Old 01-06-2019, 02:49:37 PM
Trekrider2001 Trekrider2001 is offline
Default Re: Kohler - unsteady voltage
Bingo! We are actually in a power fail right now (Seattle storm) so I took the opportunity to kill everything and re-torque L1, L2 and N. I did not do the receptacle thing, as the lights oscillating happened without the TV (just happens faster with TV). So I opened these connections, re-positioned the cable and torqued the lugs to 12 NM (no documentation I could find as to the torque). It seemed that this was just a tad bigger than what they were. So far so good. We are on generator, turn the oven on, turn the TV on and I only get a small dip as the oven cycles on and off, but otherwise the voltage is stable. Will continue to monitor throughout the power outage, but so far this looks like a fix. Anyway, I am unable to create the problem.
Old 01-06-2019, 04:56:57 PM
On reading the literature, it seems like these connectors need to be torqued to 250 inch pounds or about 26-28 NM. Would you guys agree that I need to torque these more? I just don't want to strip the threads as it is only aluminum.
Old 01-06-2019, 07:45:32 PM
Zephyr7 Zephyr7 is offline
Yes, but do it after the storm unless the wire is hot near the lug (feel the insulated part of the wire close to the lug). I’d pull the wire out and make sure it’s not corroded too. If you see corrosion, clean the lug with a wire brush and restrip the wire to get a clean end for termination.
It’s unusual to actually use a torque wrench to tighten these lugs. Most everyone just does it German style — “gutentight” you do need some practice to know how tight is right though. Use the torque wrench if you want to be careful.
Bill
Old 01-06-2019, 09:26:19 PM
dkamp dkamp is offline
eMail NOT Working
Electrical connections are subject to a variety of strange things... electrical HEATING is obvious enough (once the connection gets a little resistive, it gets warm). Another... is corrosion... a little dissimilarity in metals develops a slightly dielectric film between the two, causing strangeness. Cleaning and retorquing generally resolves it. Aluminum conductors DEMAND the use of corrosion-resistant paste... NonOX and De-Oxit are two trade names that come to mind.
If that solved your problem, GREAT! (now check all the rest... they probably need a little attention too... )
Old 01-07-2019, 06:06:08 PM
The connections all needed a good amount of tightening. I used the torque wrench just to be sure as all those connectors are just aluminum and I have big wrench! I did a load test and there was no problem or oscillation of voltages. In other words, can't reproduce the problem, so is it fixed? At this point yes. Let's see at the next power outage. We have two more storms coming this week (first is tomorrow morning) so we don't have to wait long. Thanks for all the comments and suggestions from everybody.
Old 01-07-2019, 07:23:21 PM
If you want to play it safe, check the tightness of all the connections once a year. Best time is around a big season change (like spring) due to the big temperature changes which tend to make any problem worse; and thus easier to find.
If anything loosens up before your next storm then something is wrong with the lug. Iíve seen pugs crack before and once that happens they wonít stay tight.
Bill
The Following User Says Thank You to Zephyr7 For This Post:
Kohler 2.5 CMZ RV with low, low voltage blaster88 Kohler Generators 6 11-13-2018 08:18:39 PM
Kohler 7.5 RMK Low voltage f150 limited Kohler Generators 28 11-10-2016 07:48:22 PM
Kohler 7.5-C61 Voltage Too Hi Need Help Glenn Ayers Kohler Generators 12 08-03-2013 11:06:42 AM
MEP-002 Unsteady Output DieselTech420 Military MEP and Aircraft Gen-Sets 16 12-08-2012 05:36:59 PM
Kohler 6.5kw low voltage surfventura Kohler Generators 15 09-12-2008 09:32:25 PM