Marathon Magnamax 300kw reconnect
this thread has 7 replies and has been viewed 273 times
Old 08-26-2019, 08:50:28 PM
J.B. Castagnos J.B. Castagnos is online now
Default Marathon Magnamax 300kw reconnect
I have a Marathon 300kw generator, tag on the enclosure says 480 volts. The tag on the generator is hard to read but it looks like 277/480 volts. The business that's interested in it is fed by high voltage, 480? to a transformer then to a transfer switch. I was wondering if the machine could be wired to feed the transfer switch. I took the cover off the generator and there are 12 leads coming out, I didn't read them all but it looks like they are tagged 1 through 12, no L or T. The machine was rebuilt, don't know if this is rebuilders tags or factory. Should they just get a 300 KW transformer, a 480V transfer switch to go before the existing transformer, or try to reconnect it? If reconnected does the voltage regulator automatic sense the correct voltage or would it have to be addressed?
Old 08-26-2019, 09:59:46 PM
Email NOT Working
Default Re: Marathon Magnamax 300kw reconnect
Just reconnect it for the voltage the transfer switch runs at. If the info is not inside the generator box then a call to Marathon should get it. It will require minor adjustment after reconnection but not much else.
Old 08-27-2019, 05:43:54 PM
scottie scottie is offline
All the reconnect info and diagrams are available on the Marathon website
The Following User Says Thank You to scottie For This Post:
Old 08-27-2019, 06:47:48 PM
Thanks Birken and Scottie, I looked at the web site, talked to Marathon, very helpful. I was wondering how the regulator would adapt, Mike at Marathon explained that the regulator see's 240 in the center of the 480 configuration, will see the voltage at the line on 208, will have to be lowered.This is new to me but I really enjoy doing it and learning.
Old 08-28-2019, 12:49:49 AM
One 'bad' news is now you will need a new ~1200 amp breaker, and those are NOT cheap. You'll also need more copper between the gen and ATS. Are you sure you can't reconfigure the ATS? How many amps is the ATS?
Old 08-28-2019, 04:53:11 AM
I would have liked to see them buy a 300kva transformer, I see them offered for $2-3000 used. It may work out OK though, the unit is oversized for the transfer switch building, about 15 feet of cable needed here. I think the generator has a 600 amp breaker, will have to check. If this will be enough to supply the switch they may be able to add two 200 amp breakers to supply an office and a laundromat, these are within 100 feet.
Old 08-28-2019, 01:12:32 PM
i DO NOT recommend hooking a transformer directly to the output of a generator, such that it has to start and stop directly connected. They make all kinds of ugly noises when you do that.
If you're going to have other feeds to more ATS at 208 volts, best to reconfigure now.
Old 08-28-2019, 01:46:28 PM
All of the transfer switches will be manual.
300kw - scrap? trukinbear Onan Generators 47 01-23-2019 01:04:51 AM
Delco AC Model Y1-4907 M2 300Kw Burningoil Generators & Electric Motors General Discussion 2 01-11-2014 12:43:43 AM
Reconnect Question Cruiser Onan Generators 3 12-03-2010 12:52:56 AM
Marathon generators Roger Hayenga Generators & Electric Motors General Discussion 1 02-09-2003 10:41:58 PM