Onan Generators

Onan 7.5JB Centrifugal switch HELP!


this thread has 31 replies and has been viewed 2081 times

Reply
 
Thread Tools Display Modes
  #11  
Old 10-30-2013, 07:06:12 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,956
Thanks: 5,250
Thanked 5,646 Times in 3,017 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

Does the nylon plunger move back when the engine starts & comes up to speed?
You might try it with the rubber boot removed, so you can see the plunger better. It may leak a little oil, but should not be much.
Reply With Quote
Sponsored Links
  #12  
Old 10-30-2013, 08:44:44 PM
gov2mod gov2mod is offline
Registered
 
Join Date: Oct 2013
Location: Dover, DE
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

I'll have to look in the next couple of days. I had surgery on my right hand last week and the stitches come out soon so I hope to get greasy again working on my 1001 projects.
Reply With Quote
  #13  
Old 08-12-2017, 11:47:29 PM
silverlake82 silverlake82 is offline
Registered
 
Join Date: Aug 2017
Location: Stockton, California
Posts: 10
Thanks: 11
Thanked 1 Time in 1 Post
Default Re: Onan 7.5JB Centrifugal switch HELP!

I am new to this so forgive me if I post this wrong. I have the same issue with the centrifugal disconnect switch. Having difficulty finding a drawing or part #.
Also, is there an option to bypass this switch another way. Thanks.
Reply With Quote
  #14  
Old 08-12-2017, 11:56:23 PM
JohnnyC JohnnyC is offline
Subscriber
 
Join Date: Jun 2014
Location: Boonton, New Jersey
Posts: 4,943
Thanks: 1,733
Thanked 2,481 Times in 1,430 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

Hi SilverLake82 and welcome aboard! To get the fastest and most accurate responses, please start a new thread (topic listing) and include the full model and serial number along with the problems details (more details the better). Pictures are a great help too in many cases. You will have fast responses from the smart guys here (I'm only a smart azz ).

JohnnyC
New Jersey
Reply With Quote
The Following 2 Users Say Thank You to JohnnyC For This Post:
  #15  
Old 08-13-2017, 01:00:30 AM
Motorhead's Avatar
Motorhead Motorhead is offline
Subscriber
 
Join Date: May 2007
Location: Central Coast, California
Posts: 3,895
Thanks: 1,825
Thanked 2,693 Times in 1,395 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

Starting your Onan isn't like you would start a car. I was always told let off of the starter position as soon as the car engine fired up or "You'll RUIN the starter!"
On the generators with the centrifugal points, you have to hold the start button until the engine picks up speed and the points will cancel the starter. It is a hard thing to get used to but that seems the way they were designed. Having your engine tuned right so it starts and comes up to RPM will make it seem like you don't have to hold the start button so long.
__________________
The Control panel
and gauges of my
7.5JB
Reply With Quote
The Following 7 Users Say Thank You to Motorhead For This Post:
  #16  
Old 08-13-2017, 07:46:08 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,947
Thanks: 712
Thanked 2,325 Times in 1,359 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

If I am remembering correctly, your problem may not be with the centrifugal switch, but the ignition start relay inside the control box. What is the condition of your control box? Maybe just a dirty ignition relay contactor. Max, check me out on this, am I correct? I have had similar problem, that is, it would fire up and then die when the start switch was released. I merely sprayed contact cleaner on that relay and wha la good for a few more years.
Reply With Quote
The Following 3 Users Say Thank You to Leon N. For This Post:
  #17  
Old 08-13-2017, 08:17:18 AM
Handyhiker1 Handyhiker1 is online now
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 772
Thanks: 423
Thanked 333 Times in 176 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

Leon, he says it stays running if he hold the switch closed.
Reply With Quote
  #18  
Old 08-13-2017, 10:26:23 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,947
Thanks: 712
Thanked 2,325 Times in 1,359 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

Handy hiker Yes that is because he is bypassing the start ignition relay. Once the plant reaches 900 rpm, the centrifugal switch closes and this starts off another chain of events, namely, it energizes the ignition relay which in turn disconnects the starting motor and the choke (if used). Then the operator releases the start switch which de energizes the start ignition relay and start solenoid.

So, I think he should study the Onan cycle diagram found on page 10 in the JB owners manual, 967-320 as well as the appropriate wiring diagram for his particular model. Good Luck.
Reply With Quote
The Following 2 Users Say Thank You to Leon N. For This Post:
  #19  
Old 08-13-2017, 11:16:15 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,147
Thanks: 8,876
Thanked 14,490 Times in 6,840 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

As Leon posted. On starting the run system is bypassed. When the switch closes it becomes another system. Run relay in control box takes over.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
The Following 2 Users Say Thank You to Billy J Shafer For This Post:
  #20  
Old 08-13-2017, 02:16:17 PM
Handyhiker1 Handyhiker1 is online now
Registered-II
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 772
Thanks: 423
Thanked 333 Times in 176 Posts
Default Re: Onan 7.5JB Centrifugal switch HELP!

I guess i just don't understand how it could be something other then the points if closing the points manually make it run and not closing the points make it die as soom as the start button is released.
If I understand the system right, holding the start button pypasses the points and lets it start. Then when runningcthe points should close and continue to run and also disengage the starter. What am I missing?
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan 7.5 jbfl centrifugal pts part #? Mikey NY Onan Generators 18 10-14-2013 07:47:06 PM
Onan 7.5 MDJE Centrifugal switch points gap FLracer Onan Generators 3 03-19-2013 08:25:55 PM
cummins onan 15JCL centrifugal switch lyonsden Multi-Cylinder Stationary Engines and Power Units 2 02-06-2013 10:45:37 PM
GE RS-IR Centrifugal Switch Problem desertoasis1 Generators & Electric Motors General Discussion 3 09-16-2009 03:14:20 PM
Centrifugal oil cleaners Robt. Antique Gas Engine Discussion 4 03-01-2007 02:48:25 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:59:41 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277