Kohler 12 RES Neutral/Ground Connection


this thread has 12 replies and has been viewed 443 times

Reply
 
Thread Tools Display Modes
  #1  
Old 12-02-2018, 01:09:17 PM
TNBob TNBob is offline
Registered
 
Join Date: Dec 2018
Location: Old Hickory, Tennessee, USA
Posts: 5
Thanks: 2
Thanked 1 Time in 1 Post
Default Kohler 12 RES Neutral/Ground Connection

Hi Guys,

I'm a newbie here and my Kohler question isn't about vintage equipment so apologies if this isn't an appropriate question. However, I lurked on the site a while and there seems to be a lot of expertise here so I'm hoping someone can help me out. First, some background.

I'm putting together a homestead far off grid and I recently installed a 6.5 KW solar array with a 17.5 KWH Li-Fe-Ph battery bank and associated equipment. It's working fine but as backup I'm adding a Kohler RES 12 propane fueled genny. My neutral/ground connection for the entire system is in the power center where the charge controllers, inverters, (and now generator input) all come together.

However, while installing the genny and reading the manual, I see that the neutral is bonded to the ground in the generator 'junction box' as well. Additionally there is a prominent decal indicating that the generator neutral is bonded to the frame.

There is also a statement in the Kohler installation manual that, "At installation, the neutral can be grounded at the generator set or lifted from the ground stud and isolated if the installation requires an ungrounded neutral connection at the generator."

Obviously, since I already have one neutral/ground bond in the system, I need to isolate this neutral and ground in the genny. All this is pretty clear and seemingly straight-forward.

Secondly there are additional instructions to connect the grounding cable (assuming they mean the equipment ground) to the generator set ground lug 'inside the controller compartment.)

There are no pictures are drawings to indicate exact locations in either case.

My problem is this - apart from the rather general directions, all of the wiring runs into a single box behind the control panel which I assume is both the 'controller compartment' and 'junction box' they're referring to. There doesn't seem to be any way to access the wiring in the box without practically dissembling the generator enclosure. I'll do that if I have to but it really seems strange to me that would be required. I tried taking the back off the controller compartment, but there just isn't room to remove it sufficiently to access the inside of the box,

I can sort of see where this level of effort might be required to swap the neutral/ground configuration because a lot of customers won't be doing that anyway. However, everyone will have to ground the genny and I don't see putting the grounding lug in an inaccessible location as a good design. Therefore, it has me scratching my head and thinking I must be missing something.

Bottom line is I have two questions:

1. Is there a 'grounding lug' in some location I'm overlooking (quite possible)

2. Is there some simple way to access the inside of this controller box that I'm overlooking as well. That's also quite possible, but from the looks of things, it all goes together a bit like a puzzle, with this side of the box bolted to one side of the enclosure with another side of the box bolted to another side of the enclosure. It looks like to me that if I take that all apart it's going to be a PITA and take three hands to get back together.

Obviously, none of this is a gigantic technical hurdle, but on the off chance someone is familiar with this set up and can clue me in to an easier way to get inside this box, I thought I'd post this question. Any help appreciated.

Many thanks,

TNBob
Attached Thumbnails
Click image for larger version

Name:	Control Box - Front view.jpg
Views:	45
Size:	146.7 KB
ID:	323835   Click image for larger version

Name:	Back of Control Box - Looking Down from Top.jpg
Views:	41
Size:	124.5 KB
ID:	323836   Click image for larger version

Name:	Back of Control Box - Looking Down from Top - Screws Removed from Back Cover Plate.jpg
Views:	40
Size:	148.4 KB
ID:	323837   Click image for larger version

Name:	Back of Control Box - Looking Down from Top - 'Peeking Through Crack'.jpg
Views:	37
Size:	110.9 KB
ID:	323838  
Reply With Quote
Sponsored Links
  #2  
Old 12-02-2018, 07:56:44 PM
Zephyr7 Zephyr7 is offline
Registered-II
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 974
Thanks: 237
Thanked 521 Times in 358 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

The wiring compartment may well be hard to get to. They build these things to be compact and ease of access in many cases is a secondary concern (if that), especially for things that won’t be accessed frequently.

The ground connection is probably in the same compartment as the phase and neutral connections. Ground is probably a copper lug bolted somewhere. I personally would use a compression lug on the ground wire and land it on a bolt or stud with a lockwasher.

I agree you should open the ground/neutral bond at the genset in your case. I’d also recommend running the power cabling to the generator in metal conduit (probably EMT) to ensure a little extra safety. Make sure control wiring is in a seperate conduit from the power conductors.

Bill
Reply With Quote
  #3  
Old 12-02-2018, 08:37:06 PM
AlanR AlanR is offline
Registered-I
 
Join Date: Sep 2018
Location: Walla Walla, Washington, USA
Posts: 90
Thanks: 4
Thanked 104 Times in 60 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

You're in the right location - but they want you to take the end sheet metal off, too. Instructions for controller access start at page 36, page 37 fig 4-20 shows the controller compartment with the back off, and you can see what's probably the ground bolt/wiring visible on the floor of the compartment, behind the circuit breakers.

http://www.kohlerpower.com/onlinecatalog/pdf/tp6196.pdf

Alan
Reply With Quote
  #4  
Old 12-02-2018, 08:51:12 PM
Mark Dieckmann Mark Dieckmann is offline
Registered-I
 
Join Date: Mar 2009
Location: Osgood, IN, USA
Posts: 122
Thanks: 34
Thanked 31 Times in 23 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

Forgive me, it's been awhile, but I think these units had a connection box on the back.
Reply With Quote
The Following User Says Thank You to Mark Dieckmann For This Post:
  #5  
Old 12-02-2018, 10:04:47 PM
AlanR AlanR is offline
Registered-I
 
Join Date: Sep 2018
Location: Walla Walla, Washington, USA
Posts: 90
Thanks: 4
Thanked 104 Times in 60 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

Quote:
Originally Posted by Mark Dieckmann View Post
Forgive me, it's been awhile, but I think these units had a connection box on the back.
They DO have a connection area in the back. Unfortunately, while they have separate connection points there for neutral and ground, that's NOT where they tied neutral TO ground - for whatever reason, they did it in the controller box. The neutral lead from the gen end (L0) goes along with L1 and L2 to the controller box. L1 and L2 go to the circuit breaker there, then to the rear connection area. L0 goes to a ground point in the box, then to the rear connection area. So, to isolate neutral from ground, you have to get into the controller box.
Reply With Quote
  #6  
Old 12-02-2018, 10:08:18 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,201
Thanks: 2
Thanked 731 Times in 518 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

Picture #1. Two phillips head screws on the left side of the control box through the side cover. One bolt head into the floor down by the battery. Two bolts in the back. Remove all those, main generator side panel comes off, then remove the cover from the wiring box and all will be revealed.
Reply With Quote
The Following User Says Thank You to Birken Vogt For This Post:
  #7  
Old 12-03-2018, 09:24:41 AM
TNBob TNBob is offline
Registered
 
Join Date: Dec 2018
Location: Old Hickory, Tennessee, USA
Posts: 5
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Kohler 12 RES Neutral/Ground Connection

Thanks Bill,

Regarding:

Quote:
Originally Posted by Zephyr7 View Post
I’d also recommend running the power cabling to the generator in metal conduit (probably EMT) to ensure a little extra safety. Make sure control wiring is in a separate conduit from the power conductors.
Already done. I separated the control and power wiring however I used metal flex as opposed to EMT as required by Kohler for vibration.

Thanks for your help and especially the quick reply.

Yep. This is pretty much what I thought but it seemed to be such an illogical and sucky design that I was hoping I was mistaken. Thanks for the confirmation.

Bill, Sorry I'm just getting the hang of this. That last sentence was actually meant to be in reply to one of Alan's posts. As you see I'm incompetent in many areas.

Thanks Alan,

That Service Manual will come in VERY handy. I had only the Installation and Operations Manuals. I appreciate the help.

Bob

Damn it! I did it again.

Quote:
Originally Posted by AlanR View Post
You're in the right location - but they want you to take the end sheet metal off, too. Instructions for controller access start at page 36, page 37 fig 4-20 shows the controller compartment with the back off, and you can see what's probably the ground bolt/wiring visible on the floor of the compartment, behind the circuit breakers.

http://www.kohlerpower.com/onlinecatalog/pdf/tp6196.pdf

Alan
Thanks Alan. That Service Manual will come in VERY handy. I only had the Installation and Operation Manuals.

Best, Bob

Okay, apologies to all for my message board incompetence. In attempting to give individual replies to each of your posts, they all seemed to get chained together in a single reply. However, I hope it was at least somewhat clear. Thanks to all for the help and sorry for the confusion.

It appears that rather than attempting to 'reply' to each individual post that I should just reply to the thread 'in general' and quote the post I'm to which I'm trying to reply.

Best - Bob

Okay, that didn't work either as my last reply was just tagged on to the bottom of my previous one. If anyone can clue me into what I'm doing wrong, I'd appreciate it.

Thanks,

Bob
Reply With Quote
  #8  
Old 12-03-2018, 11:17:56 AM
Zephyr7 Zephyr7 is offline
Registered-II
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 974
Thanks: 237
Thanked 521 Times in 358 Posts
Default Re: Kohler 12 RES Neutral/Ground Connection

The forum merges all your replies into one lengthy post if no one posts something in between your multiple posts. Use “quote” and edit the quoted text and then it makes more sense since we can all see who you were responding to with each individual reply.

Don’t worry about it, we all started not knowing stuff and learn as we go

Bill
Reply With Quote
  #9  
Old 12-04-2018, 08:36:43 AM
TNBob TNBob is offline
Registered
 
Join Date: Dec 2018
Location: Old Hickory, Tennessee, USA
Posts: 5
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Kohler 12 RES Neutral/Ground Connection

Thanks, Bill. I thought it was me.
Reply With Quote
The Following User Says Thank You to TNBob For This Post:
  #10  
Old 12-17-2018, 07:35:11 PM
TNBob TNBob is offline
Registered
 
Join Date: Dec 2018
Location: Old Hickory, Tennessee, USA
Posts: 5
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Kohler 12 RES Neutral/Ground Connection

Thanks to all. With a little info I was able to solve my problem and my Kohler genny now has the neutral isolated from the ground and the genny itself is well grounded.

I do have another question if anyone wants to jump in.

When I bought the genny, a carb heater was listed as an option and I bought it as an 'add on.' Not a bit deal technically as it just bolts on around the carb under the air cleaner and plugs into one of the 115 VAC plugs that are pre-installed on the back of the controller box. However, in looking at the installation manual the temp sensor is in the power cord and the thing comes on anytime ambient temp dips below 40 degrees F.

Okay in theory I suppose, but I'm totally off grid and solar powered and this thing using juice 24/7 when the temp hits 40 seems like a big waste of power. I figured it would cycle on at a MUCH lower temp, as we can go for days in my area with the temp in the 30 to 40 range. Even without the carb heater, the genny started first time every time during our recent cold spell with temps in the low 20s.

It doesn't use much power, but on the other hand, I'm sure there will be some point (especially as I 'add' stuff) when I'm counting every watt and I'm sorta beginning to think this impulse buy was a bit of overkill.

Any opinions from you folks familiar with Kohlers?
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Ground roof top antenna to neutral-ground of power line? sdowney717 Generators & Electric Motors General Discussion 43 12-12-2013 09:38:09 PM
Onan 6.5 NHD separating ground from neutral? Magnetite Onan Generators 11 03-27-2012 03:58:03 PM
Need INFO on neutral and ground c east Generators & Electric Motors General Discussion 12 08-29-2011 08:01:47 PM
neutral or ground OMCposty Generators & Electric Motors General Discussion 3 10-14-2005 02:08:19 PM
MEP017A neutral/ground John T Military MEP and Aircraft Gen-Sets 1 10-02-2004 09:07:49 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 07:23:55 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277