Generac Stator Rewind? DPE Winding?


this thread has 29 replies and has been viewed 17362 times

Reply
 
Thread Tools Display Modes
  #1  
Old 10-10-2011, 10:34:42 AM
ProudDad2005 ProudDad2005 is offline
Registered
 
Join Date: Feb 2009
Location: Fort Worth, Texas
Posts: 20
Thanks: 5
Thanked 8 Times in 2 Posts
Default Generac Stator Rewind? DPE Winding?

Gentlemen, I have a 20KW Generac diesel generator that had a shorted stator. I have found a motor shop that has rewound the stator but they failed to add the DPE winding and now I have no excitation at the voltage regulator. The motor shop claims they did not see a DPE winding when they disassembled the stator but after showing them the wiring diagram they conceaded that there was one. The motor shop says they can add the DPE winding if they know the wire size and the number of turns. I have tried to contact Generac and they refuse to talk to me. Is there any way to obtain this info? Can I use an aftermarket voltage regulator that does not need a DPE winding instead. Any help would be appreciated. Just paid a lot of money to rewind this stator and really hope it was not in vain. Unit model # is M99A02340-S. Serial # is 2047574.
Reply With Quote
Sponsored Links
  #2  
Old 10-10-2011, 10:42:20 AM
K D Redd K D Redd is offline
In Memory Of
 
Join Date: Nov 2004
Location: Southwest Missouri
Posts: 5,348
Thanks: 166
Thanked 1,196 Times in 1,057 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

I would FIRST sue the rewind shop to get my money with damages back. If they can not tell the difference between a generator stator and a motor stator they DO NOT need to be in the rewinding business.

Kent
Reply With Quote
  #3  
Old 10-10-2011, 01:22:08 PM
Motorwinder Motorwinder is offline
Registered
 
Join Date: Jul 2011
Location: Yuma, Arizona
Posts: 20
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Generac Stator Rewind?? DPE Winding??

I'd take it back and tell them to figure it out.

I have some old data that said 7 turns of #18.
Reply With Quote
  #4  
Old 10-10-2011, 03:19:29 PM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,105
Thanks: 299
Thanked 866 Times in 652 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

Ide just use a transformer rather than rewind
one with lots of windings can usually be bucked or boosted to the right voltage
Reply With Quote
  #5  
Old 10-10-2011, 04:11:15 PM
ProudDad2005 ProudDad2005 is offline
Registered
 
Join Date: Feb 2009
Location: Fort Worth, Texas
Posts: 20
Thanks: 5
Thanked 8 Times in 2 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

Mtorwinder, thanks for your help. That is more info then I can get from Generac. Do you think that old data is accurate for my 20KW?

---------- Post added at 03:11 PM ---------- Previous post was at 02:46 PM ----------

Armandh, what would you use for the primary input to the txfmr?
Reply With Quote
  #6  
Old 10-10-2011, 04:39:20 PM
Wayne 440 Wayne 440 is online now
Registered
 
Join Date: Nov 2004
Location: Kentucky
Posts: 7,428
Thanks: 487
Thanked 6,895 Times in 3,215 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

The motor shop guys should be the ones calling/looking etc. for the DPE winding info, not you. You paid for a rewind, not part of a rewind.

One issue will be finding what voltage the Generac regulator requires from the DPE winding. A second will be how much residual voltage the set retains. It may require flashing on each start without the DPE winding.
Reply With Quote
  #7  
Old 10-10-2011, 06:18:04 PM
Arkie Arkie is offline
Registered
 
Join Date: Sep 2009
Location: Oklahoma USA
Posts: 1,165
Thanks: 12
Thanked 288 Times in 262 Posts
Default Re: Generac Stator Rewind? DPE Winding?

Right on about it's the motor shop's issue now, even if they have your money already.

Take it back and dump it in their lap and do get a receipt for the return and get a expected turn around date. A good rewind shop can come up with that data! If you come up with the wrong data and give it too them, it's then your fault if their rewind don't fly!

Ask for the Supervisor/shop manager when you return and I would not even call, just go! If they start hum hawing and offer your money back take it, if they don't offer money back and their time limit runs out, go and tell them that Judy Judge is very interested in your case!
Try to get the name of someone with the company that has a email address and make later inquiries by email and keep their responses for court evidence for Judge Judy for later!
Reply With Quote
  #8  
Old 10-10-2011, 07:00:38 PM
Motorwinder Motorwinder is offline
Registered
 
Join Date: Jul 2011
Location: Yuma, Arizona
Posts: 20
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Generac Stator Rewind?? DPE Winding??

Quote:
Originally Posted by ProudDad2005 View Post
Mtorwinder, thanks for your help. That is more info then I can get from Generac. Do you think that old data is accurate for my 20KW?

---------- Post added at 03:11 PM ---------- Previous post was at 02:46 PM ----------

Armandh, what would you use for the primary input to the txfmr?
This was for a 15KW Generac. http://www.poweredgenerators.com/gua...als/0E0226.pdfI'm betting the AVR is the same, so it be worth a try.

This one had a 12 pin plug. (show this to your winder)>>The 2 DPE coils in the stator had a 1- 10 span in the 24 slot stator. 2 adjacent coils, all leads brought out for a total of 6 leads. One at start, one tapped to the 4th turn, one at finish. on both coils. One #18 7 turns. Of course the leads hook to the plug, and I'd have to scan my data sheet to show how it hooked. But this should give them the basic info for the coils and taps. I'll try to explain though. With plug tab facing down, number the pins 1-12. Start of 1st coil is pin #2. Tap of 1st coil is pin #4. Finish of 1st coil is pin#3. Start of 2nd coil is pin #10. Tap of 2nd coil is pin #8. Finish of 2nd coil is pin #9.

Hope this helps. Good luck.

---------- Post added at 04:00 PM ---------- Previous post was at 03:40 PM ----------

Quote:
Originally Posted by Arkie View Post
Right on about it's the motor shop's issue now, even if they have your money already.

Take it back and dump it in their lap and do get a receipt for the return and get a expected turn around date. A good rewind shop can come up with that data! If you come up with the wrong data and give it too them, it's then your fault if their rewind don't fly!

Ask for the Supervisor/shop manager when you return and I would not even call, just go! If they start hum hawing and offer your money back take it, if they don't offer money back and their time limit runs out, go and tell them that Judy Judge is very interested in your case!
Try to get the name of someone with the company that has a email address and make later inquiries by email and keep their responses for court evidence for Judge Judy for later!

Getting the data would be a major problem for the motor shop. Proprietary information they won't cut loose with. If they can't get it to work, the only thing the motor shop could do is buy him a new stator.
Reply With Quote
The Following User Says Thank You to Motorwinder For This Post:
  #9  
Old 10-10-2011, 08:29:07 PM
Lloyd H Lloyd H is offline
Subscriber
 
Join Date: Feb 2008
Location: Chester, Illinois, USA
Posts: 519
Thanks: 169
Thanked 158 Times in 122 Posts
Default Re: Generac Stator Rewind? DPE Winding?

If the rotor resistance is high enough for a SX-460 (min of 15 Ohms I think) the rewind shop might spring for it and make you an AVR genset out of it.
Reply With Quote
  #10  
Old 10-10-2011, 10:24:30 PM
Motorwinder Motorwinder is offline
Registered
 
Join Date: Jul 2011
Location: Yuma, Arizona
Posts: 20
Thanks: 2
Thanked 1 Time in 1 Post
Default Re: Generac Stator Rewind? DPE Winding?

You could put a Bassler SR1 on it, if you can tap 115 volts.
Reply With Quote
  #11  
Old 10-10-2011, 10:56:16 PM
EricWood's Avatar
EricWood EricWood is online now
Subscriber
 
Join Date: Oct 2005
Location: West Concord, Minnesota USA
Posts: 2,009
Thanks: 249
Thanked 1,554 Times in 828 Posts
Default Re: Generac Stator Rewind? DPE Winding?

Yes,

It is very likely you can run this unit without the DPE winding/third-party regulator. Its a dedicated source for the Generac voltage regulator. I've converted Generac's to other regulators--you'll just have to find one that is tolerant to the field ohms, as Generac loved their low-ohms fields.

(i believe the spec for the Onan 200-2880 you hear mentioned on this board is a very low ohm field tolerant unit--but I can find the info i was looking for tonight. You might want to call Flight Systems and see what they say about their spec's for their replacement unit for the 300-2880.)

eric
Reply With Quote
  #12  
Old 10-11-2011, 09:36:47 AM
ProudDad2005 ProudDad2005 is offline
Registered
 
Join Date: Feb 2009
Location: Fort Worth, Texas
Posts: 20
Thanks: 5
Thanked 8 Times in 2 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

Wayne 440, you made a comment that it will need to be flashed everytime without a DPE winding. I did attempt to flash the field with 12vdc and the voltage only raised to 158vac L to L. When I removed the 12vdc the voltage dropped to 80vac L to L. Is this normal since the DPE winding is missing or should that have reached 240vac L to L even without the DPE winding? Do you think there is another problem with the stator. The owner of the rewind shop personally inspected the stator and said that there was nothing wrong with the rest of it but what I dont understand is that shouldnt have I been able to get correct L to L voltage when applying 12vdc directly to the brushes?

Just to give a little more history on this generator. its a 20kw and before I took the stator in to the rewind shop the unit produce steady 120/240vac. The problem was is that it started sounding like there were loose rocks or marbles in the generator end. After inspection during operation I found a lot of arcing and sparking going on between the rotor and stator. Also the stator was getting extremely hot in one spot. Hot enough I was unable to hold my hand on it. The rewind shop said one of the coils in the stator was shorting to ground. They rewound the stator and ever since have had the issue above.
Reply With Quote
  #13  
Old 10-11-2011, 10:31:13 AM
Gunny Gunny is offline
Subscriber
 
Join Date: Feb 2005
Location: North Carolina
Posts: 3,835
Thanks: 1,856
Thanked 1,717 Times in 1,074 Posts
Default Re: Generac Stator Rewind? DPE Winding?

How about this?

Involve the rewind shop as they have a huge interest in this.

Go here: http://www.power-tronics.com/ They have a regulator that will work for about any generator ever made.

Feel it should be the rewind shops responsibility to make this right.
Reply With Quote
  #14  
Old 10-11-2011, 10:32:11 AM
Power Power is offline
Registered
 
Join Date: Aug 2011
Location: New Jersey
Posts: 5,432
Thanks: 1,254
Thanked 3,286 Times in 1,932 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

This is very difficult to diagnose long distance. I will tell you about a recent experience that may help, as you may have a similar issue.
Gen was rewound, would not produce full voltage. Returned to shop, who said it was rewound correctly. Owners took it to a generator specialty shop, which blew a diode in the bridge, but could not find a problem.
I was asked to look at it. I replaced the diode. After lot of tests, I concluded one of the coils was hooked up backwards! I wrote instructions on how to reconnect coil, they took it back to original shop, he said that would be backwards, and coil would burn out. They reconnected it. Generator now produces normal voltage and full rated kw.
Reply With Quote
  #15  
Old 10-11-2011, 10:36:31 AM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,105
Thanks: 299
Thanked 866 Times in 652 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

Quote:
Originally Posted by ProudDad2005 View Post
[/COLOR]Armandh, what would you use for the primary input to the txfmr?
I'm looking at a 17.5 KW generac sheet and it looks as if the DPE winding supplies just the voltage regulator through a circuit breaker. I presume it is the field power as the regulator and speed governor get voltage reference from two separate leads attached to the main output windings

so on second thought an after market regulator such as
http://www.partsfortechs.com/asapcar...648-p-153.html
would do the job better if you cant get the rewind free

I would use a variac and an isolation transformer to determine the needed voltage from the mains.
by bringing up the ac power feeding the VR to the point of proper output and then noting the steady output raise it a few volts more.

then watch it under varying load
the isolation is needed because of generac's use of a continuous flashing,
and the few volts more to provide the head room for power input voltage fluctuation under changing main output load

Last edited by armandh; 10-12-2011 at 07:24:50 AM.
Reply With Quote
The Following User Says Thank You to armandh For This Post:
  #16  
Old 10-11-2011, 03:04:59 PM
ProudDad2005 ProudDad2005 is offline
Registered
 
Join Date: Feb 2009
Location: Fort Worth, Texas
Posts: 20
Thanks: 5
Thanked 8 Times in 2 Posts
Default Re: Generac Stator Rewind? DPE Winding?

Someone help me out, the part that I am question is if the stator has been wound wrong. Taking the voltage regulator and DPE winding out of the equation shouldnt I still get full L to L voltage when I placed 12vdc directly to the brushes?
Reply With Quote
  #17  
Old 10-11-2011, 03:10:31 PM
BTPost's Avatar
BTPost BTPost is offline
Moderator
 
Join Date: Jan 2005
Location: Excursion Inlet, Alaska USA 99850-0090
Posts: 4,832
Thanks: 519
Thanked 1,817 Times in 1,200 Posts
Talking Re: Generac Stator Rewind? DPE Winding?

That would depend on the design of the Genend. Was it designed for a nominal 12Vdc Exciter Voltage to produce 120/240Vac, or maybe 18Vdc, or maybe 24Vdc? Unless you know what the Genend Exciter Voltage should be, for Nominal Output AC voltage, you can't answer that question.
__________________
Bruce in alaska
Reply With Quote
  #18  
Old 10-11-2011, 03:16:26 PM
ProudDad2005 ProudDad2005 is offline
Registered
 
Join Date: Feb 2009
Location: Fort Worth, Texas
Posts: 20
Thanks: 5
Thanked 8 Times in 2 Posts
Default Re: Generac Stator Rewind? DPE Winding?

Wouldnt that be decided by the voltage regulator. Generac part #67680.
Reply With Quote
  #19  
Old 10-11-2011, 04:37:10 PM
armandh armandh is offline
Sponsor
 
Join Date: Aug 2006
Location: Suburban St. Louis, Missouri
Posts: 3,105
Thanks: 299
Thanked 866 Times in 652 Posts
Default Re: Generac Stator Rewind? DPE Winding?

Quote:
Originally Posted by ProudDad2005 View Post
Someone help me out, the part that I am question is if the stator has been wound wrong. Taking the voltage regulator and DPE winding out of the equation shouldnt I still get full L to L voltage when I placed 12vdc directly to the brushes?
that is the typical test to check for a functioning gen end. but not necessarily the correct voltage.

the transformer idea is ok if you have one around but otherwise the aftermarket VR is the easiest to do.
I have not seen any spec on my print for excitation voltage.

but it looks as if the reference voltage causes the regulator to vary the output created from the DPE winding source.


having no idea about the VR innards I suggested a test with a variac. but measurements from a working unit would be easier


a constant voltage to the field would give varying output voltage with varying load
voltage regulators keep the output voltage constant by varying the field voltage/current to compensate for varying load.

Last edited by armandh; 10-12-2011 at 08:05:07 AM.
Reply With Quote
  #20  
Old 10-11-2011, 06:38:14 PM
Wayne 440 Wayne 440 is online now
Registered
 
Join Date: Nov 2004
Location: Kentucky
Posts: 7,428
Thanks: 487
Thanked 6,895 Times in 3,215 Posts
Default Re: Generac Stator Rewind?? DPE Winding??

Quote:
Originally Posted by ProudDad2005 View Post
Wayne 440, you made a comment that it will need to be flashed everytime without a DPE winding...
I stated that it "may require flashing"- that largely depends on how much residual voltage the unit retains.

Quote:
Originally Posted by ProudDad2005 View Post
...flash the field with 12vdc and the voltage only raised to 158vac L to L. When I removed the 12vdc the voltage dropped to 80vac L to L. Is this normal since the DPE winding is missing or should that have reached 240vac L to L even without the DPE winding? Do you think there is another problem with the stator...
It is making voltage, that is a good sign. As others indicate, the excitation voltage may have to be more that 12V for full output. There could or could not be "another problem" with the stator.

Quote:
Originally Posted by ProudDad2005 View Post
...The owner of the rewind shop personally inspected the stator and said that there was nothing wrong with the rest of it...
My confidence in the rewind shop would not be absolute, as they somehow managed to leave an entire winding out of the job.
Reply With Quote
Reply

Bookmarks


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

F o r u m Jump

Similar Threads Chosen at Random
Thread Thread Starter F o r u m Replies Last Post
How-To, Exciter Rewind (both Stator & Rotor) a31ford Onan Generators 21 02-19-2017 07:26:40 PM
Stator Winding Removal Doogdoog Generators & Electric Motors General Discussion 18 06-24-2011 06:53:03 PM
Marine Generator Stator - Average lifespan? Rewind? Rotor too? antinucci Kohler Generators 24 04-22-2011 08:56:31 AM
Onan 25EC-4R8/302D Stator rewind questions Old Style Onan Generators 22 12-29-2010 03:10:35 PM
Stator Winding - Voltage Reference Question Jonathan Onan Generators 2 01-12-2006 01:29:30 PM


Use "Ctrl" mouse wheel to change screen size.
All times are GMT -4. The time now is 09:12:19 PM.

Smokstak and Enginads site search!


All use is subject to our TERMS OF SERVICE
SMOKSTAK® is a Registered Trade Mark - A Community of Antique Engine Enthusiasts
Copyright © 2000 - 2019 by Harry Matthews P.O. Box 5612 - Sarasota, FL 34277