Kohler 30RES UU issues


this thread has 6 replies and has been viewed 234 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-18-2019, 11:25:12 PM
Hellrider Hellrider is offline
Registered
 
Join Date: Mar 2019
Location: Kamloops British Columbia, Canada
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Kohler 30RES UU issues

Generator originally had issues faulting on under voltage intermittently. Discovered that the rotor bearing had seized, and spun in the end frame housing. As a result, the SCR module had also failed due to brushes jumping up and down on the slip rings.
Replaced the bearing, frame , and SCR module.
Unit starts and loads up, but every couple of starts it faults on UU still.
Performed separate excitation test- nothing is showing faulty.
Now, I have noticed that the flash relay flickering before the unit shuts down. Voltage signal to the RIB is fluctuating during these events as well.
Now for the question- how do I isolate the control board, or the RIB as the fault?
Could the control board be responding due to poor speed signal?
How do I isolate this?

TIA
Reply With Quote
Sponsored Links
  #2  
Old 03-19-2019, 12:05:24 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,407
Thanks: 2
Thanked 827 Times in 577 Posts
Default Re: Kohler 30RES UU issues

IIRC, the controller grounds wire FL which completes the circuit on the flash relay. The high side of the flash relay coil is hooked to +12VDC. So wire FL has +12vdc on it when inactive and 0vdc on it when active. During active time the slip rings will be receiving battery voltage across them.

I had one do something like this a few years back. The problem was the relay on the relay board. New board, problem solved. Except when the owner tried to start it while connected to load. It would not come up to voltage when it was connected to an external load.
Reply With Quote
  #3  
Old 03-19-2019, 12:37:33 AM
Hellrider Hellrider is offline
Registered
 
Join Date: Mar 2019
Location: Kamloops British Columbia, Canada
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Kohler 30RES UU issues

so the relay is basically allowing battery voltage to the rings as initial excitation till system voltage builds, and is activated by the adc 2100 grounding FL from the RIB?
Reply With Quote
  #4  
Old 03-19-2019, 01:00:06 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,407
Thanks: 2
Thanked 827 Times in 577 Posts
Default Re: Kohler 30RES UU issues

Correct,

1. the LED is in parallel with the relay coil, so it shows when it should be active

2. the relay is double pole so it switches both ground and hot to the field winding, and leaves them float when not activated

3. the control board has its own funny flash pattern, even in normal operation, you will see it blink a couple times, and it happens real fast.
Reply With Quote
  #5  
Old 03-19-2019, 10:42:51 AM
Hellrider Hellrider is offline
Registered
 
Join Date: Mar 2019
Location: Kamloops British Columbia, Canada
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Kohler 30RES UU issues

Ok, so start with new relay board and go from there.
I guess I could prove it, by cutting FL and grounding externally and checking for inconsistent operation?
Tough system to troubleshoot, with out parts swapping, being that there is some form of feedback loop between each component
Reply With Quote
  #6  
Old 03-19-2019, 11:16:03 AM
Birken Vogt Birken Vogt is offline
Email NOT Working
 
Join Date: Sep 2009
Location: Penn Valley, California, USA
Posts: 2,407
Thanks: 2
Thanked 827 Times in 577 Posts
Default Re: Kohler 30RES UU issues

I don't remember how I troubleshot the one I had trouble with, other than thinking it was not so hard to figure. I believe the relay board has power at all times so you can just remove FL from the controller and ground it without anything running. See if the relay works every time. Also remember the relay switches both power and ground at the same time so be checking both.
Reply With Quote
  #7  
Old 03-19-2019, 09:14:52 PM
Hellrider Hellrider is offline
Registered
 
Join Date: Mar 2019
Location: Kamloops British Columbia, Canada
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: Kohler 30RES UU issues

Birken Vogt, thanks for the advice. I will be returning to complete the repair later this week, and I will let you know how I make out.

Thanks !
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 30RES - Fuel Conversion Confusion Adaptel Kohler Generators 3 10-18-2017 10:51:59 PM
Kohler 7kw issues sofl Kohler Generators 6 08-28-2017 07:10:52 AM
Kohler 10RY62 starting issues Kohler Model 10RY62 Serial #451811 rhondabrwn Kohler Generators 2 06-23-2013 08:04:52 AM
Kohler 30RES 1.6L Vortec Water Pump Question savtech Kohler Generators 2 02-13-2013 02:19:39 AM
Kohler 10RZ issues Rick Randall Kohler Generators 11 02-27-2009 06:03:04 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 05:39:17 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277