Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts


this thread has 8 replies and has been viewed 679 times

Reply
 
Thread Tools Display Modes
  #1  
Old 06-12-2019, 11:17:07 AM
James A. B. James A. B. is offline
Registered
 
Join Date: Jun 2019
Location: Lucerne Valley, California
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Angry Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Generac Guardian Standby Generator
(model)item#:0041094, s/n:35254444,volts:120/240, amps:66.6/33.3, watts:8000
My Generac generator (when rocker switch is set to manual) starts, runs for maybe 10 seconds then shuts down, restarts (on it's own) and shuts down again in lesser time. These are the same symptoms as if the High Temperature Sensor would be faulty. History- I have had trouble with the Low Oil Pressure Sensor, the High Temperature Sensor and the main Regulator from the propane tank.
These problems occurred in a short period of time, couple months each and after each issue the generator worked fine after faulty part replacement. My current problem has the same symptoms as if the High Temperature Sensor is bad but there are there aren't any Fault LED's lit. When the ambient temperature would get hot enough the generator would stay running as if there isn't any problems. I have connected a Water Column Gauge to the demand regulator (internal regulator thats connects to the carburetor) and the Gauge reads 11.5" to 12" Water Column which is the proper pressure. For fuel I use a 7 gallon propane tank and have been using that size tank for 8 years without any problems. I have researched this problem through the internet and have not found any answers or anybody else having this problem. It definitley has me baffled and I would truly appreciate anybodys input. Thanks
Reply With Quote
Sponsored Links
  #2  
Old 06-12-2019, 12:04:44 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,665
Thanks: 2
Thanked 938 Times in 653 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Is it putting out voltage during the short time it runs? Some of these will shut down if they don't see voltage output and restart in hopes of exciting the field again.
Reply With Quote
  #3  
Old 06-22-2019, 09:41:22 PM
James A. B. James A. B. is offline
Registered
 
Join Date: Jun 2019
Location: Lucerne Valley, California
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Hi Birken,
I finally had a cool temperature morning recently in the high desert of SoCal and tested the AC after starting the generator and it was putting out 124 volts AC. But what baffled me (again) is the generator didn't shut down like it has been in cooler temperatures. I just don't understand WHY! Thanks for the input. I will be testing the AC output everytime I start the generator until the time it will shut down to get your question answered. Thanks again.
Reply With Quote
  #4  
Old 08-15-2019, 11:30:21 PM
James A. B. James A. B. is offline
Registered
 
Join Date: Jun 2019
Location: Lucerne Valley, California
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Hi Birken,
I recently had my generator shutting down again and tested the AC voltage and it appears I'm getting the excitation voltage of 15.7 AC volts. Is it my understanding that if I'm getting the excitation voltage then the voltage regulator is supposed to kick in and produce the 120/240 voltage? If so would you happen to have any idea what in the voltage regulator would work on hot but not cooler temperatures?
Reply With Quote
  #5  
Old 08-16-2019, 12:27:14 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,665
Thanks: 2
Thanked 938 Times in 653 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Put 12 volts momentarily to the wire with the printed number 4 on the voltage regulator (while running) and see if it "takes off" and starts making 120 volts.
Reply With Quote
  #6  
Old 09-10-2019, 11:12:07 PM
James A. B. James A. B. is offline
Registered
 
Join Date: Jun 2019
Location: Lucerne Valley, California
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Hi Birkin, I tested my Generac Guardian generator today using a service manual that belongs to newer Generac models. I did the test 4 - Fixed Exitation Test/ Rotor Amp Draw Test which had me test the voltage regulator related to your suggestion. The 1st test was to remove wire 4 from voltage regulator and connect jumper wire from 4 to wire 15 the 12 volt fused battery supply and remove wires 2 and 6 from voltage regulator and connect multimeter test probes to test the AC voltage output. The AC voltage output was 87Vac. 2nd test Reconnect wire 2 and 6 then disconnect wires 11 and 22 and put test probes on these wires and record the AC voltage also. The reading on these wires showed 80Vac, reconnect wires 11 and 22. 3rd and 4th test was to set multimeter to DC amps remove jumper from wires 4 and 15 and connect one probe to wire 15 and other probe to already disconnected wire 4 and record static rotor amp draw and running rotor amp draw. The static rotor amp draw was 0.705A and the running rotor amp draw was 0.650A. Reconnect everything. The problem I'm having is Test 4 results chart are for the newer models which have different specifications/readings than my model. I also wanted to mention that taking the wires off the voltage regulator I had noticed a bluish color residue on the majority of the voltage regulator male pins and female connectors. They cleaned up easily and it wasn't very hot today and the generator didn't shut down. That residue might have been the problem I won't know for sure until the weather gets cooler. I tried getting my model rotor amp test specifications but not succeeding. Would you or anyone else might have an idea where I can get a service manual for Generac Guardian generator model/ item # 004109-4. Thank you again for all your help. James
Reply With Quote
  #7  
Old 09-10-2019, 11:25:21 PM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,665
Thanks: 2
Thanked 938 Times in 653 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

I have done that test in the past but too complicated to follow over this forum format.

Do I understand it makes voltage sometimes and doesn't other times?

In any case, these old units are known for doing this sort of mischief and consider how much you want to pour into it before committing too much.
Reply With Quote
  #8  
Old 09-12-2019, 03:27:14 PM
James A. B. James A. B. is offline
Registered
 
Join Date: Jun 2019
Location: Lucerne Valley, California
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Yes, that was my problem. Started, ran for 10 seconds, shuts down then restarts and shuts down again. When it did that I was getting 17.4 Vac at the output which I assume is the excitation voltage for the voltage regulator. Now after cleaning the connections, during the Test 4 I mentioned, on the voltage regulator and connecting wires I have not had a problem of the generator shutting down. I ran it again this morning with no problems. The biggest mystery I would like to have a logical answer for (if cleaning voltage regulator hookups is a 100% fix) is why would it run without any problems during hot weather. SMH
Reply With Quote
  #9  
Old 09-12-2019, 04:21:02 PM
radiodoc radiodoc is offline
Registered-I
 
Join Date: Mar 2017
Location: Dierks, Arkansas, USA
Posts: 228
Thanks: 121
Thanked 148 Times in 82 Posts
Default Re: Generac Guardian Gen 8kw Starts, Runs, Shuts down Then Restarts

Just a wild guess but perhaps the contraction of the metal in the contacts when cooler and the blue residue was creating a high resistance in the connection...
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generac 0047000: Shuts Down After AC Runs for a Few Minutes Danceswithbeercans Generac Generators (SEARS, etc.) 11 07-24-2018 02:52:19 AM
17kw generac starts and shuts down after 2 sec wstang254 Generac Generators (SEARS, etc.) 11 11-21-2012 11:50:30 AM
Generac 17kw starts n shuts down wstang254 Generac Generators (SEARS, etc.) 13 11-17-2012 04:00:59 AM
Onan 6.5MCCK-3CR/1H Starts runs for 45 seconds and shuts off truk911 Onan Generators 4 10-16-2011 03:47:58 PM
Onan 4.0 BFA runs and dies but restarts r68grumpy Onan Generators 9 04-28-2010 10:34:13 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:59:01 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277