Kohler 15R063 Marine Generator Will Not Crank


this thread has 11 replies and has been viewed 813 times

Reply
 
Thread Tools Display Modes
  #1  
Old 08-22-2018, 09:49:11 AM
reedb reedb is offline
Registered
 
Join Date: Aug 2018
Location: Bowen Island, British Columbia, Canada
Posts: 5
Thanks: 0
Thanked 3 Times in 1 Post
Default Kohler 15R063 Marine Generator Will Not Crank

Kohler Generator: 15R063
Spec: 6640C
S/N: 289259
32V starting
Control: B/268198

The unit will not crank and is blowing the 15A glass fuse in the control. Unfortunately the wiring diagram is no longer legible. Calling the local distributor brought no joy (he wasn't able to find the diagram). The unit has a Roosa injector pump with two wire connections. I assume one is the fuel cutoff. I have no idea what the other would be. I suspect the engine might be a Waukesha Diesel Model 180DLC, but I haven't been able to find the number plate yet. If anyone might have a wiring diagram for this control that would be a huge help. Also any general knowledge about how the remote start switches were wired would be great (I suspect hackery in this area).
Thanks, -Reed
Reply With Quote
Sponsored Links
  #2  
Old 08-22-2018, 06:49:22 PM
nblack nblack is offline
Registered-I
 
Join Date: Dec 2012
Location: Rutledge, Tennessee
Posts: 193
Thanks: 127
Thanked 88 Times in 68 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

1. check the FAQ on this section, post #2. very helpful.
2. Is the engine loose? i.e. can you turn it over with a ratchet, or bar.
3. How long has it been sitting? months, years, decades...
4.depending on the answer to the previous question, the approach to any movement of the crank by hand or electricity changes.
5. Wookies are a FORMIDABLE power source, and should be revered as such. Their design speaks volumes with regard to the engineers perception of longevity, serviceability,and overall value.
6. Roosa-master pumps have been used in countless diesels, and many updates are available for them as well.
7. Wookies normally have their id badge on the LH side right below the valve cover, riveted to the block. (all that I have seen) (others may correct with more experience).
8. report back, and PLEASE continue to do so as your unit undergoes repair. It helps many people, not just you.
9. Last, but not least, Welcome to the 'Stak!.,and best of luck!

Last edited by nblack; 08-22-2018 at 06:50:35 PM. Reason: welcome!
Reply With Quote
  #3  
Old 08-22-2018, 07:02:30 PM
LWB250 LWB250 is offline
Registered-III
 
Join Date: Oct 2008
Location: Tampa, FL USA
Posts: 1,430
Thanks: 27
Thanked 445 Times in 385 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

This is probably an exciter cranked unit. If it is (no external Bendix style starter like you would have on an automotive engine) then having strong batteries, heavy cables and clean connections is absolutely critical.

Slapping a Group 24 battery on this unit will result in nothing. Exciter cranked units use the generator exciter windings to crank the engine over, and as a result require a massive amount of current to turn the unit over.

Dan
Reply With Quote
  #4  
Old 10-10-2018, 11:03:47 AM
Roamer Roamer is offline
Registered
 
Join Date: Oct 2017
Location: Slidell, Louisiana
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

Hey my friend I think this is your lucky day. I have the same unit as you. If you have a good knowledge of electric schematics, I think I have what you need. Let me search and see if I can locate the schematics for this unit. First as others have asked, does it rotate at all when attempting to crank it over? If the wiring to the batteries is in good condition along with connections clean and tight, the reset button is depressed, the start relay is probably gone bad. A quick test may help. When attempting to crank, does the reset button pop out? If it does, use caution here, hold in the reset and attempt to crank it over, for only a second or two. If it does the you have isolated the problem to the overload switch or starting relay or possibly a bad cutout switch i.e. LOP, high temp. If no response the you'll have some tracking to do to find out where in the starting circuit the problem lies.
Reply With Quote
  #5  
Old 10-10-2018, 05:59:43 PM
LWB250 LWB250 is offline
Registered-III
 
Join Date: Oct 2008
Location: Tampa, FL USA
Posts: 1,430
Thanks: 27
Thanked 445 Times in 385 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

Call one of the distributors I mentioned in the FAQ section and tell them you need a drawing number 268202. Be sure to ask for the service department, NOT parts department.

Either one of them will have a copy of this drawing. Our you can call Bay City Electric in San Diego since they're a little closer. They'll have it, too.

Dan
Reply With Quote
  #6  
Old 03-03-2019, 06:15:58 PM
reedb reedb is offline
Registered
 
Join Date: Aug 2018
Location: Bowen Island, British Columbia, Canada
Posts: 5
Thanks: 0
Thanked 3 Times in 1 Post
Default Re: Kohler 15R063 Marine Generator Will Not Crank

First of all thanks to those who replied. I removed the screen and was able to roll the generator by hand. Thus emboldened, I jumped around the start solenoid and was able to get the generator to crank. This is an exciter cranked unit, no starter. I've attached my partial wiring diagram for the control. I had no luck with the local dealer when asking for drawing number 268202. Claimed that his documents didn't go back that far. If anyone can help fill in the terra-incognito in my partial diagram I can probably get this thing going again. Many thanks in advance. -Reed
Attached Thumbnails
Click image for larger version

Name:	B_268198_wiring_diagram.jpg
Views:	32
Size:	187.5 KB
ID:	329848  
Reply With Quote
  #7  
Old 03-03-2019, 06:18:06 PM
reedb reedb is offline
Registered
 
Join Date: Aug 2018
Location: Bowen Island, British Columbia, Canada
Posts: 5
Thanks: 0
Thanked 3 Times in 1 Post
Default Re: Kohler 15R063 Marine Generator Will Not Crank

We're still working on the 15R063. If you have a diagram which is better than the one I posted, I would love to see it. Thanks, -Reed
Reply With Quote
  #8  
Old 03-03-2019, 06:55:34 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,405
Thanks: 8,205
Thanked 2,405 Times in 1,638 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

One thing you will want to do before you put a load on the set is to replace the selenium rectifier shown on the diagram with a silicon rectifier. This rectifier is in series with the auxiliary field winding and the compounding transformer. As AC load is increased, DC auxiliary field current is increased proportionally. This keeps the output voltage ~constant across the load range.

The selenium rectifiers fail merely with age. In this circuit, when it fails open circuit, a very high voltage is developed across the transformer, destroying it.

Keith
Reply With Quote
The Following User Says Thank You to Vanman For This Post:
  #9  
Old 03-03-2019, 08:41:42 PM
reedb reedb is offline
Registered
 
Join Date: Aug 2018
Location: Bowen Island, British Columbia, Canada
Posts: 5
Thanks: 0
Thanked 3 Times in 1 Post
Default Re: Kohler 15R063 Marine Generator Will Not Crank

Thanks for the tip. I have the load disconnected now. I was thinking of replacing the selenium bridge rectifier, but I wasn't sure what the voltage/current rating of the silicon bridge rectifier should be. I'm still really casting about for a better wiring diagram than the one I posted. Even if it's not from the same year, I would like to look at a wiring diagram that gives me the general idea of how these older controllers are wired. I still have a short in the controller somewhere I need to track down. For now we're trying to start the "wookie" to see what it's condition is. Many thanks! -Reed
Reply With Quote
  #10  
Old 03-04-2019, 06:05:55 PM
Kevin K Kevin K is offline
Registered-III
 
Join Date: Jan 2005
Location: upstate New York USA
Posts: 4,145
Thanks: 3,970
Thanked 4,501 Times in 2,318 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

According to the Kohler Field data chart I attached, a 15Kw single phase generator would have an auxiliary field resistance of about 13 ohms and a auxiliary field voltage about 40 volts at full load. This would give a current of about 3 amps. So a 200 volt bridge rated at 10 amps would be a good replacement. I just use a 1,000 volt 50 amp bridge, as they don't cost much more from Digi-Key or Mouser Electronics. The shipping will cost more than the part. I miss Radio Shack when I need a quick part. On the other hand, you can save shipping by purchasing from Ali Express, but you need to wait a few weeks.

https://www.digikey.com/product-deta...861-ND/2214448

If you have Amazon Prime with free shipping that may be the best way to go as Digi-Key and Mouser like to add about $10 for shipping.

https://www.amazon.com/Taiss-KBPC501...s%2C200&sr=8-6

https://www.amazon.com/10pcs-Single-...6S1JHGZEPK0AQN
Attached Files
File Type: pdf Field Data .pdf (74.7 KB, 9 views)
Reply With Quote
The Following User Says Thank You to Kevin K For This Post:
  #11  
Old 03-10-2019, 02:01:08 PM
reedb reedb is offline
Registered
 
Join Date: Aug 2018
Location: Bowen Island, British Columbia, Canada
Posts: 5
Thanks: 0
Thanked 3 Times in 1 Post
Default Re: Kohler 15R063 Marine Generator Will Not Crank

Quick update:

We were able to get the "wookie" started, without the control, by bleeding the Roosa Master Injection Pump and filling the engine with boiling water. Not sure the last time this engine ran, but all of the diesel which we drained from the pump and filter had a very strong varnish smell. Based on the current owner we know it has been at least five years since the last run.

WRT the control: it has been heavily modified with a recent time delay relay which looks like it may have taken the place of the item marked ITS on my partial diagram. Still investigating the short and mods in the control. Thanks to all who have helped! -Reed
Reply With Quote
The Following 3 Users Say Thank You to reedb For This Post:
  #12  
Old 03-12-2019, 06:55:35 PM
mdj21 mdj21 is offline
Registered-I
 
Join Date: Nov 2005
Location: Jacksonville, Florida USA
Posts: 84
Thanks: 7
Thanked 8 Times in 7 Posts
Default Re: Kohler 15R063 Marine Generator Will Not Crank

If you want to put the controller back to original, you can still get that 1TS push button circuit breaker from Digikey. The original was made by ETA and the part number was 46-400-P10-A3-Si 4141-245803. The new one is still made by ETA, but their numbering system has changed. The new number that crosses to that old number is 2-6400-IG8-P10-A3-Si-401041.
Reply With Quote
The Following 2 Users Say Thank You to mdj21 For This Post:
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 7.5a27 model number L654ep marine generator 1976 Won't Crank NEED HELP Cody4766 Kohler Generators 7 02-09-2017 10:17:31 PM
Kohler 7.5 marine generator TennHDman Kohler Generators 1 04-09-2015 03:02:21 PM
Kohler 7.5 marine generator Rick Christerson Kohler Generators 19 11-30-2014 02:32:52 AM
Kohler Marine 5E wont Crank turboboss Kohler Generators 0 04-06-2010 01:04:56 AM
Kohler marine generator Christopher Brewer Kohler Generators 1 10-02-2004 03:59:15 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:03:53 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277