Kohler L600 vs L654 choke wiring


this thread has 8 replies and has been viewed 237 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-22-2019, 01:21:17 PM
Kenny Crenshaw Kenny Crenshaw is offline
Registered-I
 
Join Date: Nov 2015
Location: Millington, Tennessee
Posts: 51
Thanks: 1
Thanked 13 Times in 9 Posts
Default Kohler L600 vs L654 choke wiring

Someone here was kind enough to lead me to a schematic for the controller on my 6.5 KW with an L600 engine. My original choke is rusty, and so I bought a similar one on Ebay (Sisson 700 series). But, the Ebay chokes are always 6 volt, with only one connection for the 6 volt hot wire. On my unit the original choke had two leads running to it, one is hot all if the time, and one grounds when you hit the starter switch. I would like to use my Ebay 6 volt choke. I noticed on the schematic that the L654 had one wire running to the choke that becomes hot when the engine cranks. Why did they do that, and can I use the L654 wiring along with a resister (I have an old ignition wire in ceramic resister)?
Reply With Quote
Sponsored Links
  #2  
Old 03-22-2019, 08:25:21 PM
jack0 jack0 is offline
Registered-I
 
Join Date: Dec 2015
Location: Burlington, Vermont, USA
Posts: 99
Thanks: 61
Thanked 63 Times in 47 Posts
Default Re: Kohler L600 vs L654 choke wiring

Not sure what you have here. Does your diagram indicate a 2 wire choke?
I have never seen 2 wire chokes on these plants. Could it be that the starting contactor and choke are ground actuated? Which is not the norm.
Usually the choke and starting contactor are energized B+ through the crank-run and coil clearing relays.

Maybe if your starting contactor is ground actuated and you have the aux. terminal that goes B+ you could use the 6v. one wire choke with the correct size resistor.
Reply With Quote
  #3  
Old 03-22-2019, 10:34:44 PM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,454
Thanks: 3,486
Thanked 4,673 Times in 1,961 Posts
Default Re: Kohler L600 vs L654 choke wiring

I think that the hot lead to choke runs from hot lead to coil. If so, just insert a voltage regulator circuit such as this;
using suitable heat sink for both 2N3055 & LM317. ANY beefy enough NPN transistor will work for the 2N3055, including 2SC5200. Voltage output is set by pot.
Doc
__________________
Ever notice that everybody thinks that the way they think themselves is the right way to think, despite any evidence.
Reply With Quote
  #4  
Old 03-22-2019, 11:04:51 PM
Kenny Crenshaw Kenny Crenshaw is offline
Registered-I
 
Join Date: Nov 2015
Location: Millington, Tennessee
Posts: 51
Thanks: 1
Thanked 13 Times in 9 Posts
Default Re: Kohler L600 vs L654 choke wiring

The wiring diagram for my controller shows a two wire setup for the L600 and a single wire setup for the L654. The L654 hot wire runs off of the 2CR relay output that goes into the RR relay. The one wire going to the choke is hot all of the time and the other wire goes to ground through the ignition switch.
Attached Thumbnails
Click image for larger version

Name:	20190322_215646.jpg
Views:	15
Size:	53.3 KB
ID:	331150  
Reply With Quote
  #5  
Old 03-22-2019, 11:12:57 PM
Thaumaturge Thaumaturge is offline
Subscriber
 
Join Date: Mar 2014
Location: Beryl, Utah USA
Posts: 4,454
Thanks: 3,486
Thanked 4,673 Times in 1,961 Posts
Default Re: Kohler L600 vs L654 choke wiring

The 6v ebay choke likely has a hard wired chassis ground. My circuit only drops voltage. But a simple thing to add an automotive relay to circuit you got.
Doc
__________________
Ever notice that everybody thinks that the way they think themselves is the right way to think, despite any evidence.
Reply With Quote
  #6  
Old 03-23-2019, 08:45:07 AM
Kenny Crenshaw Kenny Crenshaw is offline
Registered-I
 
Join Date: Nov 2015
Location: Millington, Tennessee
Posts: 51
Thanks: 1
Thanked 13 Times in 9 Posts
Default Re: Kohler L600 vs L654 choke wiring

So use the L654 wire and a resitor, or the L600 wiring with a relay and a resistor?
Reply With Quote
  #7  
Old 03-23-2019, 01:06:27 PM
jack0 jack0 is offline
Registered-I
 
Join Date: Dec 2015
Location: Burlington, Vermont, USA
Posts: 99
Thanks: 61
Thanked 63 Times in 47 Posts
Default Re: Kohler L600 vs L654 choke wiring

Could you post the complete ladder diagram?

Wondering if this plant was the end run off the L600 during the transition period to the L654. Did they put on the Kohler side draft carb (2 wire choke that's normally seen on the L654) or do you have the Tillotson updraft carb with the Sisson choke on the exhaust manifold?

I have a L654 with a side draft carb and the radiator of an L600. I wonder if those years were a mix and match trying to use up old inventory.
Reply With Quote
  #8  
Old 03-23-2019, 07:55:58 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,979
Thanks: 605
Thanked 1,116 Times in 761 Posts
Thumbs up Re: Kohler L600 vs L654 choke wiring

I wouldn’t use a solid state active voltage regulator to run a choke. Inductive kick is likely to fry the regulator without protection, and active voltage regulation isn’t needed here — this is a non-critical application in terms of voltage stability. Also, for under 5A, you can just use an LM338 and be done.

I’d use either a resistor, if you can easily calculate the load, or a Beefy zener diode reverse connected in series with the choke if you can’t. If you use a 6V zener diode rated for the current of the choke, and connect it “backwards” in series with the choke, that one zener diode will drop 12v down to 6v. A 0.1uF ceramic capacitor across the diode will help a bit with protection. Either the zener or the resistor will be much more robust than an active voltage regulator.

Bill
Reply With Quote
  #9  
Old 03-24-2019, 07:53:19 PM
Kenny Crenshaw Kenny Crenshaw is offline
Registered-I
 
Join Date: Nov 2015
Location: Millington, Tennessee
Posts: 51
Thanks: 1
Thanked 13 Times in 9 Posts
Default Re: Kohler L600 vs L654 choke wiring

It has a Tillotson updraft carb and a Sisson choke. This thread contains a schematic. Thanks.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Kohler 6.5 KW, L600, correct wiring for Sisson choke? Kenny Crenshaw Kohler Generators 0 03-06-2019 12:22:10 AM
Kohler L600 L654 5A61 manuals roundup Kohler Generators 12 10-02-2018 06:25:17 PM
Kohler L654 or L600 Gary Potts Kohler Generators 2 06-14-2011 09:08:18 PM
Difference between Kohler L600 / L654 ? Arthur Kohler Generators 4 12-31-2008 09:11:28 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 05:40:32 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277