  #21  
Old 03-22-2010, 10:27:11 AM
cornbinder89 cornbinder89 is offline
Registered-II
 
Join Date: Feb 2010
Location: Lyman, Iowa
Posts: 687
Thanks: 33
Thanked 294 Times in 222 Posts
Default Re: Generator parts and frequently asked questions.

Quote:
Originally Posted by armandh View Post
to make the whole bonding issue simple.........
correct bonding makes it impossible for a point of failure in the return path to create a hazardous condition.

]
OK, to a layman, I am haveing trouble following this. I know your not supposed to have more then one bond point.... But, again to a layman, when you open your breaker panel in your house, you see all the nuterals and grounds tied to the same strip. I'm haveing trouble grasping the concept that more is worse then one. If the gen was grounded, the house or other end user grounded with a seperate ground rod, why is this more dangerous then a single ground point with both the nuteral and grounds connected? If I understand why it helps make sure I do it right all the time.
It seams with a single bonding point, a single failure would lead to no grounding and a "floating" nuteral... Am I wrong?
A transfer sw without a nuteral switch could back feed the grid if the ground is lost (do I at least have this correct?) and as such nuterals should be disconnected from the grid when back up power is used... But why the issue of a single bond point?
HELP!!
Reply With Quote
The Following User Says Thank You to cornbinder89 For This Post:
Sponsored Links
  #22  
Old 03-22-2010, 12:39:00 PM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,818
Thanks: 552
Thanked 1,829 Times in 1,195 Posts
Images: 1
Default Re: Generator parts and frequently asked questions.

Chainsawman, No, a CT (Current Transformer) does not need any electrical connection to the measured circuit. It uses Inductive Coupling to sample the Current thru the wire run thru the center of the CT.

cornbinder89, You are not the only one confused by this part of the NEC, Many Electricians, Electrical Engineers, and Electrical Inspectors are also in the same boat. Neutral/Ground Bonding is NOT the real issue here. That is well understood, by almost all. It is when you add a Backup, or Alternate Source, of power to your system, that things get complicated. This issue has only been part of the NEC for the last 15 years and only really became relevant since the issues were documented after all the Y2K Backup Gensets were installed, Tested, and found wanting. Also the introduction of GFI Outlets and Breakers, in the last two decades, has complicated the issue significantly. There are MANY different ways to accomplish this type of connection, but to do it Safely, and where there are minimum chances for a Single Point Failure causing, problems, that persist because a Breaker or Fuse doesn't Trip, is a complicated issue, and that doesn't even get into the Gound Loop part of the Issue. The NEC in this area is just now getting to the point where it is fairly stable, on this issue, as terms like "Separately Derived Source" definitions, have been in the NEC for a few years, and are taught in ALL Apprentice Courses. My buddy sits on the NEC Board that writes the code, and teaches NEC to Inspectors, Electricians, both Master, and Journeyman, as well as the Apprentice Courses, and he insists that this section of the NEC is the least understood, and most miss-applied Section.
__________________
Bruce in alaska
Reply With Quote
The Following 2 Users Say Thank You to BTPost For This Post:
  #23  
Old 03-22-2010, 01:41:27 PM
cornbinder89 cornbinder89 is offline
Registered-II
 
Join Date: Feb 2010
Location: Lyman, Iowa
Posts: 687
Thanks: 33
Thanked 294 Times in 222 Posts
Default Re: Generator parts and frequently asked questions.

Do you have a good source that does help explaine it? Looking at how my house is wired, I already see things that I doubt are to code. I am thinking about adding a transfer sw (at least my main disconnect is on the yard pole, so easy to make it a full transfer.). I want to have a full understanding of what should be, before tackleing what is!
Reply With Quote
The Following User Says Thank You to cornbinder89 For This Post:
  #24  
Old 03-22-2010, 02:18:15 PM
Jim Rankin Jim Rankin is offline
Registered-III
 
Join Date: Nov 2004
Location: Faunsdale, Alabama USA
Posts: 4,436
Thanks: 71
Thanked 1,185 Times in 967 Posts
Default Re: Generator parts and frequently asked questions.

http://www.ecs.umass.edu/ece/hollot/...DS06/ESD_2.pdf

A 2.12 MB PDF file that shows grounding and bonding for both transformers and transfer switches as well as equipment grounding and ground fault interrupting devices.
Reply With Quote
The Following 2 Users Say Thank You to Jim Rankin For This Post:
  #25  
Old 03-22-2010, 02:41:06 PM
Chainsawman1 Chainsawman1 is offline
Registered-II
 
Join Date: Dec 2008
Location: Napa, California
Posts: 116
Thanks: 52
Thanked 6 Times in 6 Posts
Default Re: Generator parts and frequently asked questions.

Hey armandh....(SHIPMATE)
I dont remember any CT Meters in the Navy.
I dont even think we cared how much power we used.
But I know we used loads of it. Did I miss something?
I do remember we had to go light up san francisco when PG&E croaked.
Reply With Quote
  #26  
Old 03-23-2010, 12:55:15 AM
Chainsawman1 Chainsawman1 is offline
Registered-II
 
Join Date: Dec 2008
Location: Napa, California
Posts: 116
Thanks: 52
Thanked 6 Times in 6 Posts
Default Re: Generator parts and frequently asked questions.

1-Q: How many amps will it take to kill you?
A: Female, 50 miliamps for 2/10 of a second,for male, 75 miliamps for 1/2 of a second will send heart into ventricular fibrilation.

2-More than 6 ma current passes through your heart shall KILL you.
Reply With Quote
  #27  
Old 03-23-2010, 08:19:17 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 2,995
Thanks: 260
Thanked 793 Times in 617 Posts
Default Re: Generator parts and frequently asked questions.

and simple E=IxR tells you that lowering the contact resistance with water or increasing the voltage will increase the current

using a large gen to feed several transfers would require doing it much like a large building distribution

bonding at the generator
overload protection for the feed to each transfer
bonded disconnects at each meter base
transfers that have neutral transfer
and isolated neutral distribution panels after the transfer


or transfer only the largest panel and provide several small emergency runs
to emergency transfer and sub panels in outbuildings.


as to why
here in MO a kid got killed climbing on to a boat dock
the 3 wire hookup became hot when the neutral got loose

there must be independent earth ground and neutral returns to the bonding point. deadly situations exist when conductors fail and the current seeks an alternate return path through you

incorrect bonding/grounding provides that alternate route.
Reply With Quote
The Following User Says Thank You to armandh For This Post:
  #28  
Old 03-23-2010, 01:25:48 PM
Fred M. Fred M. is offline
Registered-III
 
Join Date: Sep 2006
Location: Titusville, Florida, U.S.
Posts: 792
Thanks: 32
Thanked 152 Times in 147 Posts
Default Re: Generator parts and frequently asked questions.

It may be slightly off topic, but how about adding a link to one of Walmart's new boxes:

<http://www.walmart.com/catalog/product.do?product_id=12568628&findingMethod=rr>

Fred

Last edited by BTPost; 03-23-2010 at 01:53:29 PM. Reason: Funny, but not quite germane to the conversation...
Reply With Quote
  #29  
Old 03-23-2010, 01:50:32 PM
Chainsawman1 Chainsawman1 is offline
Registered-II
 
Join Date: Dec 2008
Location: Napa, California
Posts: 116
Thanks: 52
Thanked 6 Times in 6 Posts
Default Re: Generator parts and frequently asked questions.

Now that is the only electric box that I dont want!!!
You dont get a meter or big switch or even a little green light.
Reply With Quote
  #30  
Old 03-24-2010, 10:57:11 AM
Chainsawman1 Chainsawman1 is offline
Registered-II
 
Join Date: Dec 2008
Location: Napa, California
Posts: 116
Thanks: 52
Thanked 6 Times in 6 Posts
Default Re: Generator parts and frequently asked questions.

I was even thinking about why people dont use a rubber mat 6000 volt..
To stand on.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Frequently Asked MEP Questions Harry Military MEP and Aircraft Gen-Sets 5 04-15-2018 11:05:21 PM
Frequently Asked Generator Questions Harry Generators & Electric Motors General Discussion 26 02-27-2018 10:45:28 PM
Frequently Asked Kohler Questions Harry Kohler Generators 15 12-16-2017 01:35:45 PM
Generac Frequently asked Questions (FAQ's) BTPost Generac Generators (SEARS, etc.) 2 03-20-2017 12:29:35 PM
Frequently asked Questions (FAQ's) BTPost Honda, Yamaha, Kawasaki, Isuszu Generators 0 02-27-2009 02:58:47 PM