  #1  
Old 02-11-2014, 12:25:14 AM
mech1369dlw mech1369dlw is offline
Registered
 
Join Date: Dec 2013
Location: Junction City, Kansas USA
Posts: 8
Thanks: 3
Thanked 1 Time in 1 Post
Default Onan Gen Shutdown

I have read a few times about not letting the generator shut down while under load by running out of gas. Why? What happens that is so bad about this happening? just curious. Thanx
Reply With Quote
Sponsored Links
  #2  
Old 02-11-2014, 12:34:53 AM
Jim Marcozzi Jim Marcozzi is offline
Registered-II
 
Join Date: Nov 2013
Location: Hempfield, PA, USA
Posts: 538
Thanks: 60
Thanked 324 Times in 167 Posts
Default Re: Onan Gen Shutdown

Quote:
Originally Posted by mech1369dlw View Post
I have read a few times about not letting the generator shut down while under load by running out of gas. Why? What happens that is so bad about this happening? just curious. Thanx

It can:

Kill the residual magnetism that's required to start generation
Overload the regulator since it will go full field to try to compensate for low output
Damage the load due to spikes, low voltage or incorrect frequency

I'm sure others will add
Reply With Quote
  #3  
Old 02-11-2014, 08:36:25 AM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 6,266
Thanks: 370
Thanked 5,282 Times in 2,549 Posts
Default Re: Onan Gen Shutdown

In addition to the possibilities Jim mentions, add "considerably lighten one's wallet".
Reply With Quote
The Following User Says Thank You to Wayne 440 For This Post:
  #4  
Old 02-11-2014, 10:06:19 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,580
Thanks: 9,070
Thanked 14,976 Times in 7,067 Posts
Default Re: Onan Gen Shutdown

The older ones with out regulators are not effected as much as the ones with them. It doesn't always damage them. But you want to avoid a loaded shut down as much as you can. Don't need to see the magic smoke come out.
Reply With Quote
  #5  
Old 02-11-2014, 10:34:48 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 4,144
Thanks: 725
Thanked 2,439 Times in 1,437 Posts
Default Re: Onan Gen Shutdown

Shutting down a Magneciter designed generator under load will not damage this style generator but it may do harm to the connected loads. Just not a good idea to abuse your refrigerator compressor or even the TV. As mentioned already, it may damage the later designed Onan voltage regulator controlled generators.

Nevertheless, back in 1970 I designed and successfully installed my own version of a generator shunt trip device for the very reasons mentioned above. There are all kinds of so called shunt trip devices. However, mine monitors the generators frequency. When the frequency is within spec limit, + or - 3 hertz, a contactor closes there by making the 120/240 output available. The circuit is also damped to prevent nuisance tripping.

Leon
Reply With Quote
  #6  
Old 02-11-2014, 10:42:15 AM
Billy J Shafer's Avatar
Billy J Shafer Billy J Shafer is offline
Subscriber
 
Join Date: Nov 2004
Location: Centerville, Texas
Posts: 17,580
Thanks: 9,070
Thanked 14,976 Times in 7,067 Posts
Default Re: Onan Gen Shutdown

They call that roll off protection now of days Leon. Sure saves some money
Reply With Quote
  #7  
Old 02-11-2014, 04:27:10 PM
Isaac-1 Isaac-1 is offline
Subscriber
 
Join Date: Aug 2008
Location: Leesville, Louisiana
Posts: 3,277
Thanks: 120
Thanked 1,153 Times in 914 Posts
Default Re: Onan Gen Shutdown

Thanks for bringing up this topic, it reminded me that I had a 200 amp shunt trip molded case breaker laying around, maybe I will use it to build a safety out of range (high / low voltage or frequency) trip for my MEP-003a since they tend to go high voltage on AVR failure.
Reply With Quote
  #8  
Old 02-11-2014, 05:04:51 PM
scoops scoops is offline
Registered-III
 
Join Date: Oct 2008
Location: pittsburgh
Posts: 1,091
Thanks: 362
Thanked 464 Times in 338 Posts
Default Re: Onan Gen Shutdown

Quote:
Originally Posted by Leon N. View Post
Shutting down a Magneciter designed generator under load will not damage this style generator but it may do harm to the connected loads. Just not a good idea to abuse your refrigerator compressor or even the TV. As mentioned already, it may damage the later designed Onan voltage regulator controlled generators.

Nevertheless, back in 1970 I designed and successfully installed my own version of a generator shunt trip device for the very reasons mentioned above. There are all kinds of so called shunt trip devices. However, mine monitors the generators frequency. When the frequency is within spec limit, + or - 3 hertz, a contactor closes there by making the 120/240 output available. The circuit is also damped to prevent nuisance tripping.

Leon
I'd be more interested in what you built Leon.
Care to share how it was constructed?
Reply With Quote
  #9  
Old 02-11-2014, 05:13:57 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 4,144
Thanks: 725
Thanked 2,439 Times in 1,437 Posts
Default Re: Onan Gen Shutdown

Scoops, yes think I can assemble some information. I am not a computer wiz, but I will see what I can do.
Reply With Quote
  #10  
Old 02-11-2014, 05:32:27 PM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 1,456
Thanks: 560
Thanked 418 Times in 297 Posts
Default Re: Onan Gen Shutdown

Quote:
Originally Posted by Leon N. View Post
Scoops, yes think I can assemble some information. I am not a computer wiz, but I will see what I can do.
Is that schematic from the Radio Amature Handbook for a voltage controlled trip using a GFI still floating around here?
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
ONAN NHE shutdown while running Ray Armstrong Onan Generators 8 09-16-2013 01:28:10 PM
need help with Onan RDJF 17.5 overtemp shutdown ollie Onan Generators 7 07-25-2012 03:04:50 PM
Onan MDJA shutdown Mod. Daverepair Onan Generators 1 04-28-2012 09:43:37 PM
Onan Shutdown Circuit won't allow Start Robert Ward Onan Generators 8 06-15-2011 12:08:06 PM
Onan 7.5JB: Add low oil pressure shutdown? ChadS Onan Generators 14 04-28-2005 10:34:32 AM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 03:37:25 AM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2016 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277