Quote:
Originally Posted by Max Thompson View Post
That info is in #T-015 gaseous fuels manual. I think it is on the twainslan site.
It's there.
Ray

http://www.twinslan.net/~n0nas/manuals/onan/
Reply With Quote
The Following User Says Thank You to Ray Lynch For This Post:
Sponsored Links
  #102  
Old 04-15-2017, 11:47:47 AM
nothingbutdarts nothingbutdarts is offline
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 1,730
Thanks: 3,792
Thanked 672 Times in 477 Posts
Default Re: Quick help with Onan 12.5

Being I just had the T-015 manual out yesterday giving the propane company the consumption for a SK, I will post full load consumption for your 12.5 JC: 92 Cubic feet per hour propane and 228 cubic feet for natural gas.

Last edited by nothingbutdarts; 04-15-2017 at 01:18:53 PM. Reason: spelling
Reply With Quote
The Following 2 Users Say Thank You to nothingbutdarts For This Post:
  #103  
Old 04-15-2017, 12:00:14 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,991
Thanks: 318
Thanked 4,620 Times in 3,377 Posts
Default Re: Quick help with Onan 12.5

That's ~ 230k Btu/hr , which is about 2x as much as your house furnace uses.
Look at the gaseous fuel manual, you may have to increase your gas pipe diameter to fuel the gen , and have gas co change the flow restrictor in the meter outlet.

Or have gas co up it's pressure to 2 psi.

Last edited by len k; 04-15-2017 at 12:54:49 PM.
Reply With Quote
The Following User Says Thank You to len k For This Post:
  #104  
Old 04-15-2017, 02:40:30 PM
Handyhiker1 Handyhiker1 is offline
Registered-I
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 277
Thanks: 150
Thanked 79 Times in 54 Posts
Default Re: Quick help with Onan 12.5

I have a 1.5" main line with the boiler and hot water tank sharing a 1/2" line. The only other gas I use is for the burners on the stove, the oven is electric. I only need to run about 25' to the outside wall where the generator hook up will be. From the chart that I looked at in the T-015 manual (thanks for the info), it looks like 1" pipe will work in the house.
Reply With Quote
  #105  
Old 04-15-2017, 03:59:12 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,991
Thanks: 318
Thanked 4,620 Times in 3,377 Posts
Default Re: Quick help with Onan 12.5

1" pipe sounds small, but I haven't looked at manual.
Others know this stuff off the top of their head without looking in manual.
Reply With Quote
  #106  
Old 04-15-2017, 04:05:24 PM
Handyhiker1 Handyhiker1 is offline
Registered-I
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 277
Thanks: 150
Thanked 79 Times in 54 Posts
Default Re: Quick help with Onan 12.5

Quote:
Originally Posted by len k View Post
1" pipe sounds small, but I haven't looked at manual.
Others know this stuff off the top of their head without looking in manual.
I will recheck when I have a little more time to actually sit down and read it. Just took a quick glance today.
Reply With Quote
  #107  
Old 04-15-2017, 08:16:15 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,546
Thanks: 4,723
Thanked 4,997 Times in 2,768 Posts
Default Re: Quick help with Onan 12.5

Quote:
Originally Posted by len k View Post
1" pipe sounds small, but I haven't looked at manual.
30' of 1" BLK iron will deliver 377 CFH (377,000 BTU). Add 10' for each 90 degree turn, (going around a tee = a 90). Not knowing how long your run of 1 1/2" is, but "assuming 140 CFH for the boiler and 40 CFH for the water heater, I will bet you will be in good shape.

Double check the size of your existing trunk line. In my area, 1 1/2" (ID) is uncommon in a residential system, 1 1/4" was "standard" back in the old days and now we rarely run anything larger than 1". Commercial is a whole different game.
Reply With Quote
The Following User Says Thank You to Max Thompson For This Post:
  #108  
Old 04-16-2017, 08:24:50 AM
Handyhiker1 Handyhiker1 is offline
Registered-I
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 277
Thanks: 150
Thanked 79 Times in 54 Posts
Default Re: Quick help with Onan 12.5

My meter is right outside the front wall of the house and comes in the basement. It goes through 2 elbows to my main trunk line. it is all the same size at 1-1/2" pipe. The guy that built this house, we are the third owner, built it to commercial specs. I know that sounds weird but all of our 1st story floors are poured concrete with steel girders in the basement ceiling for support. I have no support posts in the basement. The basement walls are 18" thick and fire rated block, the upstairs walls are 2x6 stud plus brick and insulation board.
Reply With Quote
  #109  
Old 04-16-2017, 10:25:14 AM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,546
Thanks: 4,723
Thanked 4,997 Times in 2,768 Posts
Default Re: Quick help with Onan 12.5

Sounds like a "preppers" dream home.
Reply With Quote
  #110  
Old 04-16-2017, 11:44:22 AM
Handyhiker1 Handyhiker1 is offline
Registered-I
 
Join Date: Jul 2014
Location: Akron, Ohio
Posts: 277
Thanks: 150
Thanked 79 Times in 54 Posts
Default Re: Quick help with Onan 12.5

Quote:
Originally Posted by Max Thompson View Post
Sounds like a "preppers" dream home.
When we bought it, the neighbors called it the "bomb shelter house". Everything is poured concrete.
Reply With Quote
  #111  
Old 04-16-2017, 12:14:27 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 12,991
Thanks: 318
Thanked 4,620 Times in 3,377 Posts
Default Re: Quick help with Onan 12.5

Quote:
Originally Posted by Handyhiker1 View Post
Everything is poured concrete.
No termites.
Reply With Quote
The Following User Says Thank You to len k For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan Quick CCK remote prime question. Flintstone Onan Generators 41 02-19-2015 05:21:28 AM
Onan JC quick connect natural gas hose vlocci Onan Generators 9 09-15-2014 03:27:03 PM
Quick question on Onan DJB rcowboy Onan Generators 7 02-10-2013 04:38:03 PM
Found a good quick way to strip paint from an Onan CCK carburetor Motorhead Onan Generators 14 02-06-2013 03:21:37 AM
Need quick help!! Kman Oil Field Engines 4 02-03-2008 07:21:14 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:59:04 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277