  #41  
Old 03-18-2017, 05:53:27 PM
mheltunen mheltunen is offline
Registered-I
 
Join Date: Mar 2017
Location: Atlantic Mine, Michigan, USA
Posts: 87
Thanks: 56
Thanked 20 Times in 11 Posts
Default Re: Onan 7.5 JB-3CR running issue

That's for a different year. On my original post I have the name tag and I believe it said mine is a 1977 model
Reply With Quote
The Following User Says Thank You to mheltunen For This Post:
Sponsored Links
  #42  
Old 03-18-2017, 10:23:00 PM
Max Thompson Max Thompson is offline
Sponsor
 
Join Date: May 2009
Location: N.W. Missouri, USA
Posts: 5,924
Thanks: 5,213
Thanked 5,606 Times in 3,006 Posts
Default Re: Onan 7.5 JB-3CR running issue

The build sheet may have been used for several years for the same set configuration. The wiring diagrams were used for many years, you will sometimes see modification notes on them with dates far from the original drawing date.

If the model & spec. on the build sheet match your set, the wiring diagram listed on the sheet is correct.
Reply With Quote
The Following 2 Users Say Thank You to Max Thompson For This Post:
  #43  
Old 03-18-2017, 11:09:05 PM
mheltunen mheltunen is offline
Registered-I
 
Join Date: Mar 2017
Location: Atlantic Mine, Michigan, USA
Posts: 87
Thanks: 56
Thanked 20 Times in 11 Posts
Default Re: Onan 7.5 JB-3CR running issue

Diagram #612-4794 matches my set. My question/problem is the coil looks to be fed from 1 lead (#4 from tb12). Wires #5 and the wire leading from B terminal to the centrifugal switch have been cut and the switch was removed. Looking at the diagram I assume #4 wire is full voltage (12v) for starting and then once started it switches to #5 terminal on tb12 but I don't understand the routing to the coil. In my mind by looking at the schematic once relay k12 closes and energizes the #5 wire how does it reach the positive terminal of the ignition coil?

---------- Post added at 11:09:05 PM ---------- Previous post was at 11:02:21 PM ----------

And what is the function of the centrifugal switch? I'm slowly working my way thru this set and becoming more familiar with its circuits. Anyone with replys don't be afraid to "dumb it down" for me. Again all help is appreciated
Reply With Quote
  #44  
Old 03-19-2017, 12:01:52 AM
nothingbutdarts nothingbutdarts is online now
Sponsor
 
Join Date: Apr 2014
Location: Bailey, Colorado, USA
Posts: 2,602
Thanks: 5,789
Thanked 1,250 Times in 824 Posts
Default Re: Onan 7.5 JB-3CR running issue

The centrifugal switch is nothing more than a mechanical RPM sensing device, (before the days electrical magnetic pick-ups). It is installed on these generators I believe as a safety device, it will not let the generator stay running till it reaches about 900RPM, if it doesn't see 900RPM once you let off the start switch the engine will just die. Once the engine is running up to 1,800RPM and you walk away, if the engine should faulter and drop below 900RPM and not totally die it will again shut the engine off.

The starting sequence for a "J" line engine whether a JB or a JC is that, you hold the start/stop switch in the start position till you hear it get up to speed, once the centrifugal switch senses 900RPM it will automatically turn on the run relay, latching in the fuel shut off solenoid, powers the ignition coil and kicks out the starter.
Unlike a car when you turn the key to start and you hear the engine go to idle and just let off the key and it stays running, on the Onan, if you were to just let off the start switch the second you hear the engine start it would just die because the centrifugal switch has not yet sensed that the engine has reached 900RPM.
Reply With Quote
The Following 4 Users Say Thank You to nothingbutdarts For This Post:
  #45  
Old 03-19-2017, 07:56:25 PM
mheltunen mheltunen is offline
Registered-I
 
Join Date: Mar 2017
Location: Atlantic Mine, Michigan, USA
Posts: 87
Thanks: 56
Thanked 20 Times in 11 Posts
Default Re: Onan 7.5 JB-3CR running issue

So if I'm understanding correctly the 2 leads leading to the centrifugal switch make contact (via the switch) once it obtains 900 rpms. So for a possible testing scenario I could put a simple switch inline on the two wires and manually switch it over. Again this is not a permanent "fix" just one to tide me over until I find a centrifugal switch and cover. I also may need a 6v coil. How does one test the coil to make certain it is indeed faulty?
Reply With Quote
  #46  
Old 03-19-2017, 08:33:22 PM
fisherman81654 fisherman81654 is offline
Registered-I
 
Join Date: Oct 2015
Location: goodview, virginia
Posts: 93
Thanks: 102
Thanked 28 Times in 14 Posts
Default Re: Onan 7.5 JB-3CR running issue

Quote:
Originally Posted by mheltunen View Post
So if I'm understanding correctly the 2 leads leading to the centrifugal switch make contact (via the switch) once it obtains 900 rpms. So for a possible testing scenario I could put a simple switch inline on the two wires and manually switch it over. (Yes, but you have to remember to turn it off when you power down the unit.)









I also may need a 6v coil. How does one test the coil to make certain it is indeed faulty?
This should help http://gardentractorpullingtips.com/ignelect.htm
Reply With Quote
  #47  
Old 03-19-2017, 09:11:29 PM
len k len k is offline
Registered-III
 
Join Date: Jun 2012
Location: Manchester, New Hampshire
Posts: 15,888
Thanks: 427
Thanked 5,750 Times in 4,177 Posts
Default Re: Onan 7.5 JB-3CR running issue

To test my 6 volt JB coil I folded up paperclips to make a spark gap between the towers. Then wired up the coil, a 6 volt gelcell, and a points cap in series. Then briefly connected and disconnected a shorting wire across the cap.
Don't hold the bare primary wires....ZAP .
(Four alkaline D cells in series would work too if didn't have a gelcell.)

I got ~ 1.5 inch spark (~ 45,000 volts) , but since then I've been told you shouldn't make the gap that large as it stresses the coil insulation.

Primary resistance on my good coil was .9-1.0 ohms, manual has specs on secondary ohms.

I had to clean the "mucky" primary connections on brass terminals to get mine to work, bad connection.
Reply With Quote
The Following 2 Users Say Thank You to len k For This Post:
  #48  
Old 03-19-2017, 09:16:35 PM
squidtrap squidtrap is offline
Subscriber
 
Join Date: Nov 2012
Location: Forked River, New Jersey
Posts: 1,218
Thanks: 1,807
Thanked 583 Times in 392 Posts
Default Re: Onan 7.5 JB-3CR running issue

starting on page 29 of manual 967-0500 it goes through the whole testing procedure. The coil should be between 7-10K but u should go through the whole section and do all the tests.
Reply With Quote
The Following 2 Users Say Thank You to squidtrap For This Post:
  #49  
Old 03-20-2017, 09:13:04 AM
mheltunen mheltunen is offline
Registered-I
 
Join Date: Mar 2017
Location: Atlantic Mine, Michigan, USA
Posts: 87
Thanks: 56
Thanked 20 Times in 11 Posts
Default Re: Onan 7.5 JB-3CR running issue

It runs!! after borrowing a coil and adding a (temporary) single pole switch to the wires feeding the centrifugal switch I was able to get it running. the engine is searching a bit so I can see some fine adjustments will be needed. My next question looking forward to the AC portion is connections. I will attach some pictures as well. In the box where the AC output connections are terminated I see 4 wires leading into the box. 2 of the wires lead to a ground lug and the other 2 are wire nutted individually. I am assuming the the two leads with the wire nuts are the hot wires. Each lead I assume is 120V and doubling them would bring it to 240. At this time I only wish to use 120V. So to wire a simple outlet in would I use one of the 120 leads to the hot side of the outlet and the wires leading to the ground lug for the neutral? Is there any way to ground the outlet like in a conventional house circuit? Again I apologize for what may be a basic set of questions. I'm not an electrician by trade but find I can usually figure it out with research and questions.

Thanks!
Reply With Quote
  #50  
Old 03-20-2017, 09:15:30 AM
mheltunen mheltunen is offline
Registered-I
 
Join Date: Mar 2017
Location: Atlantic Mine, Michigan, USA
Posts: 87
Thanks: 56
Thanked 20 Times in 11 Posts
Photo Re: Onan 7.5 JB-3CR running issue

Attached are a couple of pictures of my AC output box and the control box as well.
Attached Thumbnails
Click image for larger version

Name:	image1.JPG
Views:	45
Size:	109.9 KB
ID:	278007   Click image for larger version

Name:	image2.JPG
Views:	38
Size:	107.2 KB
ID:	278008  
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Onan KY Microlite 4000 Running Issue bills02jeep Onan Generators 14 12-10-2016 12:32:44 PM
small associated running issue (help!) Chris Steffen Antique Gas Engine Discussion 8 12-25-2012 01:57:23 PM
Onan Model 4.0 DKC-3CR/1A Serial # E860820953 Running issue KWA915 Onan Generators 1 07-02-2012 10:29:47 PM
Maytag 92 running issue Lvolling Maytag Engine Collectibles 3 05-29-2011 01:34:09 AM
Onan DJC12 start/run, stay running issue dougvnbalto Onan Generators 2 10-29-2010 08:59:03 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 04:52:27 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277