Onan MDJE - How can you tell what is T1, T2, T3 or T4?


this thread has 65 replies and has been viewed 1895 times

Reply
 
Thread Tools Display Modes
  #31  
Old 02-13-2018, 08:16:16 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,716
Thanks: 671
Thanked 2,130 Times in 1,279 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

No NO Please! What Wayne and BigBlockChev said is correct. You have to ground T2& T3 to the generator frame, period. They constitute the neutral. The neutral is electrically tied to the white wire and the so called green wire when they are connected to your house panel.

It is or can be very dangerous to not to tie T2 & T3 to the generator chassis., if you want 120/240 service. For example, what if there is an insulation failure in the generator? The generator frame could become alive and you touch the machine and get a shock. Please with all due respect, do not do that.
Reply With Quote
Sponsored Links
  #32  
Old 02-13-2018, 08:21:39 AM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,507
Thanks: 336
Thanked 4,628 Times in 2,196 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

And here we go...
Reply With Quote
The Following 2 Users Say Thank You to Wayne 440 For This Post:
  #33  
Old 02-13-2018, 09:01:27 AM
KPack KPack is offline
Subscriber
 
Join Date: Feb 2016
Location: Bryan, Texas
Posts: 496
Thanks: 1,582
Thanked 401 Times in 203 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Quote:
Originally Posted by Topman View Post
Okay, Wayne 440. Thank you very much.

So if I understand you correctly, and as BigBlockChev says:
T-2 and T-3 together are the neutral.

I would need to remove both T-2 and T-3 from the ground post to un-bond the generator.
Keeping them together on an insulated terminal, they would be the (white) Neutral.
Bare wire goes to the frame.
Hopefully, that's it?
Thanks, Iver.
Are you going hook your generator to your house panel or are going to use the generator by its self?
Reply With Quote
  #34  
Old 02-13-2018, 10:29:41 AM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,716
Thanks: 671
Thanked 2,130 Times in 1,279 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

There is nothing mysterious about this. The owner should refer to the Onan operators manual for the kind of information I attached in my previous post.
Reply With Quote
  #35  
Old 02-13-2018, 02:22:05 PM
KPack KPack is offline
Subscriber
 
Join Date: Feb 2016
Location: Bryan, Texas
Posts: 496
Thanks: 1,582
Thanked 401 Times in 203 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Quote:
Originally Posted by Leon N. View Post
There is nothing mysterious about this. The owner should refer to the Onan operators manual for the kind of information I attached in my previous post.
Just that it can be bonded in two different places. But a lot of people do it and don’t have trouble.
On a welding forum I read they hook there welders to there house panel but don’t unbond t2 and t3 at the welder.
Reply With Quote
  #36  
Old 02-13-2018, 03:03:39 PM
Topman Topman is offline
Registered
 
Join Date: Jan 2018
Location: Abbotsford, B.C. Canada
Posts: 40
Thanks: 23
Thanked 17 Times in 10 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Okay, just when I thought it was resolved.......
This generator was originally designed to operate in a boat. The manual describes the wiring with T-2 and T-3 bonded to the frame which is how it should operate in that environment.
And if it was to operate on land as a stand-alone power source that also would be the case.
However, my plan is to use this generator as a back up power source for our house. Now from all I have read and from what I understand is that the residential electrical system requires neutral bonding ONLY once. Generally at the service entrance power panel.
So, if I want to be in compliance I need to unbond the generator or unbond the service entrance panel.

If the generator is combined with the house system, and the house system neutral is bonded at source, does that not protect the system?

I am open to any suggestions as to what to do.
Thanks , Iver.
Reply With Quote
  #37  
Old 02-13-2018, 03:49:37 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,716
Thanks: 671
Thanked 2,130 Times in 1,279 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

OK you are getting there. May I address your comments because I have successfully installed my JB into our home electrical system.

Okay, just when I thought it was resolved.......
This generator was originally designed to operate in a boat. The manual describes the wiring with T-2 and T-3 bonded to the frame which is how it should operate in that environment.
And if it was to operate on land as a stand-alone power source that also would be the case. [ YES that is correct]

However, my plan is to use this generator as a back up power source for our house.

[This is exactly what I have done now some 48 years ago and it continues to work very nicely]


Now from all I have read and from what I understand is that the residential electrical system requires neutral bonding ONLY once. Generally at the service entrance power panel.

[ Yes. When you say "neutral bonding" what that means to me is that the neutral is bonded to earth ground at one and only one point in the electrical system. It means the utility neutral inside your entrance panel has a relatively heavy wire running from the neutral ground bus inside your panel to a water pipe or a single earth ground point. This is where all the white and green Romex wires are connected]

So, if I want to be in compliance I need to unbond the generator or unbond the service entrance panel.

[No! The generator frame like any electrical motor or device need to electrically grounded, that is tied to the neutral (t2/T3) and hard wired to the neutral in your house power panel I just described. You should never unbound the service entrance panel. I assume you mean disconnect the utility neutral from that earth ground/water pipe.]

If the generator is combined with the house system, and the house system neutral is bonded at source, does that not protect the system?

[Yes, however,when you say " combined with the house system" what you should mean the generator neutral should not be switched but solidly connected to the house neutral. By using the term " combined" I hope you mean disconnecting the utility hot leads analogous to the generators T1 & T4 and switching the house loads over to the generator by using, for example a double pole double throw circuit breaker type contactor inside your house panel.]

[In my installation, my generators output leads are configured as previously shown in my attached Figure 1-11. T2 & T3 are hard wired not only to the generator chassis but run to and hard wired to the house panel /utility neutral bus which in turn is earth grounded to the house water pipe. I employ a two-pole interlock type circuit breaker mounted inside the house panel along with the branch circuit breakers. This allows me to select either utility or gen power but obviously not both at the same time. I do not employ an automatic transfer switch.]
Reply With Quote
  #38  
Old 02-13-2018, 04:12:11 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,507
Thanks: 336
Thanked 4,628 Times in 2,196 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

.........
Reply With Quote
The Following 2 Users Say Thank You to Wayne 440 For This Post:
  #39  
Old 02-13-2018, 09:59:42 PM
Leon N. Leon N. is offline
Registered-III
 
Join Date: Oct 2009
Location: N. Chelmsford, MA, USA
Posts: 3,716
Thanks: 671
Thanked 2,130 Times in 1,279 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Oh come on Wayne, it isn't that bad. Seriously, what I said is what I have done and I have never had a connectivity problem. If you have any questions I would be happy to explain.
Reply With Quote
  #40  
Old 02-13-2018, 10:16:37 PM
Wayne 440 Wayne 440 is offline
Registered-III
 
Join Date: Nov 2004
Location: Kentucky
Posts: 5,507
Thanks: 336
Thanked 4,628 Times in 2,196 Posts
Default Re: Onan MDJE - How can you tell what is T1, T2, T3 or T4?

Leon, I understand what you have done. And at the time, that was (as far as I know) a commonly accepted method. But today, (again as far as I know) it is generally not. My understanding is that N-G should be connected at either the generator set or the service panel, not in both places.

I am going to do myself and possibly others a favor and no longer discuss N-G bonding on this board. It is a dead horse that deserves no further beating from yours truly.
Reply With Quote
The Following 3 Users Say Thank You to Wayne 440 For This Post:
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
onan 7.5 MDJE needs help blaise805 Onan Generators 35 04-20-2014 05:07:10 AM
Onan MDJE 6-7.5KW Help Mainshiptom Onan Generators 4 04-19-2010 05:32:50 PM
7.5 KW Onan MDJE won't crank bayoucadillac Onan Generators 12 02-20-2010 03:44:53 PM
Onan 7.5 MDJE - 3CR Help LarryGlover Onan Generators 11 07-19-2007 04:38:12 PM
Onan MDJE 6-7.5KW Help Mainshiptom Onan Generators 0 09-28-2005 05:48:23 AM