Kohler Generators
Kohler 80kw fast response
this thread has 7 replies and has been viewed 242 times
Old 04-28-2019, 07:54:13 PM
2255oliver 2255oliver is offline
Default Kohler 80kw fast response
I am looking for any information on the stud board on my generator if I move down to the bottom studs will that give me single phase or is it still 3 phase. How would i get single phase off this generator
ID:	333632   Click image for larger version
ID:	333633   Click image for larger version
Old 04-28-2019, 08:32:39 PM
Tracy T Tracy T is online now
Default Re: Kohler 80kw fast response
although i am not familar with your unit, most generators go from three to single phase with reconnection of the leads. yours looks like it is built in and is as simple as turning the knob in the 3rd picture to the left, one click to the left of off appears to the 120 and two clicks looks to be 220, both singel phase as noted on the control board
everything to the left side is single phase. but dont take my word for it, i am going from a picture.
a better picture of #2 would help me figure this out.
Old 04-28-2019, 08:41:19 PM
Hope this helps
ID:	333635   Click image for larger version
ID:	333636   Click image for larger version
Old 04-28-2019, 09:21:42 PM
Hope these help
Old 04-28-2019, 10:38:36 PM
Your unit can do high voltage 3 phase (typically 480) or low voltage 3 phase (typically 240 or 208) but does not appear to have any simple way to do single phase. The knob is just a volt meter select knob to pick which leg the volt and amp meters read. It has NO effect on the output voltage whatsoever.
Old 04-28-2019, 11:03:08 PM
LWB250 LWB250 is offline
The studs appear to correspond with the alternator output leads 1-12.
You can get a reconnection drawing for a Fast-Response generator and just "do the math" looking at the connections used for each voltage range.
As for the knob on the meter box, all it does is switch the sensing voltage to the metering. In fact, reconnecting the alternator makes nothing change on the voltmeters, as they're wired across the individual coils.
Dan
Old 05-02-2019, 01:33:25 PM
Zephyr7 Zephyr7 is offline
I just saw this post.
The other posters are correct, the knob is just for the meters. It basically selects what voltage to measure (phase to neutral or phase to phase), and on which of the three phases you want to measure current (amps). It does not change anything regarding output of the generator. The lamps (the “upper” and “lower” meter scales lamps) are set with a jumper on the control board.
All that bolt panel is is a reconnection board configured so as to make basic configuration changes easy and foolproof. You often see these types of arrangements on portable rental generators to make field reconnection quick and easy for people unfamiliar with generator operations.
Any 12 lead generator can be reconfigured for single phase output, but not always at full capacity. Kohler often used what is known as the “zigzag” arrangement which connects the windings in series. The other common arrangement is “double delta” which looks like two triangles connected at one corner, and that corner becomes the neutral. Both configurations are considered standard ways to do it.
You’ll need to identify you generator leads to make the switch to single phase. You probably won’t be able to use the bolt panel alone to do this, you’ll probably need to make up some new jumpers. Aside from that, and some simple changes to the metering and maybe a voltage regulator adjustment, reconfiguring for single phase output is not a big deal.
Bill
Old 05-05-2019, 09:29:28 PM
Thanks for the help everyone
Kohler 80kw fast response 2255oliver Kohler Generators 3 10-15-2018 10:53:15 AM
Kohler Fast Response Generator with Low Output Voltage mklein Kohler Generators 24 08-12-2018 08:29:44 PM
Kohler 20kw: Fast Response 2 RRT74 Kohler Generators 4 01-26-2018 06:32:55 PM
30ROZJ Fast Response II flicker? Isaac-1 Kohler Generators 13 09-04-2016 07:29:27 PM
Kohler 30RZ202 Fast Response 2 - Pre alarm low oil pressure Shah Mat Kohler Generators 2 01-19-2016 08:44:09 PM