.0 BFA runs and dies but restarts r68grumpy Onan Generators 9 04-28-2010 10:34:13 AM