Default Re: Wiring up 6.5NH (Backfeed Discussion)

Thanks for the detailed write-up! I have #10 (10/4) running from the generator inlet box to the breaker box running to a dual 30-amp breaker. I'm OK getting a grounding rod and installing it at the generator chassis.

In the input box, the ground should connect from gen to box ground and to ground going into neutral bar in the main box? Here's how I'm envisioning the setup based on my understanding.

Also am I modifying the way neutral works in the NH such that it will no longer be able to be used standalone (which is OK)?

Reply With Quote
Sponsored Links
  #22  
Old 04-14-2017, 11:54:53 PM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 416
Thanks: 143
Thanked 74 Times in 39 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Quote:
Originally Posted by AppleTech View Post
In the input box, the ground should connect from gen to box ground and to ground going into neutral bar in the main box?

Also am I modifying the way neutral works in the NH such that it will no longer be able to be used standalone (which is OK)?
You are correct, regarding the grounding at the inlet box and the panel. The ground wire in the SOOW cord will effectively ground the generator when the L14-30 connector is mated to the inlet box.

Will you need the NH as a stand-alone generator, or will it be exclusively used as a home standby? If you keep the neutral and ground isolated at the generator, it will be easy enough to tie them together, if needed in the future.

Neutral/ground connections have been a hotly debated issue on this bulletin board as well as many other fronts in the electrical industry. The National Electrical Code is updated every three years. Many changes are initiated because an incident/accident happened. I have seen older standby generators (1980s and earlier vintage) that had a bolt stud factory welded to generator stator, with the generator's neutral leads connected to that bolt along with a lug for field wiring connections. There definitely wasn't any neutral/ground isolation on them.

BTW, nice job on your graphics.
Reply With Quote
  #23  
Old 04-15-2017, 12:15:40 AM
AppleTech AppleTech is offline
Registered-I
 
Join Date: Aug 2016
Location: Nashville, Tennessee, USA
Posts: 63
Thanks: 1
Thanked 13 Times in 6 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

I don't need it as a standalone I was just curious if I'd need to reconfigure it back should I choose to do so - sounds like I do.

Thanks for your advice!
Reply With Quote
  #24  
Old 04-15-2017, 02:13:13 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 2,590
Thanks: 3,011
Thanked 1,018 Times in 714 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

Steve, is the ground rod at the generator now required even when supplying a building where a main bonding jumper is installed, such as the OP's scenario?

I always thought that the ground rod was only required when the generator has a bonded neutral, and the building served doesn't, or at least that portion served by the generator doesn't and the transfer switch switches the neutral.

Or is this possibly just a local jurisdiction issue?

Keith
Reply With Quote
  #25  
Old 04-15-2017, 10:34:07 PM
Steve Dawkins Steve Dawkins is offline
Sponsor
 
Join Date: Feb 2005
Location: Virginia Beach, Virginia, USA
Posts: 416
Thanks: 143
Thanked 74 Times in 39 Posts
Default Re: Wiring up 6.5NH (Backfeed Discussion)

It's probably more of a local jurisdiction issue that morphed out of a manufacturer's installation diagram or recommendation. Some of the local cities wanted to see a ground rod at the generator, and others did not. The inspectors that did want a ground rod just checked to see if it was connected to the base or frame of the generator.

As we know, grounding electrodes (rods or otherwise) are not required for non-separately derived systems. NEC 250-54 does allow for "Auxiliary Grounding Electrodes" to be connected to the equipment grounding system for local earth reference or lightning protection.
Reply With Quote
The Following User Says Thank You to Steve Dawkins For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Vintage ad of the day discussion? 73eldo Antique Gas Engine Discussion 3 01-02-2013 11:50:14 PM
With all the discussion about painting engines... David Steam Stationary Engines, Traction Engines, Steam Boats 2 05-06-2010 08:26:09 PM
Backfeed Disaster Almost 2cubs2cases Onan Generators 13 08-06-2009 09:05:27 PM
Reverse Discussion Ray Wangler Steam Stationary Engines, Traction Engines, Steam Boats 41 08-22-2006 09:53:56 PM
What would you do? (eBay Discussion) Smoke eBayŠ Auction Discussion 16 11-15-2004 09:54:11 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 01:18:14 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277