Generators and Motors
[Home] - [HELP] - [Forums] - [Library] - [Photo Gallery] - [Groups] - [Classified Ads] - [Subscribe] - [Links] - [Books] - [Sponsors] -

Go Back   SmokStak > SmokStak® Vintage Electrical Equipment > Generators & Electric Motors General Discussion > Onan Generators
Forgot Password? Join Us!

Notices

Onan Generators Restoring, operating and maintaining vintage Onan generators.

Onan Generators

Onan MDJE - How can you tell what is T1, T2, T3 or T4?


this thread has 65 replies and has been viewed 2282 times

Reply
 
Thread Tools Display Modes
  #51  
Old 02-14-2018, 03:42:43 PM
Topman Topman is offline
Registered
 
Join Date: Jan 2018
Location: Abbotsford, B.C. Canada
Posts: 42
Thanks: 27
Thanked 19 Times in 12 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

I have installed several sub-panels in our electrical system (Square D).
Most of these sub-panels come with a screw/bolt which connects the ground bar and neutral bar in the sub-panel itself. (In the case where the panel is used as a main). When used as a sub-panel this screw/bolt must be removed. (Un-bonding). The sub-panel and its circuits are protected by the bonded neutral and ground in the main service panel to which it is connected.
This was my thinking when applying the same principal to the generator. If all the conductors were separated at the generator, (120V, 120V, Neutral, Ground), and connected to the main system, even though the generator was supplying the power, it would still be protected by the main service panel just as would happen with a sub-panel.
Just thinking......
Reply With Quote
The Following User Says Thank You to Topman For This Post:
Sponsored Links
  #52  
Old 02-14-2018, 05:49:33 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,898
Thanks: 698
Thanked 2,249 Times in 1,341 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

It will take a while for me to figure out what appears to be a contradiction. To use your description, if you unbound the sub panel, i.e., disconnect the neutral from the ground bus what about all your house appliances that are fed from the sub panel? Most appliances have the white wire and the bare copper wire connected to the neutral and the ground bus. I am not sure how you are going to provide a safety ground to the generator?

One minute you say unbonding the neutral from the ground and next you say it’s circuits are protected by the bonded neutral and ground in the main panel? I do not understand what principle you are trying to convey?

There has to be a common earth ground and only one, for all circuits regardless of using a sub panel.
Reply With Quote
  #53  
Old 02-14-2018, 05:52:46 PM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 1,282
Thanks: 463
Thanked 338 Times in 247 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Quote:
Originally Posted by Topman View Post
I guess I'm just feeling a little sorry for the horse !
Oh,,, trust us,,, this horse is way past burger.

I wonder if anyone would recognize another forums pet thread,,, about bacon, cured with no nitrate/nitrites,,, but loaded with celery powder?

Same dead horse that wont go away.
Reply With Quote
The Following User Says Thank You to grif For This Post:
  #54  
Old 02-14-2018, 07:34:33 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,898
Thanks: 698
Thanked 2,249 Times in 1,341 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

I see he's from Washinton state. Figures.
Reply With Quote
  #55  
Old 02-14-2018, 07:52:18 PM
KPack KPack is offline
Subscriber
 
Join Date: Feb 2016
Location: Bryan, Texas
Posts: 535
Thanks: 1,711
Thanked 424 Times in 217 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

I say uncle
Reply With Quote
  #56  
Old 02-14-2018, 11:51:11 PM
Topman Topman is offline
Registered
 
Join Date: Jan 2018
Location: Abbotsford, B.C. Canada
Posts: 42
Thanks: 27
Thanked 19 Times in 12 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Okay, one last time from my perspective. I can only describe how our wiring is set up.
Each sub-panel is simply an extension of the main service panel.
The sub-panel has 4 conductors which are directly connected to the main service panel.
Ground, Neutral, and 2 black (hot) conductors.
There is a continuous unbroken connection from each of these conductors to the main panel.

The circuits from the sub-panel are protected by the neutral bond in the service panel.
All I can say is that our wiring has been inspected and approved by a government inspector.
I still enjoy all the comments,
Thanks, Iver
Reply With Quote
The Following 3 Users Say Thank You to Topman For This Post:
  #57  
Old 02-15-2018, 08:57:08 AM
KPack KPack is offline
Subscriber
 
Join Date: Feb 2016
Location: Bryan, Texas
Posts: 535
Thanks: 1,711
Thanked 424 Times in 217 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Quote:
Originally Posted by Topman View Post
Okay, one last time from my perspective. I can only describe how our wiring is set up.
Each sub-panel is simply an extension of the main service panel.
The sub-panel has 4 conductors which are directly connected to the main service panel.
Ground, Neutral, and 2 black (hot) conductors.
There is a continuous unbroken connection from each of these conductors to the main panel.

The circuits from the sub-panel are protected by the neutral bond in the service panel.
All I can say is that our wiring has been inspected and approved by a government inspector.
I still enjoy all the comments,
Thanks, Iver
Sounds right to me.
Reply With Quote
The Following 3 Users Say Thank You to KPack For This Post:
  #58  
Old 02-15-2018, 09:24:38 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,898
Thanks: 698
Thanked 2,249 Times in 1,341 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Over that sounds right to me also.
Reply With Quote
The Following User Says Thank You to Leon N. For This Post:
  #59  
Old 02-15-2018, 11:20:38 AM
AndersonMillTexas AndersonMillTexas is offline
Registered-III
 
Join Date: Oct 2012
Location: Boston, Massachusetts
Posts: 554
Thanks: 327
Thanked 68 Times in 47 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

I bought a big ass Magnifying glass and discovered a whole world of things I could not see before.

Arthur Conan Doyle would be proud.

I used it yesterday when reconfiguring 220 to 110 on my antique table saw.

After 50 years of aging the "T" 1....8 were well worn.

Also, I found that on amazon, panduit sells special wire labels that you can run through your printer, waterproof abrasion resistant and only $5.00 for 90
Reply With Quote
  #60  
Old 02-15-2018, 11:52:46 AM
grif grif is offline
Registered-III
 
Join Date: Oct 2011
Location: Yakima, Washington
Posts: 1,282
Thanks: 463
Thanked 338 Times in 247 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Quote:
Originally Posted by Leon N. View Post
I see he's from Washinton state. Figures.
Yup,,, but not from the far Left Coast
Reply With Quote
The Following User Says Thank You to grif For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
onan 7.5 MDJE needs help blaise805 Onan Generators 35 04-20-2014 05:07:10 AM
Onan MDJE 6-7.5KW Help Mainshiptom Onan Generators 4 04-19-2010 05:32:50 PM
7.5 KW Onan MDJE won't crank bayoucadillac Onan Generators 12 02-20-2010 03:44:53 PM
Onan 7.5 MDJE - 3CR Help LarryGlover Onan Generators 11 07-19-2007 04:38:12 PM
Onan MDJE 6-7.5KW Help Mainshiptom Onan Generators 0 09-28-2005 05:48:23 AM