Kohler 23eoz 230v generator decides it's a 400v generator


this thread has 21 replies and has been viewed 1456 times

Reply
 
Thread Tools Display Modes
  #1  
Old 07-30-2016, 04:10:26 PM
haveaday haveaday is offline
Registered
 
Join Date: Jul 2016
Location: Chicago, Illinois, USA
Posts: 9
Thanks: 1
Thanked 0 Times in 0 Posts
Default Kohler 23eoz 230v generator decides it's a 400v generator

Hello,

I've come here looking for some help. I have a Kohler 23eoz marine generator that has suddenly started producing 400v instead of 230v. Most of the service facilities listed by Kohler marine are general purpose marine mechanics. They've tried thus far by just replacing parts not diagnosing the problem. I'm a little afraid of what that's going to cost me in parts, labor and time by the time they've fixed it.

Here's what I posted on one of the marine forums, just wondering if anyone here has any ideas.

Last sunday my 2003 Kohler 23eoz with about 1100 hours on it decided it was no longer a 240v generator and instead a 400v generator. It was putting out 199v per leg. This unfortunately resulted in frying two of my air conditioning units and two battery chargers.

I called the yard I use for service who dispatched a technician and in working with Kohler decided the generator needed a new rectifier. The board cost about $230 and my pessimism quickly kicked in. Rarely does a $230 part fix anything I break (or so I feel.) So today the part was replaced and low and behold the generator still produces a stead 400v. Now they are jumping to thinking the windings are the problem and it could need a new stator.

Im wondering if others have come across this and might have any ideas about what would cause the generator to produce a seemingly stable 400v. I"m wondering if the governor could have failed. I wouldnt think the voltage regulator would be in play because I wouldnt expect a healthy generator to produce 400v at any time.

Thoughts? Ideas? Random tests I can try? Anyone know of a good stepdown transformer from 400v to 240? Kidding....

Im a little punch drunk from a day of replacing the failed components in my AC system. That is now all back together but Id like to get the generator straightened out before I fry another bunch of equipment.

Thanks!

Ben
Reply With Quote
Sponsored Links
  #2  
Old 07-30-2016, 04:45:00 PM
len k len k is online now
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 16,915
Thanks: 485
Thanked 6,177 Times in 4,488 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Don't know kohler, but on Onans when the rotor or stator windings short gen usually makes less voltage output, not more. So I suspect it's not a winding short

My Guess is AC voltage reg (if it has one) has shorted and is applying full voltage to the feild. Or maybe reg sense leads to 120V have opened or are bad connection. Other posibility is gen gov is stuck and allowing engine to run at a much higher rpm than normal.

Gens without an inverter run at a constant rpm at all times to make a steady 60hz. If rpm is high then voltage will be too, unless it has a voltage reg to compensate for that. Might try measuring HZ , most people here use a $25 killawatt meter for that ( home depot).

Might need to use a step down transformer to run the killawatt meter at ~ 125 volt max. Or make a voltage divider from pair (or several) lightbulbs in series. My killawatt displays hz accurately down to ~ 70-80 VAC , below that display fades out to unreadable.

Other guys here know Kohler.

Last edited by len k; 07-30-2016 at 05:18:32 PM.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #3  
Old 07-30-2016, 05:18:38 PM
haveaday haveaday is offline
Registered
 
Join Date: Jul 2016
Location: Chicago, Illinois, USA
Posts: 9
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Thanks very much for the info. I've read the procedure for testing the voltage regulator unfortunately I don't have a variac with which to test. I'll start by testing the frequency of the power coming out of the generator. From there it sounds like I need a way to bench test the VRM. I'll figure that out.

Thanks
Ben
Reply With Quote
  #4  
Old 07-30-2016, 05:23:25 PM
len k len k is online now
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 16,915
Thanks: 485
Thanked 6,177 Times in 4,488 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

I don't know how Kohler is wired , you have to look at the wiring , but If voltage reg has a voltage adjustment pot, you might try following: Instead of using a variac to vary sense input voltage to reg, feed sense leads 120V utility power and vary voltage adjust pot and see if voltage across the field leads responds **. Would expect for convenience you can do this with a substitute load for field on the reg instead of actual field winding .

Be careful with utitlty power, don't touch the leads. no isolation.

**tip of the hat to Jim McIntyre for this technique
.

Last edited by len k; 07-31-2016 at 01:18:51 AM.
Reply With Quote
  #5  
Old 07-30-2016, 09:42:24 PM
haveaday haveaday is offline
Registered
 
Join Date: Jul 2016
Location: Chicago, Illinois, USA
Posts: 9
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

It does indeed have a voltage pot. I'll try the test like you describe and see if I can get any variability out of it.

One thing I've been thinking about and not sure I know the answer but perhaps others do.... The generator appears to be producing 399v right now. Is it possible that the unregulated voltage would be this high? This seems like surprisingly high voltage for a generator designed to produce 230v.

Thanks
Ben
Reply With Quote
  #6  
Old 07-30-2016, 09:57:05 PM
len k len k is online now
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 16,915
Thanks: 485
Thanked 6,177 Times in 4,488 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

No idea about a Kohler.
But on an Onan 6.5 kw NHE type rotor excitation voltage ( from reg) is ~ 18-60 VDC, while typical is 36. I think it only goes to 60 when it's fully loaded or a heavy full load is suddenly applied.

So seems there is some posibility of a very high voltage if reg fails at full output. Heard military gen regs are designed to fail at full output.

If rpm is also high that can contribute to higher voltage too.

----------------

Just occurred to me, the pots may be dirty/bad. With reg installed in gen move the pot through its full range of adjustment several times. That sometimes gets onan regs working temporarily.

If you have a volt meter on gen output while you are adjusting the pots, if the voltage makes sudden jumps all over the place, then the pots are likely dirty. If you are handy with a soldering iron you can solder in some new pots.

Last edited by len k; 07-30-2016 at 10:40:27 PM.
Reply With Quote
  #7  
Old 07-30-2016, 10:29:19 PM
haveaday haveaday is offline
Registered
 
Join Date: Jul 2016
Location: Chicago, Illinois, USA
Posts: 9
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Quote:
Originally Posted by len k View Post

----------------

Just occurred to me, the pots may be dirty/bad. With reg installed in gen move the pot through its full range of adjustment several times. That sometimes gets onan regs working temporarily.
I'll give that a whirl and see if it helps.

Thanks!
Reply With Quote
  #8  
Old 07-31-2016, 08:22:51 AM
Kevin K Kevin K is offline
Registered-III
 
Join Date: Jan 2005
Location: upstate New York USA
Posts: 3,910
Thanks: 3,565
Thanked 4,066 Times in 2,138 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Get a copy of the service manual. Without this documentation everything you do is guess work. If you don't have one, you can download a copy here:

http://www.manualslib.com/manual/105...ler-13eoz.html

This manual, TP6071, covers models 13eoz to 24eoz.

You need to verify the engine is running at 1800RPM. The easiest way to do that is to connect a voltmeter that can read frequency and check the output. It should be about 60Hz.

When you have verified the engine speed is correct, look on page 29 of the service manual and perform the separate excitation test. Let us know the results.
Reply With Quote
  #9  
Old 07-31-2016, 09:08:58 AM
haveaday haveaday is offline
Registered
 
Join Date: Jul 2016
Location: Chicago, Illinois, USA
Posts: 9
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Thanks,

I do indeed have a copy of the service manual. I'll start with the frequency test and move on from there.

Ben
Reply With Quote
  #10  
Old 07-31-2016, 10:27:46 AM
LWB250 LWB250 is offline
Registered-III
 
Join Date: Oct 2008
Location: Tampa, FL USA
Posts: 1,394
Thanks: 27
Thanked 437 Times in 378 Posts
Default Re: Kohler 23eoz 230v generator decides it's a 400v generator

Check speed first. 1800 rpm = 60 Hz.

From there you're going to want to check the sensing voltage to the regulator. This will be a direct connection from the output leads which are wires 3 & 4, which go to the terminals #2 & #3 on the regulator from the looks of the manual.

You should have whatever output voltage is on the sensing terminals. If output is 400 volts, you should see 400 volts. If it's 120 volts, you should see 120 volts. If you see nothing, that's why your generator is putting out 400+ volts. Here's why:

The regulator uses the sensing voltage to "see" what the output of the generator is. If sensing voltage is low, the regulator increases the output. This would be analogous to turning on an AC unit and having the voltage drop as a result. The regulator sees the voltage drop and sends more power to the generator via the exciter to produce more power to accept the AC load.

If the sensing leads are broken, disconnected, or there is an open circuit of some sort, the regulator sees 0 volts. Since it thinks the generator isn't producing any voltage, it goes full field, or, in a simpler sense, it "steps on the gas" to get the generator to produce more output. As a result of this condition the generator produces the maximum amount of power it can, which can be in excess of 400 volts.

If you start the unit up and see 400 volts on the sensing leads, the regulator is most likely at fault. It's going full field for no reason, in other words, it's stuck with it's foot on the gas.

To confirm this is the case, you could disconnect the exciter fields, which appear to be terminals #7 & #8 on the voltage regulator to remove all power from the generator. With the exciter disconnected, the generator should produce no power other than residual, which would be in the range of a few volts.

Hope this helps. It's certainly not rocket science.

Dan
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler Kohler 300W Belt Generator Heelerman Kohler Generators 3 10-09-2014 10:46:38 AM
Rewiring Generator from 230v to 110v JaimeRusso Generac Generators (SEARS, etc.) 6 01-12-2011 10:03:24 PM
ID kohler generator jima4624 Kohler Generators 1 09-20-2010 08:52:25 AM
kohler generator steve hawes Kohler Generators 0 04-05-2002 08:21:28 PM
Witte decides to run today... John Crist Antique Engine Archives 1 07-08-2000 07:57:31 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 02:02:04 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277