Wiring 7.5A27 kohler


this thread has 19 replies and has been viewed 371 times

Reply
 
Thread Tools Display Modes
  #1  
Old 03-31-2019, 08:15:57 AM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Wiring 7.5A27 kohler

How will I hook this up the the house boat wiring, 1970 stardust, already has 3 prong female plug to connect to boat
Attached Thumbnails
Click image for larger version

Name:	received_428484894391733.jpg
Views:	46
Size:	102.5 KB
ID:	331802  
Reply With Quote
Sponsored Links
  #2  
Old 03-31-2019, 12:36:34 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Sounds like you'll want to mount a receptacle to the generator set that matches your existing plug. The generator full load output current will be more than 60 amperes, so may want to mount a small panel, maybe even with just two breakers in it, so you can properly protect the receptacle at it's rating, and maybe have an extra receptacle served off the other breaker.

L1 and L2 are the 120 volt output. You need to follow the wiring and determine with certainty which one is bonded to the generator chassis. That will be your neutral, and needs to connect to the neutral on the receptacle.

Keith
Reply With Quote
  #3  
Old 03-31-2019, 02:34:17 PM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Wiring 7.5A27 kohler

So from what i can tell l2 runs to the neutral/ negative side of the battery. So i will only need 2 wire running out of the generator?
Reply With Quote
  #4  
Old 03-31-2019, 02:58:07 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Yes, the "2" in the model number means that this is a 120 volt, two wire generator. But you also need to run a separate ground wire as well. I am *assuming* that your boat is also 120 volt, since it has only a three prong plug? (Hot, Neutral, Ground)

So, yes, Neutral connects to the terminal that is common to the battery and bonded to the chassis, L2 as you have traced out.

Then your "Hot" comes from the other terminal, should be L1. For a ground, ideally, you'd connect it to the point where battery negative and generator neutral are both bolted to the chassis, normally in the bottom of the controller. Make sure this connection is clean and tight.

Keith
Reply With Quote
  #5  
Old 03-31-2019, 03:39:34 PM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Wiring 7.5A27 kohler

Ok thanks for all the info! One more concern i was when I used a volt meter between L1 and L2 it was showing 208v
Reply With Quote
  #6  
Old 03-31-2019, 04:05:46 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Yes, that would be a concern. Check the speed of the set by checking the frequency. 60 cycles equals 1800 rpm. At no load it should be a bit higher, perhaps 61 ~ 62. Perhaps someone has monkeyed with the governor. Raising the speed would raise the voltage on this type of generator. Also you might check with a small load on it. Sometimes digital meters give erroneous readings due to the nature of the contact between brushes and collector rings. A small load cures this.
Reply With Quote
  #7  
Old 03-31-2019, 06:25:58 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,979
Thanks: 605
Thanked 1,116 Times in 761 Posts
Default Re: Wiring 7.5A27 kohler

Is this one of the gensets that can be configured for 120/240 output? 208v would be low in this case, and would show up as ~104v on the 120 legs.

If it’s only a 120v winding, then 208v is crazy high. Might be a regulator going full field.

Bill
Reply With Quote
  #8  
Old 03-31-2019, 06:33:03 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

The 120 volt Kohlers usually (always?) have only two collector rings and therefore cannot be reconnected for 120/240 three wire service. No regulators on these. Instead they are compounded via a transformer, rectifier, and auxiliary field winding. This works very well, and is very reliable.

But, if your rectifier is the original Selenium unit (finned device) you'll want to replace it with a silicon rectifier before applying a load to the set. The Selenium rectifiers fail with age and, in this circuit, when it fails open, the compounding transformer will be ruined by high voltage across it's secondary. Primary is in series with the load.

BTW, please post a good photo of the nameplate, and of the whole set, just so we can be more certain of what you have.

Keith
Reply With Quote
  #9  
Old 04-02-2019, 10:08:30 PM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Wiring 7.5A27 kohler

I dont have a picture of the generator right now but after a little more messing with it, I got it pushing out 120v and running power. What had me for a loop what the auto start from the AC side. Hooked up a test part to it and fliping a switch on started it right up and producing recommended power
Attached Thumbnails
Click image for larger version

Name:	4291.jpg
Views:	22
Size:	186.7 KB
ID:	331971  
Reply With Quote
The Following User Says Thank You to Kevin 7.5A27 For This Post:
  #10  
Old 04-03-2019, 01:31:39 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Yes, the Kohler Automatic controllers are ingenious, dating at least as far back the early '20's and probably earlier.

Your serial number looks to be from 1971. I'm reasonably certain that will still have a selenium rectifier. A look inside the controller will reveal the answer.

Keith
Reply With Quote
  #11  
Old 04-03-2019, 11:40:15 AM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Wiring 7.5A27 kohler

Where could I go about getting a new one or updated one at?
Reply With Quote
  #12  
Old 04-03-2019, 12:46:34 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Any of the electronics supply houses will have them. Digikey, Mouser Electronics, and a few others I'm not thinking of right off hand. Probably even fleabay.

What you're looking for is a Single Phase Full Wave Bridge Rectifier. They're about one inch square by maybe 1/4" thick. They have a single mounting hole in the center and four 1/4" tab type terminals, two AC input, two DC output. They cost around $3.

This circuit runs at around 40 volts and a few amps at most. All that matters is that the ratings of the rectifier are well above the voltage expected. I ordered a ten pack of 50 amp, 1,000 volt units to get the bulk discount. They don't mind excessive current for a short time, even ten times rated, but absolutely will not tolerate excessive voltage.

In the event of a short circuit on the generator output, the rectifier would be briefly exposed to considerably higher voltage, so I probably wouldn't get one that's less than 400 volts. A 20 amp one would be well more than adequate.

Keith
Reply With Quote
  #13  
Old 04-03-2019, 01:26:39 PM
Kevin 7.5A27 Kevin 7.5A27 is offline
Registered
 
Join Date: Mar 2019
Location: Powell, Tennessee
Posts: 6
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Wiring 7.5A27 kohler

Where would i be able to get a new one for it? Do you have a link?
Reply With Quote
  #14  
Old 04-03-2019, 01:53:36 PM
Kevin K Kevin K is online now
Registered-III
 
Join Date: Jan 2005
Location: upstate New York USA
Posts: 4,138
Thanks: 3,960
Thanked 4,487 Times in 2,312 Posts
Default Re: Wiring 7.5A27 kohler

You can try one of these on Amazon. I like using Mouser and Digi-Key, but there is that little matter of a $10 shipping charge for a $3 part.

https://www.amazon.com/TOOGOO-1000V-...s%2C200&sr=8-5

https://www.amazon.com/Ximimark-KBPC...s%2C200&sr=8-6

https://www.amazon.com/Pieces-Chanzo...s%2C200&sr=8-3
Reply With Quote
The Following User Says Thank You to Kevin K For This Post:
  #15  
Old 04-03-2019, 05:07:00 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,979
Thanks: 605
Thanked 1,116 Times in 761 Posts
Default Re: Wiring 7.5A27 kohler

I’m always a little nervous buying components through amazon since they tend to be China direct specials, so questionable QC. I wouldn’t risk those for anything important. When you buy from digikey, mouser, or any other reputable electronic component distributor you know you’re getting quality parts and not seconds.

I wouldn’t try to save money here since a failure takes out an expensive part just like if the original selenium rectifier were to fail.

Bill
Reply With Quote
The Following User Says Thank You to Zephyr7 For This Post:
  #16  
Old 04-10-2019, 09:32:01 PM
LWB250 LWB250 is offline
Registered-III
 
Join Date: Oct 2008
Location: Tampa, FL USA
Posts: 1,430
Thanks: 27
Thanked 444 Times in 385 Posts
Default Re: Wiring 7.5A27 kohler

I would also suggest that you get a strong MOV or surge suppressor to place across the AC terminals of the bridge rectifier. Snag one from the same supplier as the bridge and combine your shipping costs....

When the fields collapse from the removal of a load, the resulting spike will come back down the line and hit the bridge. This is what typically trashes the selenium rectifiers after they get old. With an MOV across the AC side, it will absorb the spike and prevent the bridge from getting smoked.

Kohler used to sell a kit with a bridge and a huge MOV, but to be honest despite installing tons of these things I couldn't begin to tell you what the value of the MOV is....

Dan
Reply With Quote
  #17  
Old 04-10-2019, 10:21:05 PM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,979
Thanks: 605
Thanked 1,116 Times in 761 Posts
Default Re: Wiring 7.5A27 kohler

All you need is an MOV that will fire above whatever the normal
Operating voltage is but below the PIV rating of the rectifier. If you’re using a 1000v PIV rectifier, I’m sure a 270-300v MOV would be fine.

Note that MOVs are rated for both DC and AC firing and operating voltages. The AC voltage ratings will be lower than the DC ratings. Make sure you know what you’re ordering!

Bill
Reply With Quote
  #18  
Old 04-11-2019, 12:00:10 AM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

When the exciting current decreases and the field collapses, the bridge rectifier will merely function as a freewheeling diode. No more current can flow than was flowing in the circuit to begin with, and the voltage will merely be the forward bias of the rectifier.

The risk of high voltage on the rectifier would be from a short on the generator output. That would result in a voltage spike across the auxiliary field and it's rectifier. I'd bet it wouldn't peak out at more than a couple hundred volts though.

I installed a 50 amp, 1 kV rectifier. It was cheap. I bought a ten pack for less than $30. I'll have to check the brand though. To see if it is reputable.
Reply With Quote
  #19  
Old 04-11-2019, 11:12:33 AM
Zephyr7 Zephyr7 is offline
Registered-III
 
Join Date: Mar 2017
Location: Davisburg, Michigan
Posts: 1,979
Thanks: 605
Thanked 1,116 Times in 761 Posts
Default Re: Wiring 7.5A27 kohler

Quote:
Originally Posted by Vanman View Post
When the exciting current decreases and the field collapses, the bridge rectifier will merely function as a freewheeling diode. No more current can flow than was flowing in the circuit to begin with, and the voltage will merely be the forward bias of the rectifier.
A bridge rectifier can only act as a free wheeling (reverse biased) protection diode if the inductance is connected across the DC terminals. Is that the case here? I couldn’t find a schematic that clearly showed the rectifier connections.

There is no DC current path through the AC terminals of a full wave bridge rectifier due to the way the diodes are internally connected. No reverse transient protection is offered to anything connected to the AC terminals of a full wave bridge rectifier.

Bill
Reply With Quote
  #20  
Old 04-11-2019, 01:14:45 PM
Vanman Vanman is offline
Subscriber
 
Join Date: Aug 2011
Location: Mission Viejo, California
Posts: 5,397
Thanks: 8,167
Thanked 2,401 Times in 1,634 Posts
Default Re: Wiring 7.5A27 kohler

Yes, the rectifier allows the DC auxiliary field winding to be in series with the AC load. The transformer makes it so that the rectifier and winding do not need to carry ~50 amps.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
No Lead & E 10 used in 7.5A27 Kohler Gen. little river Kohler Generators 6 02-15-2009 05:30:15 PM
Kohler 7.5a27 trontek Kohler Generators 8 11-17-2007 10:03:48 AM
Kohler 2.5A27 MDavidson621 Kohler Generators 3 10-16-2007 12:08:12 PM
Kohler 6.5A27 Marine gen set Steve S. Kohler Generators 1 07-29-2006 07:58:45 PM
kohler 5A27 manual Brett Kish Kohler Generators 5 11-13-2003 07:35:07 PM