16kw generac stby generator 990 LP engine not starting


this thread has 4 replies and has been viewed 568 times

Reply
 
Thread Tools Display Modes
  #1  
Old 07-26-2019, 02:26:12 PM
Fast eddie Fast eddie is offline
Registered
 
Join Date: Jul 2019
Location: Nassau Bahamas
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default 16kw generac stby generator 990 LP engine not starting

Hi guys, my generac generator model #0058240 won't start unless I manually open the lever in the fuel regulator behind the diaphragm using a small screw driver, or spraying a small amount of quick start in the mixer box. When it starts it operates perfectly in all load modes. My lp fuel pressure is 11.5 in/H2O at the outlet of the regulator, compression test on both cylinders is 210 psi, and pressure holding 210psi for 10 mins. The generac tech said the regulator was bad, I replaced it but engine still did not start unless I manually opened the lever or use quick start. Does anyone know of a test, or is there a vacuum from the intake that assist the diaphragm to open the lever to.
Reply With Quote
Sponsored Links
  #2  
Old 08-27-2019, 04:56:49 PM
dkamp dkamp is online now
eMail NOT Working
 
Join Date: Oct 2007
Location: LeClaire, Iowa, USA
Posts: 1,748
Thanks: 35
Thanked 949 Times in 613 Posts
Default Re: 16kw generac stby generator 990 LP engine not starting

Eddie- first off- never manually operate the regulator in any way other than the way it was intended- using a screwdriver, etc., to push it open will damage the diaphragm, bend the lever, etc., and render it unsafe and inaccurate.

Next... I believe by your description, that the regulator you're referring to is the Demand Regulator (first one before the mixer) there should NOT be need for any vacuum or manual operator to get the regulator to properly meter fuel... the demand regulator's design makes it sensitive to demand (venturi) vacuum, it meters fuel based on airflow through that venturi... and it should be sensitive enough to respond to airflow at starting speeds.

First thing to check, is for a nice, snappy-mean-hot spark... your engine has lots of compression, and with a gaseous fuel that's rather lean, it requires lots of spark energy to light the mix.

Next thing, is to make sure your exhaust is not partially obstructed. Not uncommon for rodents, wasps, etc., to restrict the exhaust enough to alter vacuum signal during cranking. Same goes for intake air supply restrictions (air cleaner).
Reply With Quote
  #3  
Old 08-28-2019, 08:52:26 AM
Fast eddie Fast eddie is offline
Registered
 
Join Date: Jul 2019
Location: Nassau Bahamas
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default Re: 16kw generac stby generator 990 LP engine not starting

Morning all, got it running, found the vacuum leak at the rubber sleeves on the intake manifold where it is attached to the mixing box. Replaced them and the generator started up within 5 seconds of cranking. It was a tricky one, thanks for your advice.

Fast Eddie
Reply With Quote
  #4  
Old 08-29-2019, 11:38:39 AM
dkamp dkamp is online now
eMail NOT Working
 
Join Date: Oct 2007
Location: LeClaire, Iowa, USA
Posts: 1,748
Thanks: 35
Thanked 949 Times in 613 Posts
Default Re: 16kw generac stby generator 990 LP engine not starting

Good deal!
Reply With Quote
  #5  
Old 09-29-2019, 10:52:54 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Moderator
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 18,927
Thanks: 10,001
Thanked 16,802 Times in 7,774 Posts
Default Re: 16kw generac stby generator 990 LP engine not starting

It is always the simple things that get you.I was working on a transfer switch that would not transfer. Spent some time on it. Then noticed the transfer motor switch was OFF. But it all back together. Told the customer no charge and left. I felt like an idiot.
__________________
I don't talk to myself. This early in the morning. Why the hell should I talk to you.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
Generac 990 16kw Standby Generator Fast eddie Generac Generators (SEARS, etc.) 3 08-22-2019 11:49:04 PM
Generac Generator (16kW) cycles (Hz) fluctuating stitch0852 Generac Generators (SEARS, etc.) 17 04-06-2014 01:20:22 PM
Generac 16KW what is the Model? GRT Generac Generators (SEARS, etc.) 5 04-05-2014 07:07:54 AM
Onan 16kw DNAE generator with detector panel Plumber Rick Onan Generators 8 07-29-2012 04:08:15 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 08:39:54 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277