  #1  
Old 03-07-2008, 01:51:17 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Default Onan Magniciter Theory FAQ

Thanks to several members for sending the Magneciter diagrams and schematics to me. Very Helpful!

After pondering the information on saturable core reactors here, and carefully looking over the schematic, I think I have the basic idea: ( 04SX and 06SX Magneciters )

1: The gate reactors limit the current supplied to the field. There are two, one for each half of the AC cycle. Each one only receives current in one direction. The magnetic flux in each reactor is always in the same direction.

2: The control windings of the gate reactors are wound to oppose the flux of the gate windings. Increased DC voltage on the control windings reduces the current flow through the gate windings by de-saturating the core.

3: The control windings are powered by the generator output. As the generator voltage increases, the control voltage increases.

4: The control reactor seems only to reduce the voltage/limit the current to the control rectifier. It is not magnetically coupled to the gate reactors. Just a big inductor.

5: The compound winding seems to be for core flux bias. It saturates the cores to move the saturation into the 'knee' of the saturation curve, where they will be most sensitive to control inputs. These are also wound to oppose the gate flux.

6: The calibrated shunt ( hand noted on my drawing as being for 06SX only ) seems to be used to set the current in the bias winding very low. The cores only need a little bias , not full field voltage.

Magneciters are pretty cool. Hard to break them, simple to trouble shoot.

Has anyone experimented with changing the values of the damping resistor to try and tighten it up? I'm thinking of replacing it with a 500 ohm rheostat and moving it around a little to see what happens. It's in parallel with the field, so it seems like there's little risk.

It seems like the optional voltage regulator filter would be a large capacitor placed at the output of the control rectifier to smooth out the control voltage. It must be pretty choppy there. Has anyone seen anything like that? The other alternative is to have the big cap right at the feed to the field. Maybe both places could use a little smoothing. Yes, I know about bleeder resistors. I don't want to weld screwdrivers or take a farad across my heart...
Attached Thumbnails
Click image for larger version

Name:	Magneciter.JPG
Views:	2840
Size:	135.8 KB
ID:	30408   Click image for larger version

Name:	Magneciter2.jpg
Views:	2212
Size:	130.7 KB
ID:	30409  
Reply With Quote
Sponsored Links
  #2  
Old 03-07-2008, 07:35:29 PM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,788
Thanks: 552
Thanked 1,812 Times in 1,182 Posts
Images: 1
Talking Re: Magneciter Theory...

Ted, does this mean you are now going to be the "GO TO GUY" on Magniciter questions?
I am sure Jim and Gunny would like to have someone else field the Magniciter questions.
We could even get Harry to make a "Magniciter FAQ" just for you. The rest of us think
Magniciters, are just MAGIC.
__________________
Bruce in alaska
Reply With Quote
  #3  
Old 03-07-2008, 08:16:34 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Default Re: Magneciter Theory...

Hmmm. There's not much that can go wrong with a magneciter, other than letting the very expensive blue smoke out of the reactor coils, or the much cheaper smoke out of the diodes. I'm always glad to help out!

Along that note - upon seeing the prices that Onan wants to replace the magneciter, I've decided that I will be adding fuses in line to both sides of the magneciter AC input. 10 amps should be about right. That should help to keep the magic smoke in where it belongs...
Reply With Quote
  #4  
Old 03-07-2008, 11:05:21 PM
Donald Randall Donald Randall is offline
Registered-II
 
Join Date: Dec 2006
Location: Bethany, OK
Posts: 65
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Magneciter Theory...

Ted,
Wouldn't the field windings act as a choke and provide adequate filtering for the DC pulses, or is its inductance, (inductive reactance actually), too small to have much influence? If you have an operating unit, would it be a good idea to take, and make notes of, the voltages and currents of the: field windings, control windings, and each reactor winding separately, while the generator is running, unloaded or with a specific load,for future troubleshooting reference? Or does Onan supply some baseline values? I find very few specifics on voltage, current, and component values, or their functioning, in any of their manuals in my posession. If you figured out the operation of this unit only by studying the schematics, I am impressed. Don
Reply With Quote
  #5  
Old 03-08-2008, 12:09:50 AM
Donald Randall Donald Randall is offline
Registered-II
 
Join Date: Dec 2006
Location: Bethany, OK
Posts: 65
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Magneciter Theory...

Did you notice that the reactor coils are phased oppositely? (Note the dots). I understand that they induce some voltage into the control windings, and being out of phase with each other, cancel out the effects of the induced voltage on the control voltage. Which I believe, is also why they each use only their particular half of the ac cycle. One half of the ac cycle has more influence than the other, so they use the one with the least influence on each coil. Don
Reply With Quote
  #6  
Old 03-08-2008, 02:52:56 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Default Re: Magneciter Theory...

I haven't gone through and measured things yet, except the field voltage, around 40 volts at 30% load ( 10 KW single phase gen end ).

The reactor coils are phased oppositely, and the control windings are arranged so the control flux is always opposite the main ( gate ) flux - this provides the negative feedback mechanism.

I have reconsidered the purpose of the compound winding that loops through each of the reactor coils. I don't think it's a bias winding - those are only used when the control windings are fed AC. The magneciter control is DC. I also couldn't see anything like a calibrated shunt on my set, even though I have an 06SX magneciter. If I can't find it, I'll add it in to see if it provides tighter regulation. The current it would provide would be fairly miniscule. The name Onan gives it must be meaningful, but I haven't yet figured it out. as one reactor coil's field collapses, a current is induced, and transfers to the other reactor as it is building it's field. I haven't figured out yet whether it increases or lowers the flux of the opposite reactor coil, or what purpose it serves.
Reply With Quote
  #7  
Old 03-08-2008, 04:08:00 PM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,599
Thanks: 1,401
Thanked 1,507 Times in 964 Posts
Default RE: Magniciter Theory FAQ

Short sweet and easy repair course on Magneciters.

If the coils are good, replace the diodes and/or SCR as needed.

If the coils are bad (smoke got out) call Power Tronics and get a replacement regulator that replaces the whole thing. Way far cheaper.

Magneciters, thats as close to smoke and mirrors as anything I've ever encountered. Whoever dreamed up that idea was either a genius or had some very good pharmaceuticals. Same goes for the folks who designed some of those Woodward governors.

Ted cool Comment:
I agree with Gunny - If the reactor coils go bad, it's done.

Last edited by BTPost; 05-02-2009 at 01:18:54 PM. Reason: Cleaning up FAQ's
Reply With Quote
  #8  
Old 03-10-2008, 08:39:49 AM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,788
Thanks: 552
Thanked 1,812 Times in 1,182 Posts
Images: 1
Default RE: Magniciter Theory FAQ

OK, after pondering the Magneciter troubleshooting guide that describes the symptoms of trouble with the compound winding, I believe I have figured it out:

The compound winding is a positive feedback loop driven by the energy of the field collapse of the reactor that just went 'out of phase'. As the voltage goes to zero, the current is reaching its peak. This transfers energy to the other reactor coil as positive feedback, countering the action of the control windings of the now 'in phase' reactor during the first half of its cycle.

This acts as a 'ratchet' of sorts in response to demand.

1: Load increases

2: Voltage drops

3: Control voltage/current drops ( less negative feedback )

4: Field current increases

5: Compound winding current increases

6: Voltage increases

7: Control voltage increases ( more negative feedback ). Counteracted in part by increased compound winding current.

8: Voltage stabilizes at higher field current.

That 1/2 cycle delay in action seems to be crucial!


1: Load decreases

2: Voltage rises

3: Control voltage/current rises ( more negative feedback )

4: Field current decreases

5: Compound winding current decreases

6: Voltage decreases

7: Control voltage decreases ( less negative feedback ). Less counteraction by decreased compound winding current.

8: Voltage stabilizes at lower field current.

I'm still not sure about the calibrated shunts that connect the compound windings. Since it's in series with the DC to the field, it acts as sort of an ammeter shunt - more field current means more current in the compound winding circuit. I'm not sure, but I think it is set up as more positive feedback. This might be to trim the action of the compounding circuit, as it is only one turn around the coil, and a second turn might be too much.

The Magneciter is an interesting magnetic balancing act. It's amazing to me that it works as well as it does.

BTPost's Comment: Like I said...... MAGIC.......

Last edited by BTPost; 05-02-2009 at 01:20:36 PM. Reason: Cleaning up FAQ's
Reply With Quote
  #9  
Old 04-12-2008, 11:09:57 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,186 Times in 969 Posts
Default RE: Magniciter Theory FAQ

You have to go down a ways, but there's a description of the saturable reactor/magnetic amplifier at this link
http://www.allaboutcircuits.com/vol_2/chpt_9/7.html

Of course this is just part of the magneciter system, but it shows how part of it is done and why there are two reactors and why the phasing is important.

Robert S's Comment:
you will impress me more if you can tell me if it will cook my hotdog to proper temperature!!!!!

Last edited by BTPost; 05-02-2009 at 01:22:20 PM. Reason: Cleaning up FAQ's
Reply With Quote
  #10  
Old 04-13-2008, 11:30:12 AM
VaughnSimon VaughnSimon is offline
Registered-III
 
Join Date: Oct 2005
Location: Palm Beach, Florida USA
Posts: 631
Thanks: 26
Thanked 108 Times in 100 Posts
Default RE: Magniciter Theory FAQ

I had almost forgotten about this thread, and it is too important to be lost. Is it possible that it could be incorporated into the FAQ?

Ted Cool Comment:
Hi Vaughn,
You are certainly welcome to incorporate this into the FAQ in any way you find helpful. Thanks for doing this, and I hope it is of use to others. It does seem that the bottom line is to take care of it ( fuses/breakers ) , replace the diodes as necessary, and scrap it if anything else goes wrong.

BTPost's Comment:
Absolutely, that is what the FAQ is all about. Anyone can add a Post to the FAQ, and if anyone finds information in the FAQ, that is suspect or Wrong, they can get ahold of one of this forums Moderators, and we will fix it, or get a consensus of the "Resident SmartGuys" about the the item, and then update it.

Last edited by BTPost; 05-02-2009 at 01:25:03 PM. Reason: Cleaning up FAQ's
Reply With Quote
The Following User Says Thank You to VaughnSimon For This Post:
  #11  
Old 04-17-2008, 10:42:06 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 16,215
Thanks: 8,262
Thanked 13,550 Times in 6,382 Posts
Default RE: Magniciter Theory FAQ

Ted If you find out what FIRE DOWN means please let me know. I have gone through all my magnaciter manuals with no luck. I called some of the other old Onan techs from the factory. They cannot recall what it means. Power tronics makes a good replacement system for the mag. I have installed several of them. And yes if coils burn out replace system.

Ted Cool's Reply: Hi Billy,

I have the same question, too. The best I can figure is that this is the voltage at which the 'knee' in the saturation curve of the reactors is most evident - in other words, you will see the DC field voltage increase as the AC voltage increases, until you reach the 'fire down' voltage, at which point, the DC voltage will start to decrease. I haven't tried it to see if that actually happens ( Don't have a variac ) - Has anyone here tried that?
Attached Thumbnails
Click image for larger version

Name:	Magneciter 4-7.jpg
Views:	1280
Size:	35.0 KB
ID:	32525   Click image for larger version

Name:	Magneciter 4-8.jpg
Views:	984
Size:	22.5 KB
ID:	32526  

Last edited by BTPost; 05-02-2009 at 01:27:24 PM. Reason: Cleaning up FAQ's
Reply With Quote
  #12  
Old 05-08-2008, 10:31:46 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Thumbs up RE: Magniciter Theory FAQ

Wow - moved up to the top of the forum! I thought the FAQ was a good enough home. Thanks to all the rest of you here - I couldn't have done it without your help.

BTPost-Answer:
Your insights deserve the "Special Recognition" of being their own FAQ.
Anyone who can fathom the Magniciter, and explain it, so us lesser people,
can understand the MAGIC involved, deserves our best. Thanks a lot Ted.
Many will come to appreciate this down the road.

Last edited by BTPost; 05-02-2009 at 01:15:49 PM. Reason: Cleaning up FAQ
Reply With Quote
  #13  
Old 08-10-2008, 06:52:05 PM
Lloyd H Lloyd H is offline
Subscriber
 
Join Date: Feb 2008
Location: Chester, Illinois, USA
Posts: 519
Thanks: 169
Thanked 158 Times in 122 Posts
Default Re: Magniciter Theory FAQ

I once had a better understanding of saturable reactors as a Navy interior communication electrician (we called them magnetic amplifiers) The navy used them in a lot of stuff in the 50's and 60's. Gun mounts were driven with DC motors powered by "amplidynes" (dc generators driven by 480 3phase motors. The field coils were controlled by mag amps. So if anyone can come up with some of the old training material it would certainly be applicable. In school we covered mag amps in a week of school time. (1963 for me so a lot of it is gone out of the old noggin)
Reply With Quote
  #14  
Old 03-31-2009, 10:54:30 AM
BergmanJ BergmanJ is offline
Registered-II
 
Join Date: Apr 2005
Location: Duluth, Minnesota USA
Posts: 380
Thanks: 287
Thanked 179 Times in 118 Posts
Default RE: Magniciter Theory FAQ

As promised a while ago, here is re-done diagram with all re-winding particulars for the 315-103 Gate Reactors. I also attached the modified Onan testing procedure for reference.

Well, folks, I put together a paper describing some of the details of re-winding an Onan 315-102 Gate Reactor. I tend to be just a wee bit windy when it comes to documentation like this; so, --- bear with it.

I've attached it below & hope it's useful to someone.

Thanks, JLB
Attached Thumbnails
Click image for larger version

Name:	Magneciter8_B_3.jpg
Views:	1058
Size:	65.1 KB
ID:	51397   Click image for larger version

Name:	Method 'E'.jpg
Views:	843
Size:	63.5 KB
ID:	51407  
Attached Files
File Type: doc Onan315_102Winding.doc (31.0 KB, 529 views)
Reply With Quote
The Following 2 Users Say Thank You to BergmanJ For This Post:
  #15  
Old 04-01-2009, 01:45:24 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Default Re: Magniciter Theory FAQ

Thanks - That info is priceless for magneciter repair.

Also, I'm glad to see you figured out what the heck the compound winding and shunt wire were doing. I'm just an electrical 'hacker', not truly knowledgeable...

Reviewing my notes on the compounding winding, I think I was on the right track - more current to the field provides a little positive feedback, such that it will balance out at 120 volts at a higher field current as load increases.

It's interesting that Onan used two different gauge 'Load Sense Loop' wires over time - I guess that's how to tweak the feedback. Either that, or 13 gauge was just too hard to find/ not worth it. It seems like experimenting with the length and gauge of these two wires might be worthwhile to try to get better regulation.

Did you rewind the gates yourself, or did you send them out somewhere? These are really similar to what Amateur Radio 'Hams' would make for a high power antenna matching balun. I've seen the wire and insulating tape available at their supply houses.

Do you have the specs on the winding of the Voltage Control Reactor 315 -100?

Thanks Again!
Reply With Quote
  #16  
Old 04-01-2009, 02:13:21 PM
BergmanJ BergmanJ is offline
Registered-II
 
Join Date: Apr 2005
Location: Duluth, Minnesota USA
Posts: 380
Thanks: 287
Thanked 179 Times in 118 Posts
Default RE: Magniciter Theory FAQ

Ted,

I'm the guilty party all by myself.

I'm also a 'ham': KC0BWT, but haven't been active recently due to the spouse and I also building a new totally 'off-grid' retirement home. It keeps us extraordinarily busy.

No, I don't have any specs for any of the other reactors; I would need to have a working-good example, AND a 'burned-up' one from which to work. Perhaps someone else would like to contribute work on some others.

You need to very carefully take the bad one apart, counting each and every last turn, measuring wire guage, noting any other specific quirks, etc. Then you need to compare (electrically) the newly re-wound reactor to it's partner 'working-good' reactor as far as being the electrical equivalent. This might require accurate DVM's, Oscilloscopes, frequency generators, etc.

I used the 25-watt lightbulb test in conjunction with my DMM to result in an identical unit to its mate by measuring 60-hz 120VRMS utility power through the light bulb and reactor to customize the final winding turns so that each winding would match both the open-circuit, and shorted Control winding series RMS current while running the lightbulb test [Method E] comparing the new against the old (good) one. The heavy Gate winding is the most particular for exact number of turns. Both windings can be adjusted a few turns + or - to exactly match the 'known-good' one.

The same kind of work would be applicable to reverse-engineer any of the other reactors for other models.

Then, there is the time element! Mine took many 10's of hours to figure-out, then collect materials, and re-wind.

I did mine out of sheer necessity of being 'off-grid' and going into winter (around here it can get to -40 deg. F. occasionally - this requires space heating to survive; which, in turn, requires some electrical service to run the heating (yes, I know, wood heat would do. but I'm still 'working for a living' too)).

It should cost about $100.00 or so to have a motor shop re-wind the 315-102 per my specs. above. This would NOT include any fine tuning of the number of turns.

Thanks, JLB

I have a 15kW MDJF marine unit with a magneciter inside, and it is poorly corroded after sitting for several years. Inout appreas to be 3 lead from sttaor and output is to 2 pairs of carbon brushes on the rotor.

Can it be replaced with an electronic voltage regulator (less than $200), like later AA spec models (part# 300-1540)? If so, it'd save me a lot of money and time.
Reply With Quote
  #17  
Old 05-09-2009, 03:23:28 PM
bmilbourn bmilbourn is offline
Registered-I
 
Join Date: Apr 2009
Location: ossipee new hampshire usa
Posts: 7
Thanks: 3
Thanked 0 Times in 0 Posts
Default Re: Magneciter Theory...

Well put Ted!
Reply With Quote
  #18  
Old 11-17-2009, 12:32:48 PM
Ted_Cool Ted_Cool is offline
Subscriber
 
Join Date: Jan 2006
Location: China, Maine
Posts: 1,094
Thanks: 420
Thanked 337 Times in 246 Posts
Default Magneciter differences -06SX

Does anyone know when/where/why the different 06SX magneciters were used? I have a 10.0 JC spec 'H' with the 06SX1N1B. Is the 06SX1N3B used in a later spec? The Onan Service Bulletin dated 3-73 says 'Some newer units have an automatic field flashing circuit...'

06SX1N1A - No field flash.

06SX1N1B Field flash push button switch.

06SX1N3B 'Automatic' field flash via extra diodes. Two in series, same part numbers as the regular field diodes.

Why two in series? <To Increase the PIV Rating Of the Diodes>

150 ohm stabilizing resistor listed as 50 watt in specs, but appears to be a Dale G series 10 watt.

'Compound Winding' 14 gauge ( Rev A ) or 13 gauge ( Rev C ) wire 27.5 inches

'Calibrated shunt' 16 gauge wire 27.5 inches long in parallel with 'Compound Winding'

Same gate and control reactors.
Reply With Quote
  #19  
Old 12-17-2009, 10:14:13 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,186 Times in 969 Posts
Default Re: Magniciter Theory FAQ

I figured there was enough demand for these Onan Magneciter pages that I would just put them here instead of everyone having to request them from someone who has them.

I won't duplicate what has already been posted in this thread, so if you don't see the one you need, check the rest of this Magneciter threead.
Attached Thumbnails
Click image for larger version

Name:	magneciter checkout 2 [1024x768].jpg
Views:	643
Size:	67.7 KB
ID:	69384   Click image for larger version

Name:	mag trouble shooting 1 [1024x768].jpg
Views:	472
Size:	74.9 KB
ID:	69385   Click image for larger version

Name:	magneciter checkout 3 [1024x768].jpg
Views:	473
Size:	103.8 KB
ID:	69387   Click image for larger version

Name:	magneciter checkout 4 [1024x768].jpg
Views:	439
Size:	119.6 KB
ID:	69388  

Reply With Quote
The Following User Says Thank You to Jim Rankin For This Post:
  #20  
Old 12-17-2009, 10:36:11 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,186 Times in 969 Posts
Default Re: Magniciter Theory FAQ

It looks like you have to click on the thumbnail,
then click on the picture that loads in the dark screen and
then boost the magnification so you can read it, but it doesn't get too fuzzy.

Here's some more
Attached Thumbnails
Click image for larger version

Name:	magneciter checkout 5 [1024x768].jpg
Views:	555
Size:	92.8 KB
ID:	69389   Click image for larger version

Name:	magneciter checkout 6 [1024x768].jpg
Views:	395
Size:	63.3 KB
ID:	69390   Click image for larger version

Name:	magneciter checkout 7 [1024x768].jpg
Views:	386
Size:	90.0 KB
ID:	69391   Click image for larger version

Name:	02sx magneciter [1024x768].jpg
Views:	500
Size:	94.7 KB
ID:	69392  

Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
25kW Onan 3 phase 208 W/Magniciter Ford 6 mrmuzic Onan Generators 57 06-17-2012 11:43:06 PM
Onan YD vs Magniciter GHanners Onan Generators 14 05-20-2012 06:48:39 PM
Onan 30EK UR, Magniciter 07SX1N1C high voltage franciscanfriars Onan Generators 35 09-22-2011 08:01:59 AM
Theory of low compression on Onan CCKs c east Onan Generators 10 04-14-2011 05:27:55 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 01:46:50 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277