3800W 120/240V Homelite Textron generator goes full throttle till overload trips


this thread has 19 replies and has been viewed 1304 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-19-2019, 12:18:55 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

It's just that I have owned and used it hard for 25 years so it's special to me. It's also 30 years old being a 1989 model per the S/N best I can tell. I repaired it from a scrap pile in 1994 as it was badly damaged (crushed) by yellow iron on a construction site. It had served us well ever since. The engine went through the back of the control/plug board and broke a wire thus the two red wire nuts and new wire you see as a old repair in the pics.


This winter it snowed on us hard, rare for the Phoenix dessert heat area I live in. The fan grate on my heat pump froze up so I figured to burn some older gas and power a hair dryer to melt the ice off the grille. Burning through gas to keep it fresh is a thing for equipment you need in an emergency.


30 weight oil is not correct for 32 degrees on the starter rope. I got about 60 seconds of power on the hair dryer before the genset went full throttle and shortly tripped the field overload breaker. (Was still making AC power.) Unplugged everything and reset the breaker - instant full load and trips the thermal breaker again after a delay. Then back to full speed no load with thermal breaker tripped. Something is shorted somewhere?

I have checked everything I can with a voltmeter. Separated the windings from the control board - no shorts to ground. Don't have the tools to get a good resistance check other than voltmeter. No shorts on the plugs that the voltmeter can see.

What else can I do to test? Visually it doesn't look good in the generator.

Attached Electric Schematic SC 00065 Homelite PN 49570

Homelite Textron 176R142-A
UT: 03631A
3800W 120/240V
Attached Thumbnails
Click image for larger version

Name:	homelite_textron.jpg
Views:	64
Size:	115.8 KB
ID:	331002   Click image for larger version

Name:	Electric Schematic SC 00065 Homelite PN 49570.jpg
Views:	71
Size:	136.1 KB
ID:	331003   Click image for larger version

Name:	hot_slip_rings.jpg
Views:	67
Size:	129.9 KB
ID:	331004   Click image for larger version

Name:	hot_slip_rings_r.jpg
Views:	67
Size:	124.7 KB
ID:	331005   Click image for larger version

Name:	hl.jpg
Views:	86
Size:	93.3 KB
ID:	331006   Click image for larger version

Name:	hl2.jpg
Views:	79
Size:	108.8 KB
ID:	331007   Click image for larger version

Name:	cp_boards.jpg
Views:	89
Size:	376.9 KB
ID:	331008  

Reply With Quote
Sponsored Links
  #2  
Old 03-19-2019, 12:25:50 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

Just a couple more pictures of the gen end windings if it will help.

Fan was off center: maybe a factory defect. It's cracked in 4 places and was rubbing the end cover and a support.
Attached Thumbnails
Click image for larger version

Name:	fs.jpg
Views:	59
Size:	215.2 KB
ID:	331009   Click image for larger version

Name:	stator.jpg
Views:	68
Size:	194.9 KB
ID:	331010   Click image for larger version

Name:	stator2.jpg
Views:	64
Size:	215.4 KB
ID:	331011  
Reply With Quote
  #3  
Old 03-19-2019, 01:37:37 PM
Andrew Mackey Andrew Mackey is online now
Sponsor
 
Join Date: Nov 2004
Location: Rockaway, New Jersey USA
Posts: 14,093
Thanks: 1,992
Thanked 6,725 Times in 4,271 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

With SAE 30, was the engine at ambient (outside) temp when it was started? If so. the engine probably starved for lubrication and the governor has probably eaten its teeth. SAE 30 does not splash well when it is that cold! I believe it (the governor) is plastic in that engine. You probably can get parts from Wisconson. The engine is a Wisconson Robin engine. Personally, I do not think it's a generator problem, rather an internal engine problem, due to the heavy oil. You probably are lucky the engine didn't throw a rod!
Reply With Quote
The Following 2 Users Say Thank You to Andrew Mackey For This Post:
  #4  
Old 03-19-2019, 09:27:20 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

Quote:
Originally Posted by Andrew Mackey View Post
With SAE 30, was the engine at ambient (outside) temp when it was started? If so. the engine probably starved for lubrication and the governor has probably eaten its teeth. SAE 30 does not splash well when it is that cold! I believe it (the governor) is plastic in that engine. You probably can get parts from Wisconson. The engine is a Wisconson Robin engine. Personally, I do not think it's a generator problem, rather an internal engine problem, due to the heavy oil. You probably are lucky the engine didn't throw a rod!
Thanks for the reply.

We usually don't get that cold here, ever, and I will be ready next time in reference to engine oil grade. I changed the oil to a winter grade in other equipment after this event. Normally we get the extreme other end of the heat scale ruining engine oil. (I have some trouble with oil samples due to oil overheating now and then and have to take corrective action.) It's 81F out today after not even a full month ago: snowing in February.

I may not have clearly said above: the engine governor is still working properly. It's not running away. Rather it's seeing a load when the generator field breaker isn't tripped.

When I reset the generator overload breaker the engine goes near wide open to maintain RPM and returns to normal throttle and RPM after the field thermal breaker trips.

Older Homelite service manual that I could find calls for a no-load 3750 RPM and to hold 3600 RPM under full-load.

The Loadamatic idle control never worked. I only recently found a manual online that described how it should work. It had some magnetic field on the electromagnet, but, never pulled the engine speed down to 2400-2600 RPM like it should. I wasn't getting any magnetic field when I looked at it last fall. Just wanted to see it work once. But didn't have time to open it up and look at it then.
Reply With Quote
  #5  
Old 03-19-2019, 10:51:30 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 6,011
Thanks: 9,899
Thanked 2,829 Times in 1,906 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

What do you get for output voltage during the short time the field breaker is closed?
Reply With Quote
  #6  
Old 03-20-2019, 07:16:28 AM
Joe Romas Joe Romas is offline
Registered-I
 
Join Date: Jan 2005
Location: Columbus, Ohio
Posts: 402
Thanks: 24
Thanked 92 Times in 84 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

For some quick troubleshooting I would first mark then remove the wires from the voltage select switch and meter it.
Reply With Quote
  #7  
Old 03-20-2019, 08:42:10 AM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,638
Thanks: 3,728
Thanked 4,938 Times in 2,061 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

I would concur on this being a govenor problem. Most smaller gens have NO feedback mechanisms between voltage output and engine RPM. Rather most all of them rely on mechanical govenor to control engine RPM. Exceptions being Inverterter type generators, which typically use a stepper motor throttle control.
Doc
__________________
'The time has come', the Walrus said,'To talk of many things: Of shoes and ships and sealing-wax Of cabbages and kings'
Reply With Quote
  #8  
Old 03-20-2019, 12:52:08 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 6,011
Thanks: 9,899
Thanked 2,829 Times in 1,906 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

To me, if the engine goes from no load to heavy load when the field breaker is closed, and then the field breaker trips, it is a generator problem. In this instance, the governor is just doing what it's supposed to.

Either the regulator has failed and is going "full field", or something is shorted somewhere, causing the generator to be overloaded. Either condition would produce the observed results.

The first one will result in high output voltage. The second one will result in low output voltage. My money is on the AVR (first problem).

I'd put a meter across both lines (240 volt output), start it up, and record the reading you get when the field breaker is closed. This will tell you how to proceed.

Keith

Last edited by Vanman; 03-20-2019 at 02:58:06 PM.
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
  #9  
Old 03-21-2019, 01:38:12 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

Thanks for the ideas. I have tested the items I can including the bridge rectifier in the generator end bell.

Not looked at the AVR board as it is either working or going full field as suggested. The 250V cap on it deserves respect as it looks to have a 120v 4 turn winding for the AVR and idle control system on it.

I will isolate the idle control board in case it's the source of a short.

So I will put it back together and see what the voltages are this weekend. I will also check the engine RPM with an optical tach just to be sure.

Thanks for the suggestion for the 240V mode getting the best result. Looks like 120v only mode ties the two windings together by reversing one of them in the select switch in reference to ground etc.
Reply With Quote
  #10  
Old 03-21-2019, 01:43:40 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

AVR and Idle board pics. I cut one of the zip tie off to check the 120V/240V single turn wire for shorts on the transformer.
Attached Thumbnails
Click image for larger version

Name:	AVR.jpg
Views:	63
Size:	168.4 KB
ID:	331094   Click image for larger version

Name:	idle_control.jpg
Views:	54
Size:	136.6 KB
ID:	331095  
Reply With Quote
  #11  
Old 03-31-2019, 05:38:58 PM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

I don't have a year specific service manual. However the one I could find calls for: no-load 3750 RPM and to hold 3600 RPM under full-load. Linked below.

I measured 164-166VAC, identical, on each 120V winding. So 164/164 to 166/166. Looks like the regulator is full field till the thermal overload device trips off.

RPM via optical hand held tach:
No Load: 3920 RPM
Breaker in: 3620 RPM

Yes, running a little fast unloaded. Has throttle left so governor is still working.


https://www.yumpu.com/en/document/re...parkinlube/113
Reply With Quote
  #12  
Old 04-07-2019, 02:48:53 AM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

I can't find a fan available anywhere.
P/N: A53769 FAN NLA

P/N: A48999B VOLTAGE REGULATOR NLA

The Voltage regulator is available on eBay as a aftermarket part. But asking ($154.75 shipped) is more than this set is worth.

Fort Rock Improved Voltage Regulator
eBay item number:
181418183370

I can't imagine something that lasted 30 years is "unreliable" as the eBay listing goes on about. They appear to be selling very well so what do I know...

The part numbers are on everything on the VR including the big NPN power transistor: MJ16010 Motorola NPN Transistor.

Anything that commonly burns up on the VR's?
Reply With Quote
  #13  
Old 04-07-2019, 04:28:25 AM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,638
Thanks: 3,728
Thanked 4,938 Times in 2,061 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

Okay....
1. OMB stocks your fan. https://www.ombwarehouse.com/homelit...bo-a53769.html

2. Unless I have totally misread this entire thread THIS ISN'T AN ELECTRICAL CONTROL PROBLEM.. The engine runs at full throttle, CAUSING regulator to trip out breaker. Fix the engine RPM! Problem will go away.
Doc
__________________
'The time has come', the Walrus said,'To talk of many things: Of shoes and ships and sealing-wax Of cabbages and kings'
Reply With Quote
  #14  
Old 04-07-2019, 11:05:06 AM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 6,011
Thanks: 9,899
Thanked 2,829 Times in 1,906 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

His post #11 confirmed what I suspected and suggested all along. Faulty regulator stuck at full excitation. That modestly fast governor setting would not cause the observed results. I wonder if this would be a suitable application of the handily cheap SX-460 that everyone talks about?

Keith
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
  #15  
Old 04-07-2019, 11:21:24 AM
Wayne 440 Wayne 440 is online now
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 7,390
Thanks: 485
Thanked 6,893 Times in 3,199 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

Quote:
Originally Posted by Vanman View Post
...I wonder if this would be a suitable application of the handily cheap SX-460...
If it was my set, I would try one, "suitable" or not. No way (no offense to the OP) that I would spend $150 on something like this.
Reply With Quote
The Following 2 Users Say Thank You to Wayne 440 For This Post:
  #16  
Old 04-08-2019, 01:55:14 AM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

How risky is it to run with the cracks in the fan?
Sigh... OMB fan... "In Stock At Distributor: No"

No Load: 3920 RPM is 65.3 HZ
Thermal Breaker in: 3620 RPM is 60.3 HZ

I took a close look at the VR today. Not even coated so repair is as easy as it gets.

Couple things stand out:
MJ16010 Motorola NPN TO3 Transistor.
LM358N Low Power Dual Operational Amplifier. Got to be a similar design to the Generac reverse engineered VR around here.

The heavy lifting is done by the TO3 package NPN as in field brush to ground. Good place to start as any. Sure enough it's shorted out. C-E measures 18 Ohms both ways: The Transistor is toast! I removed it just to be 100% sure on measurements. Other transistors up the control path (on the base pin) of the TO3 appear ok. (That would be the two big ones held down by the white stuff.)

So spent an hour looking up spec sheets... Nothing in my TO3 junk box is rated to take the punishment of 20A and the extreme 450V the MJ16010 can. A higher rated MJ16010A appears to be more available today. My junk box does have a heat sink to "improve" the design.

So the repair looks like it can be done for $20 for a transistor off of eBay (pair for sale for this amount, maybe they sell just one?) or $20 for a SX-460...
Attached Thumbnails
Click image for larger version

Name:	IMG_20190407_195648_01.jpg
Views:	44
Size:	333.0 KB
ID:	332319   Click image for larger version

Name:	IMG_20190407_195621_01_01.jpg
Views:	35
Size:	214.0 KB
ID:	332320   Click image for larger version

Name:	20190407_185147.jpg
Views:	41
Size:	270.7 KB
ID:	332321  
Reply With Quote
The Following 2 Users Say Thank You to Warwagon For This Post:
  #17  
Old 04-08-2019, 12:50:30 PM
Vanman Vanman is online now
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 6,011
Thanks: 9,899
Thanked 2,829 Times in 1,906 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

That's pretty cool! While I'm not normally much of a fan of electronics, I do appreciate the nice, old designs that can still be serviced by those that know how. Nice!
Reply With Quote
  #18  
Old 04-10-2019, 02:43:37 AM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

I took another look at this board to confirm an answer I got in the SX-460 thread.

It has patent number on it.

https://patents.google.com/patent/US4697135A/en

The patent has a description of how it actually works in extreme detail.

I found the following info from it very interesting:

Commercial generators produced utilizing a power transformer to regulate the output voltage typically have regulated output voltage to about ±4%, and motor starting ability is about 0.35 hp/kw. These values are less than desired.

... electronic voltage regulator ... it is possible to regulate the output voltage of the generator so that it is about ±0.8%, and to provide a motor starting ability of about 0.75 hp/kw.
Attached Thumbnails
Click image for larger version

Name:	US4697135-drawings-page-2.jpg
Views:	31
Size:	77.0 KB
ID:	332418  
Reply With Quote
The Following 2 Users Say Thank You to Warwagon For This Post:
  #19  
Old 04-10-2019, 07:27:15 AM
Kevin K Kevin K is offline
Subscriber
 
Join Date: Jan 2005
Location: Mechanicville, New York, USA
Posts: 4,276
Thanks: 4,211
Thanked 4,688 Times in 2,408 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

If you can find some time, it would be interesting to compare the circuit diagram in the patent to the actual circuit board, and add some component values.
Reply With Quote
  #20  
Old 07-31-2019, 11:05:29 AM
Warwagon Warwagon is offline
Registered
 
Join Date: Mar 2019
Location: Fountain Hills, Arizona
Posts: 35
Thanks: 48
Thanked 17 Times in 8 Posts
Default Re: 3800W 120/240V Homelite Textron generator goes full throttle till overload trips

IT'S ALIVE!

I found severe "rust" on the wire connectors going to the thermal overload breaker. I suspect this didn't help.

I cleaned the rust up and replaced the big power transistor. Also added overkill of a heatsink I had around. Some insulation between the heatsink and MOV surge to make sure it doesn't get any ideas of shorting to the heatsink.

Fired up and got 121v on each leg. Ran a 1500W heater for 45 min and voltage still checked out.
Attached Thumbnails
Click image for larger version

Name:	repaired_regulator.jpg
Views:	24
Size:	647.0 KB
ID:	340427  
Reply With Quote
The Following 3 Users Say Thank You to Warwagon For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Full throttle Saloon Internationals Fairmontman Antique Engine Photos 3 02-19-2016 07:45:08 AM
HATZ / BMW marine - Stuck on full throttle! egilman Antique Marine Engines and Outboard Motors 3 06-19-2014 01:53:45 AM
Coleman Powermate 5000 only runs full throttle robvann Generators & Electric Motors General Discussion 11 12-27-2013 10:29:34 AM
Question re. Homelite Textron Generator G-3600-2 walkingbc Generac Generators (SEARS, etc.) 3 09-21-2010 05:58:58 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:47:02 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277