Rectifier Electrical / Electronic Question


this thread has 30 replies and has been viewed 959 times

Reply
 
Thread Tools Display Modes
  #1  
Old 11-21-2018, 05:54:46 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 4,854
Thanks: 6,532
Thanked 2,085 Times in 1,424 Posts
Default Rectifier Electrical / Electronic Question

Suppose I have a 60 volt, 50 ampere, single phase AC source, and I want to supply a 30 volt, 100 ampere DC load.

The source and the load need not be isolated.

Center tapped transformer secondary windings in conjunction with two diodes are frequently employed so as to achieve full wave rectification without the need for a four diode full wave rectifier.

I wish to use a single winding transformer with a center tapped 60 volt winding, and two diodes, connected across the source.

The question is: What is the required ampacity of the transformer winding?

I believe it would be 50 amperes. Is this correct?
Attached Thumbnails
Click image for larger version

Name:	IMG_20181121_135527348.jpg
Views:	64
Size:	47.7 KB
ID:	323318  
Reply With Quote
Sponsored Links
  #2  
Old 11-21-2018, 06:08:22 PM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,060
Thanks: 3,087
Thanked 4,129 Times in 1,748 Posts
Default Re: Rectifier Electrical / Electronic Question

Roughly... rule of thumb is 20% overhead on desired rating. Critical design spec for transformers however isn't amps, but VA, or basically continuous heat load on windings without release of magic smoke.

For the kind of load you are looking for though, I'd go for a switching supply.
Doc

If you could live with 220VAC input TWO of these in paralell would cover it for roughly $200 https://m.banggood.com/AC-200V-250V-...yABEgJShvD_BwE
__________________
"There is always some yayhoo turning left!" - my father.

Last edited by Thaumaturge; 11-21-2018 at 06:31:00 PM. Reason: Fat fingers, touch keyboard.
Reply With Quote
  #3  
Old 11-21-2018, 06:26:51 PM
Bob Willman Bob Willman is offline
Registered-II
 
Join Date: Sep 2009
Location: Bowling Green, Ohio
Posts: 400
Thanks: 1
Thanked 229 Times in 153 Posts
Default Re: Rectifier Electrical / Electronic Question

Is your input voltage RMS AC or a peak voltage? What your diagram shows is not a standard transformer which would have 2 windings, a primary and a secondary. If you are going to draw 100 A from the winding, the wires in the winding must be capable of 100 A. The diodes will also need to be rated for 100 A. Without some capacitors after the diodes the output will be pulsed DC not a true DC voltage. I'm not sure your circuit will do what you want it to.

Bob
WB8NQW
Reply With Quote
  #4  
Old 11-21-2018, 07:48:20 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 4,854
Thanks: 6,532
Thanked 2,085 Times in 1,424 Posts
Default Re: Rectifier Electrical / Electronic Question

The AC voltage of the supply is RMS. The circuit is just going to be charging a big battery, sometimes with a load on it. So it doesn't need to be clean or smooth or even regulated DC.
Reply With Quote
  #5  
Old 11-21-2018, 08:41:45 PM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,994
Thanks: 260
Thanked 792 Times in 616 Posts
Default Re: Rectifier Electrical / Electronic Question

do it in Watts

100x30=3000 watts

3000/117 about 26 amps
3000/60 is yes 50 amps

RMS volts not peak
__________________
.
by using this free advise, you, your heirs, etc
absolve, save, and hold harmless the advisor.
CAVEAT EMPTOR
YMMV
Reply With Quote
  #6  
Old 11-21-2018, 10:14:34 PM
DMeed DMeed is offline
Subscriber
 
Join Date: Nov 2014
Location: Victoria Corner, New Brunswick, Canada
Posts: 294
Thanks: 176
Thanked 127 Times in 80 Posts
Default Re: Rectifier Electrical / Electronic Question

Think about when the diodes are conducting. Each diode is conducting for 1/2 the AC waveform and off for the other 1/2 the AC waveform. So each diode is acting alone. For 100 amps output, you will need 100 amps through each diode and from the transformer windings as well. You are getting the 100A*30V or 3000 watts alternately from each half of the transformer. So the transformer needs to be rated for 6000 watts.

Are the 60V CT transformer windings fed from a separate 60v AC source or are they are the sole source of current for feeding the diodes. It might make a difference if the current through the diode can come from the 60V AC source separately from the transformer winding (and the windings are just splitting the centre. Might work with a 50 amp winding in that case (?someone else will have to chime in on that one?) There was a thread showing how to feed a single phase split 120/120v circuit from a 240v Generator with a transformer rated 1/2 the generator wattage. In any case the diodes will have to be 100 amp anyway.

Thinking further - with diodes in there steering the current each 1/2 cycle I don't see how it would balance the current over both windings.

Last edited by DMeed; 11-21-2018 at 11:01:49 PM.
Reply With Quote
  #7  
Old 11-21-2018, 11:10:14 PM
Railroads Railroads is offline
Registered-III
 
Join Date: Sep 2013
Location: North Carolina, USA
Posts: 1,432
Thanks: 960
Thanked 1,096 Times in 456 Posts
Default Re: Rectifier Electrical / Electronic Question

Keith, What do you need 100 amps at 60v for?

Is this some exciter unit or something?

Robert
Reply With Quote
  #8  
Old 11-21-2018, 11:33:30 PM
G.M.Johnson G.M.Johnson is offline
Subscriber
 
Join Date: Jul 2015
Location: Ann Arbor, Michigan
Posts: 347
Thanks: 162
Thanked 233 Times in 126 Posts
Default Re: Rectifier Electrical / Electronic Question

If it doesn't have to be exactly 30 volts a 36 volt fork truck battery charger will do the trick. You can find them in 208/240 single phase input versions. If you are stuck with exactly 60v input then scratch that idea.
Reply With Quote
  #9  
Old 11-22-2018, 04:10:35 AM
pegasuspinto pegasuspinto is offline
Registered-III
 
Join Date: Oct 2006
Location: Floyd, AR, USA
Posts: 2,756
Thanks: 333
Thanked 1,303 Times in 845 Posts
Default Re: Rectifier Electrical / Electronic Question

Your supply as described will produce about 42 volts DC. Just keep that in mind!
Reply With Quote
  #10  
Old 11-22-2018, 08:32:05 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,994
Thanks: 260
Thanked 792 Times in 616 Posts
Default Re: Rectifier Electrical / Electronic Question

Quote:
Originally Posted by DMeed View Post
Think about when the diodes are conducting. Each diode is conducting for 1/2 the AC waveform and off for the other 1/2 the AC waveform. So each diode is acting alone. For 100 amps output, you will need 100 amps through each diode and from the transformer windings as well. You are getting the 100A*30V or 3000 watts alternately from each half of the transformer. So the transformer needs to be rated for 6000 watts..
I'm not sure that is correct

if the 60 Volt winding is producing 3 KW, [50 A]
each half can produce 1.5 KW. [50A at half the voltage]
summed together after the diodes still 3 KW [half the voltage at 100 A]

the half wave, the diodes are alternately not conducting, does not reduce the total power transferred [IMHO]


the kind of counter EMF kick one can get here it might not be a bad idea to put a MOVs or neon bulbs across the diodes
__________________
.
by using this free advise, you, your heirs, etc
absolve, save, and hold harmless the advisor.
CAVEAT EMPTOR
YMMV

Last edited by armandh; 11-22-2018 at 08:52:35 AM.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 40r bridge rectifier question Coot Kohler Generators 0 10-07-2018 09:50:01 AM
Electrical Question Winchester Smokstak Down Under 15 03-30-2017 01:37:33 AM
Another electrical question suntreemcanic Onan Generators 12 01-30-2015 09:11:12 PM
TJD Rectifier question MikeinBaja Wisconsin Engines 0 06-30-2013 03:46:24 PM
Kohler k series rectifier question Beeline Magnetos, Ignition Coils and Spark Plugs 1 01-10-2013 08:09:16 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 06:10:36 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277